Posted on Jan 25 2018 by Peter Yost
Improving the thermal performance of an existing attic is often challenging: workers are faced with narrow cavities, low clearances, and claddingMaterials used on the roof and walls to enclose a house, providing protection against weather. systems that make it hard to achieve desired R-values while still maintaining the necessary drying potential of the assembly.
The house at 81 Chapin Street in Brattleboro, Vermont, is no exception. It’s a 100-year-old wood-framed two-story home that Alex Beck and Candace Pearson are determined to comprehensively retrofit to high performance.
That’s where Eli Gould, owner and founder of Ironwood Brands, comes in. Eli is an architect and builder responsible for projects like the Lemon’s “Almost” Passive House and Alex and Jerelyn Wilson’s Leonard Farm retrofit (see multiple GBA Energy Solutions blogs on the Wilson project). The Brattleboro project has no shortage of challenges; for example, in subsequent blogs we will discuss the basement. Here, we'll focus on the attic, which needed careful hygrothermalA term used to characterize the temperature (thermal) and moisture (hygro) conditions particularly with respect to climate, both indoors and out. consideration.
Eli Gould lays out the roofing configuration used at 81 Chapin Street: “We decided to cavity fill with dense-packed cellulose and then — on the underside of the rafters — to run two staggered-seam, taped layers of 30 mm foil-faced rigid foam insulation.” Gould specified Kingspan Kooltherm rigid foam. (Kingspan is an international corporation headquartered in Ireland. Kingspan's U.S. office is located in Atlanta, Georgia.)
He continued, “This approach got us to the right total R-value, highest level of airtightness, and excellent drying potential to the exterior.” The exterior layers of the roof assembly include sheathing boards, building paperTypically referring to Grade D building paper, this product is an asphalt-impregnated kraft paper that looks a lot like a lightweight asphalt felt. The Grade D designation has come to mean that the building paper passes ASTM D779 (minimum 10-minute rating with the “boat test”) and different products are called out as “30-minute” or even “60-minute” based on D779 results. At times confused with roofing felt, roofing felts and building paper differ in two ways: felts are made of recycled-content paper, building papers of virgin paper; felts are made of a heavier stock paper; building papers a lighter stock. See also roofing felt., and slates. Gould added, “And the clincher for the attic was that the foil-faced Kootherm up there does not need any ignition barrier.”
Candace Pearson, a former editor and research analyst for BuildingGreen, explained, “Initially, we were hoping to find a wood fiberboard insulation that could be installed to the interior [of the rafters], but when we did the modeling we found out we needed a higher R-value.”
Candace said, “We became interested in Kooltherm because, unlike XPS, Kooltherm did not use a high global warming potential (GWP) blowing agent and, unlike conventional polyiso, it did not contain added chemical flame retardants. That’s what initially prompted me to suggest the product. Plus, it is a recommended product in the latest BG insulation guide.”
Kooltherm characteristics and properties
Alex Wilson of BuildingGreen has already published a great article on Kooltherm. The details are really a bit hard to believe:
  • R-6.2 per inch for 1-inch samples, and R-8.2 per inch for 3-inch samples — R-values that are third-party-certified per IECC International Energy Conservation Code. Section C402;
  • No flame retardants yet exceptional smoke development and flame development numbers;
  • Zero ozone depletion potentialAmount of damage to the ozone layer a given chemical can cause compared to trichlorofluoromethane (CFC-11), which is given a value of 1.0 on this relative scale. (ODP);
  • Low global warming potential (GWP).
Let’s go after the first two of these (the most difficult to accept, frankly).
R-value claims
You get R-6.2 or R-6.3 per inch for 1-inch samples, and R-8.2 per inch for 3-inch samples, according to the manufacturer, because of two properties of Kooltherm:
  • The insulation includes really tiny gas pockets (the smaller the pockets, the less heat flow); and
  • The insulation has a high percentage of closed cells (98% are truly trapped gas pockets).
Here is a link to a good technical reference from Kooltherm.
Flammability
I have the most trouble with the flammability performance claimed for Kooltherm. After all, it's a petroleum-based polymer matrix with a hydrocarbon blowing agent. It seems as though we are getting burned, not the insulation!
When I asked Kingspan about this, they stated that phenolic foam is “inherently flame-resistant.” That seemed like restatement, not an explanation. I was then referred to one of Kingspan’s chemists, who explained it this way: “It [comes] down to the highly cross-linked thermoset PF [phenol formaldehydeChemical found in many building products; most binders used for manufactured wood products are formaldehyde compounds. Reclassified by the United Nations International Agency for Research on Cancer (IARC) in 2004 as a “known human carcinogen."] material. [With] a phenolic matrix, unlike U-F chemistry, once cured the polymeric thermoset material is irreversible. Phenolic resins … have a highly cross-linked, high carbon (char), and aromaticity level which lends itself to excellent FST (fire, smoke, and toxicity) properties. The material is stable to well over 200°C.”
That seems to address the fire properties of the phenolic foam matrix, but what about the pentane blowing agent? Craig Lynch, commercial technical director at Kingspan, responded, “The Kooltherm blowing agent is not pentane, but pentane-based. The actual blowing agent is a proprietary mix, with constituents added to — among other things — reduce the flammability of the blowing agent.”
That makes some sense to me as well, but is not wholly convincing. Being an empirical sort of guy, I decided to torch some Kooltherm.
Using a grill starter flame source, the test yields no flame, very little smoke, and only charring.
Using a propane torch, the test yields no flame, very little smoke, and only charring.
That's pretty impressive fire resistance with both the low-temperature grill starter and the higher temperature propane torch.
Test results
To be completely fair, here is a list of fire performance standardized tests from the laboratory certification for NFPA 286: “Tested Wall Assemblies Using Kingspan Kooltherm Insulation Boards in Attics, Crawlspaces, Basements, and other Interior Applications.”
The NFPA 286 test is the “corner” test for interior applications (for example, see this video). The NFPA 285 test is the exterior assembly test (for example, see this video).
  • Performance in accordance with ASTMAmerican Society for Testing and Materials. Not-for-profit international standards organization that provides a forum for the development and publication of voluntary technical standards for materials, products, systems, and services. Originally the American Society for Testing and Materials. E84/UL 723 for smoke and flame development: Flame Spread Index <25; Smoke Developed Index <450
  • Performance for use without a thermal barrier in accordance with IBC Section 2603.4 and 2603.5.2: Approved.
  • Performance with regard to vertical and lateral fire propagation in accordance with IBC Section 2603.5.5: Approved.
  • Performance with regard to ignition in accordance with IBC Section 2603.5.7: Approved.
Clearly Kooltherm — notwithstanding that it is a directly derived petroleum-based rigid insulation — has solid high-performance credentials.
Gould concludes, “Kooltherm is now my interior rigid insulation material of choice for this type of deep energy retrofit.”
In addition to acting as GBA’s technical director, Peter Yost is the Vice President for Technical Services at BuildingGreen in Brattleboro, Vermont. He has been building, researching, teaching, writing, and consulting on high-performance homes for more than twenty years. An experienced trainer and consultant, he’s been recognized as NAHBNational Association of Home Builders, which awards a Model Green Home Certification. Educator of the Year. Do you have a building science puzzle? Contact Pete here. You can also sign up for BuildingGreen’s email newsletter to get a free report on insulation, as well as regular posts from Peter.
Tags: , , , ,
Image Credits:
  1. Images #1, #4, #5, #6, and #7: Peter Yost
  2. Image #2: Eli Gould, PreCraft
  3. Image #3: Kingspan
1.
Jan 25, 2018 8:56 AM ET
Very Kool ! ;)
by John Clark
It's nice to see a product deliver on its claims.
2.
Jan 25, 2018 9:48 AM ET
'ow much does it cost
by Keith Gustafson
3.
Jan 25, 2018 9:52 AM ET
Kooltherm cost
by Peter Yost
Kingspan claims pricing is competitive with foil-faced polyiso rigid foam insulation.
4.
Jan 25, 2018 10:05 AM ET
Edited Jan 25, 2018 10:11 AM ET.
Online pricing in the U.K.
by Martin Holladay
Here is a link to a British website selling Kingspan Kooltherm:
https://www.just-insulation.com/shop/shop-kingspan-kooltherm-rigid-pheno...
For a product described as "external wallboard insulation" measuring 50 mm (2 inches) thick, the price is £11.76 to £12.31 per square meter, depending on quantity. That translates to $16.82 to $17.60 per square meter, or $1.56 to $1.64 per square foot.
For purposes of comparison, it's worth noting that in the United States, Home Depot sells 2-inch thick Rmax polyiso for $0.95 per square foot. Here is a link:
https://www.homedepot.com/p/Thermasheath-Rmax-Thermasheath-3-2-in-x-4-ft...
5.
Jan 25, 2018 10:09 AM ET
Do the thermal properties of
by Randy Williams
Do the thermal properties of the insulation remain consistent as the insulation ages and is there any decrease in R-value when exposed to lower temperatures? Can the insulation also be used exterior?
6.
Jan 25, 2018 10:20 AM ET
Roof assembly
by Armando Cobo
Is it right to install dense packed cellulose against the roof decking, specially on cold climate?
"2015 IRC R806.5.1.3. Where both air-impermeable and air-permeable insulation are provided, the air-impermeable insulation shall be applied in direct contact with the underside of the structural roof sheathing in accordance with Item 5.1.1 and shall be in accordance with the R-values in Table R806.5 for condensation control. The air-permeable insulation shall be installed directly under the air-impermeable insulation."
7.
Jan 25, 2018 10:23 AM ET
Hard to believe
by Alan B
I would like even more testing and if true its mighty impressive.
I would like to see (safe) longer term testing with the blowtorch, a few mins would be nice at both the edge and the face.
I don't like proprietary, i want to know what i am buying, patented is okay since the patent is public knowledge.
8.
Jan 25, 2018 12:44 PM ET
Foil Facing and R-Value
by Rick Evans
According to the third party testing document (provided in this article), the actual R-Value per inch is 6.2 or 6.3 per inch. Does it become R8.2 per inch when the insulation board includes the foil facing? Without an air gap, I presume we have to bring the R-value down.
Seems like a great product though. I too am curious to see how the R-Value changes with temperature and to what extent it is vapor permeable. I would also like to see how it compares to EPS or Polyiso from a Global Warming Potential perspective.
9.
Jan 25, 2018 12:52 PM ET
Edited Jan 25, 2018 1:20 PM ET.
Response to Rick Evans
by Martin Holladay
Rick,
You are quite right: the third-party report from Intertek shows an R-value of either R-6.2 or R-6.3 per inch for 1-inch-thick samples.
For the time being, I have edited the article to reflect this report. I intend to follow up with Peter Yost in case there is more to the story than it currently appears..
10.
Jan 25, 2018 1:07 PM ET
The 1" samples are lower R/inch than the 3" @ Rick Evans
by Dana Dorsett
The fiber-faced 75mm (2.95" ) samples (K20, K5 & K3) tested at R24.9 ( /2.95" = R8.44 per inch).
The foil facers deliver LOWER R/inch.
The foil faced 75mm samples (K15, K8, K7, & K12) tested at R23.8 ( /2.95" = R8.07 per inch)
But the 25mm samples all test in the sixes.
This suggests significant non-linearity in the R v.s. mean-temperature curve, a non-linearity that is probably relevant if used on the exterior side of the assembly, just as it is with most polyisocycanurate. A double-layer of the 30mm goods (60mm = 2.36") probably comes a bit less than the R8.07/inch of the 75mm foil faced samples, but it would be useful to see the curve plotted against temperature.
11.
Jan 25, 2018 2:02 PM ET
As Armondo mentioned...
by Sean Cotter
Is it proper to put the cellulose right to the underside sheathing in a cold climate? Would it have worked better to put damp/wet applied in place, cut it back to the rafters then do the foam?
12.
Jan 25, 2018 2:08 PM ET
Edited Jan 25, 2018 2:09 PM ET.
Response to Armando and Sean
by Martin Holladay
The installation of dense-packed insulation in contact with the underside of the roof sheathing does appear to be a code violation, although it's worth pointing out that a local code official has broad authority to allow methods that appear to violate the letter of the code.
I imagine that the homeowners and architect argued that slate roofing is vapor-permeable. Because of this fact, this code violation isn't as risky as it appears. The problem, of course, is that if the house is ever sold, the next owner of the home may decide to install asphalt shingles or a standing-seam roof. Once that happens, the risk of moisture accumulation in the roof sheathing (especially on the north side of the roof) increases significantly.
13.
Jan 25, 2018 2:51 PM ET
Edited Jan 25, 2018 2:54 PM ET.
Kingspan responds to R-value questions
by Martin Holladay
I just received an email from Peter Yost, who forwarded the following response from Kingspan: "Kooltherm R-value is lower at 25mm [1 inch]. Everything we are selling in the U.S. is thicker than that and R-value increases substantially after 25mm."
Intertek (a third-party lab) reports that the R-value at 75 mm (3 inches) is between R-7.93 and R-8.3 per inch, and I have no reason to doubt that report.
14.
Jan 25, 2018 6:51 PM ET
Not buying that non linear R value improvement
by Alan B
Polymers are made of repeating monomer units, tripling the thickness would triple the effect, not more, unless this is some kind of wonder material or has different properties when made thicker. If so make it thicker and trim thin to keep the higher R value at thinner values...
15.
Jan 25, 2018 7:12 PM ET
It seems plausible that the
by Michael Maines
It seems plausible that the faces of the material would have more resin and fewer bubbles, or some other mechanical difference due to the manufacturing process, affecting the R-value for thin samples.
16.
Jan 26, 2018 8:31 AM ET
Not convinced
by Alan B
I'm still not convinced, and if true then make thick sheets and trim and sell the higher R versions in the thin iterations, there would be a market for "premium thin" insulation for those who are stuck with certain assemblies.
Its not impossible for the data to be correct but one test from one lab giving hard to believe data is not easy to accept, they need to figure out why they get this result, replicate it elsewhere and prove this counter intuitive data. If its accurate it can be done.
17.
Jan 26, 2018 9:40 AM ET
R-Value and Temperature @ Alan B
by Rick Evans
Alan B, I don't think the insulation material in non-linear. Rather, it's performance (R- Value to Temperature) may be. Dana gave the example of poly-iso. Its R-Value decreases as the temperature drops. At zero degrees F, its R-value is probably around R2 or R3, per inch. But if you cover that Polyiso with another inch of polyiso, then the first inch of poly-iso is "warmed up" and will have a measurably higher R-value-(R4ish?
With Kool Therm, the outer inches must be warming up the inner inches of foam- boosting overall R value for thicker sheets. This must mean however, that the the inner inch has a REALLY high R-value to bring the total up to 8.2 per inch.
Is there a theoretical limit to R-value per inch? This inner layers must be around R-10/inch!!
18.
Jan 26, 2018 9:52 AM ET
re
by Keith Gustafson
Michael's thought seems plausible, in fact in thinking on it, one wonders why there isn't more variance in other materials, or perhaps they are only tested at one thickness
19.
Jan 26, 2018 10:01 AM ET
I do not believe polyiso is
by Keith Gustafson
I do not believe polyiso is at R2, ever
20.
Jan 26, 2018 10:10 AM ET
R-value testing
by Martin Holladay
When a third-party lab tests an insulation material to determine its R-value, the test procedure is ASTM C518, "Standard Test Method for Steady-State Thermal Transmission Properties by Means of the Heat Flow Meter Apparatus." This is a material test to determine the R-value of an insulation material.
The ASTM method requires testing at a mean temperature of 75°F, so cold-weather performance of polyiso is not an issue.
21.
Jan 26, 2018 10:12 AM ET
ASTM C518 allows testing at
by Michael Maines
ASTM C518 allows testing at various thicknesses, up to 250mm (about 10"), as long as the testers don't think edge losses will affect the result. They can test at a single thickness or at multiple thicknesses and fit a smooth curve between the points. So different foam manufacturers can use different thicknesses of foam for their advertised R-value. I believe that most rigid foams perform best in thinner samples, presumably because the gas cells are tighter at the edges, but it sounds like Kooltherm was likely tested at a thicker sample, so the unusual edge effect would have less of an impact.
It's certainly possible to have the faces of the material shaved down, but it adds to the material cost--it's much easier to take it straight from the die or mold.
22.
Jan 26, 2018 10:16 AM ET
A higher volume to surface
by Jon R
A higher volume to surface area ratio means less gas escapes. So better R/inch in thicker versions. Similar with facing.
23.
Jan 26, 2018 10:46 AM ET
Edited Jan 26, 2018 10:49 AM ET.
"Is there a theoretical limit
by Alan B
"Is there a theoretical limit to R-value per inch? This inner layers must be around R-10/inch!!"
Thats even less believable
Aerogel has an incredible R rating per inch, but its well tested, researched, explainable and proven (and very expensive and fragile).
24.
Jan 26, 2018 11:02 AM ET
A correction
by Martin Holladay
Michael Maines just emailed me, pointing out that testing insulation at a mean temperature of 75 degree F is not a requirement of ASTM C518. Michael is right. I stand corrected.
The reason that U.S. insulation manufacturers test at a mean temperature of 75 degrees F has nothing to do with ASTM C518. It is due to the fact that federal law makes it illegal to sell insulation labeled with R-values determined at a mean temperature other than 75 degrees F. The relevant statute is the Federal R-Value Rule (16 CFR Part 460, “Trade Regulation Rule Concerning the Labeling and Advertising of Home Insulation”). Here is a link to the relevant section:
https://www.law.cornell.edu/cfr/text/16/460.5
Here are the relevant paragraphs:
“460.5 R-value tests. … R-values given in labels, fact sheets, ads, or other promotional materials must be based on tests done under the methods listed below. They were designed by the American Society of Testing and Materials (ASTM). The test methods are:
(a) All types of insulation except aluminum foil must be tested with ASTM C 177-04, “Standard Test Method for Steady-State Heat Flux Measurements and Thermal Transmission Properties by Means of the Guarded-Hot-Plate Apparatus;” ASTM C 518-04, “Standard Test Method for Steady-State Thermal Transmission Properties by Means of the Heat Flow Meter Apparatus;” ASTM C 1363-97, “Standard Test Method for the Thermal Performance of Building Assemblies by Means of a Hot Box Apparatus” or ASTM C 1114-00, “Standard Test Method for Steady-State Thermal Transmission Properties by Means of the Thin-Heater Apparatus.” The tests must be done at a mean temperature of 75 [degrees] Fahrenheit and with a temperature differential of 50 [degrees] Fahrenheit plus or minus 10 degrees Fahrenheit. The tests must be done on the insulation material alone (excluding any airspace). R-values (“thermal resistance”) based upon heat flux measurements according to ASTM C 177-04 or ASTM C 518-04 must be reported only in accordance with the requirements and restrictions of ASTM C 1045-01, ‘Standard Practice for Calculating Thermal Transmission Properties from Steady-State Conditions.’ ”
Since this is a federal law, this is how American manufacturers test and report their R-values.
In the back of my mind, I know the source of this regulation, but somehow I referred to ASTM C518 instead of the R-value Rule. Thanks, Michael, for setting me straight.
25.
Jan 27, 2018 8:57 AM ET
Fire resistance
by Steve Young
Although the insulatio values are difficult to believe, I would like to address the fire resistance. Is it any better than other foil-faced polyiso foam? We all know the EPS and XPS are very flammable (just toss a piece on an open fire), but my very empirical test of polyiso form on the same fire only resulter in veey short period of flame, but that was only after being poked with a stick. Otherwise, I would suspect that it would have just sat there barely smoldering. In another incident, I know of a parked flatbed truck loaded with the foam being struct with lightening. Once again, it did not ignite. It did smolder, though.
26.
Jan 27, 2018 10:06 AM ET
Edited Jan 27, 2018 10:09 AM ET.
@ Steve
by Alan B
Thats a good point, i remember someone giving a demonstration of nanotherm (or insulate, whatever its called), and it consisted of a hot pot of water, half the side was covered with the nano(whatever) and half was bare metal and voila the covered half was not as hot (but still warm).
It was an effective if misleading demonstration, zero R of metal vs 0.25ishR of the product. There was no comparison to other coverings and any 0.25ishR equivalent covering would have performed exactly the same (some plastic or regular paint would probably do the job).
One of those miracle sponges on TV would go on about how it absorbed (X) times its weight in water. Exactly the same as any other sponge but they neglected to mention that part.
27.
Jan 29, 2018 7:25 AM ET
Edited Jan 29, 2018 7:26 AM ET.
does this roof assembly comply with code?
by Peter Yost
There is a long answer to this, which I will probably do in a separate blog--since how most recent codes treat roof assemblies is complex and inadequate from a building science perspective--but the short answer is yes: the current VT code, in the section for existing homes states (4.1.8): "Roofs without insulation in the cavity and where the sheathing or insulation is exposed during reroofing must be insulated either above or below the sheathing." This roof assembly complies.
Suggesting that unvented roof assemblies cannot or should not be designed to dry to the exterior is like suggesting that unvented wall assemblies can not or should not be designed to dry to the interior. If you manage wintertime condensation with an interior air barrier and interior vapor retarder along with drying to the exterior, that is high performance to me.
28.
Jan 29, 2018 7:35 AM ET
Edited Jan 29, 2018 7:56 AM ET.
Response to Peter Yost
by Martin Holladay
Peter,
Thanks for sharing that section of the code. However, I disagree with your conclusion. Just because the code requires that the contractor must install insulation either above or below the sheathing, doesn't mean that the contractor gets to install the insulation in a way that violates other sections of the code.
Here is a quote from the Vermont Energy Code Handbook:
"Unvented attic assemblies (spaces between the ceiling joists of the top story and the roof rafters) are permitted in one- and two-family homes and multiple single-family dwellings (townhouses) if all the following conditions are met: ...
"2. Air-permeable (e.g., fiberglass or cellulose) insulation only. In addition to the air-permeable insulation installed directly below the structural sheathing, rigid board sheet insulation must be installed directly above the structural roof sheathing as specified in Table R402.4.1.1 for condensation control.
"3. Air-impermeable and air-permeable insulation. The air-impermeable (e.g., spray foam) insulation must be applied in direct contact with the underside of the structural roof sheathing as specified in Table R402.4.1.1 for condensation control. The air-permeable (e.g., fiberglass or cellulose) insulation must be installed directly under the air-impermeable (e.g., spray foam) insulation."
In the 2015 Vermont Residential Building Energy Standards, the relevant requirements are listed in section 402.2.2.1. Here is the link (scroll down to see the section I'm talking about): 2015 Vermont Residential Building Energy Standards section 402.2.2.1.
29.
Jan 29, 2018 10:27 AM ET
Roof assembly
by Armando Cobo
I could live with the fact that a wall assembly can be designed to dry to the outside, and if as Joe says, a roof assembly is a wall assembly on an angle, why can a roof assebly dry to the outside, right?. Slate roof over bldg paper and sheathing are permeable, and the layers of taped and seal rigid foam wont let any interior moisture to the sheathing and outside, so it makes sense... but, has any research been done to show this assembly can work? I do look forward to your next blog. Thanks.
30.
Jan 29, 2018 10:38 AM ET
Edited Jan 29, 2018 10:44 AM ET.
Response to Armando Cobo
by Martin Holladay
Armando,
As I noted already in Comment #12, the argument can certainly be made that this roof assembly can dry to the exterior because the existing roofing is slate. The problem is that roofing is often replaced by homeowners, and new roofing (for example, asphalt shingles or standing-seam metal roofing, both of which are far more common in Vermont than slate) would immediately put the roof sheathing at risk, especially on the north side of the roof.
Maybe this roof needs several stainless-steel warning plaques, installed at the ridge and eaves, noting: "Warning! Roofers of the future! If this slate roofing is ever replaced with asphalt shingles, standing-seam metal roofing, or any type of vapor-impermeable roofing, this unvented cellulose-insulated roof assembly will accumulate moisture and fail!"
31.
Jan 29, 2018 10:57 AM ET
LOL
by Armando Cobo
Good points... I love the WARNING! signs idea... LOL
32.
Jan 30, 2018 9:29 AM ET
Warning signs
by Alan B
Indeed, i remember reading about the idea of houses coming with instruction manuals, if tailored to the house its a great plan. How to convince future owners to update what they have changed, not sure.
33.
Jan 30, 2018 1:08 PM ET
Harping on exterior cladding changes vs. interior wall finishes
by Peter Yost
Really, we are worried about the impact on drying potential when exterior claddings change when any building assembly designed to dry to the interior can change whenever a homeowner decides to change interior finish?
Very few of our high performance assemblies will not need high performance re-evaluation/supervision when either the exterior claddings or interior finishes are altered.
34.
Jan 30, 2018 1:11 PM ET
Conflicts built into the code
by Peter Yost
I respect your disagreement Martin, but frankly complying with both sections of the code would come down to the local building inspector reconciling. And for sure this is not the only instance when the code got the building science wrong or had incomplete and/or conflicting language in different sections.
35.
Jan 30, 2018 1:30 PM ET
Edited Jan 30, 2018 1:33 PM ET.
by Martin Holladay
Peter,
The title of your recent comment is "Conflicts built into the code," but I see no conflict.
The code you cited informs roofers that if sheathing or existing insulation is exposed in their reroofing work, the roofers must install insulation either below the sheathing or above the sheathing.
In the house described in this blog, there was no reroofing, so the code section you cite doesn't apply. According to your Comment #27, this section of the code only applies to projects "where the sheathing or insulation is exposed during reroofing."
Furthermore, even if this were a reroofing job -- it wasn't -- a roofer could comply with the cited code provision by installing rigid foam above the roof sheathing or spray foam below the roof sheathing. I have no idea why you think that this code section compels anyone to install dense-packed cellulose against the underside of the roof sheathing. It doesn't.
36.
Jan 30, 2018 2:53 PM ET
Edited Jan 30, 2018 3:11 PM ET.
Yes, polyiso can perform at R2/inch @ Keith Gustafson
by Dana Dorsett
Take a look at this graph:
http://www.greenbuildingadvisor.com/sites/default/files/Karagiozis%20-%2...
When the mean temperature (not the cold side temperature) through the foam is about -20C /-4F the conductivity of the foam is about 0.073W/mK or a bit over 0.5 BTU in /(hr ft2 F), which at 1" would be an R value of 1"/(0.5 BTU in /(hr ft2 F) ). The fact that it's a bit over 0.5 BTU in /(hr ft2 F) means it's actually a bit less than R2.
So, in your comfy-cozy 70F house when it's -78F outside, if polyiso is the only insulation layer that foam is really only doing ~R2/inch.
If it's an exterior sheathing application and the warm side of the polyiso is +25F, it hits R2/inch at "only" a toasty -30F outside.
For most of us, in most stackups, even at the 99% outside design temperature polyiso will be performing well above R2/inch. And the seasonal average will be higher still.
Looking at Karagiozis' curve it appears that his sample hit ~R6.7 at about 16C /61F through the foam, but only about R5.8 at the FTC mandated labeling test temperature (the blue vertical dotted line), which means it was almost certainly 2lb roofing foam, not the lighter higher-R foil faced stuff, so MAYBE 1lb foil faced polyiso won't quite make it all the way down to R2/inch @ -20C mean temp, but it'll be close.
Dow claims to have solved & fixed the polyiso derating puzzle with Thermax, but they don't share their proprietary solution, only the results:
http://msdssearch.dow.com/PublishedLiteratureDOWCOM/dh_098a/0901b8038098...
37.
Jan 31, 2018 3:05 PM ET
Availability
by MKCF
I've been waiting to get my hands on some of this stuff since August. The sales rep has been about the least useful person I've ever encountered. When is phenolic board insulation going to become readily available?
As a side note, here in CT there is a company that does spray foam phenolic. Not sure where that falls compared to Kingspan in terms of performance. but I can say it sure is expensive.
38.
Jan 31, 2018 7:03 PM ET
Edited Jan 31, 2018 7:12 PM ET.
Code compliance confusion, comment #28, etc
by Derek Roff
The wording in the quoted sections of the building code don’t paint a complete and unambiguous picture for me. Peter quotes a section stating that roofs "must be insulated either above or below the sheathing.” I’m guessing that this sentence is interpreted as “and/or”, rather than an exclusive “or”. That is, the insulation can be above AND/OR below the sheathing, rather than prohibiting any/every combination of interior and exterior insulation. I’m supposing the “and/or” interpretation, because a combination of exterior and interior insulation seems to be specified/required in paragraph 2 of Martin’s quote of the building code in comment #28.
Here is a portion of the code that Martin quotes. ""2. Air-permeable (e.g., fiberglass or cellulose) insulation only. In addition to the air-permeable insulation installed directly below the structural sheathing, rigid board sheet insulation must be installed directly above the structural roof sheathing as specified in Table R402.4.1.1 for condensation control.” As I read it, this item REQUIRES a combination of interior and exterior insulation in this configuration, whereas that would be prohibited if the “or” in Peter’s quote was an exclusive “or”.
The 2015 IRC IRC R806.5.1.3. code language quoted by Armando Cobo in comment 6 seems to prohibit the roofing configuration insulation scheme described by the architect/builder Eli Gould, as quoted by Peter. The "as built" description also seems in conflict with paragraph 3 of the code section quoted by Martin in comment #28.
39.
Jan 31, 2018 7:21 PM ET
Response to Derek Roff
by Martin Holladay
Derek,
The section of the code quoted by Peter Yost is irrelevant to this project. The code section he quoted only applies to re-roofing jobs. This was not a re-roofing job. The slate is still there.
40.
Feb 1, 2018 11:07 AM ET
re Dana
by Keith Gustafson
Not trying to push the point here, but, generally we are talking about buildings below the arctic circle, so yeah, 2 is pushing it. Also that particular graph seems to go further than other graphs on this website, even conflict.
http://www.greenbuildingadvisor.com/articles/dept/musings/cold-weather-p...
https://buildingscience.com/documents/information-sheets/info-502-temper...
still haven't seen a US cost on this material
It might be interesting since it need not be covered.
41.
Feb 8, 2018 12:11 PM ET
RE Reintroduction
by Jaccen
Of note may be why this product was previously discouraged in its use:
http://msdssearch.dow.com/PublishedLiteratureDOWCOM/dh_08ab/0901b803808a...
"Phenolic foam insulation was manufactured and sold into the North American market in the 1980’s
and early 90’s, mainly as roofing insulation. Claimed benefits were high insulation value and excellent fire resistance. High moisture absorption potential and residual acid present in the foam allegedly resulted in significant corrosion issues. Class action lawsuits were filed against corporations in the early 1990’s. Past litigation in North America focused on corrosion allegedly caused by phenolic foam used in metal deck roofing applications. The resultant roofing failures and subsequent litigation are still fresh in the minds of the building community. "
Installation on the exterior or in high humidity areas (ie. bathroom) may require consulting the manufacturer of whether it is advised or not.
42.
Apr 3, 2018 6:34 PM ET
availability?
by Yukon EMR Library (K-335)
Anyone seeing anything on availability of this product in North America? I don't see much on the web.
43.
Apr 11, 2018 7:21 PM ET
usable in basement?
by Jay
this product seems to be more similar to polyiso rather than eps or xps in terms of moisture absorption. can the foil faced phenolic product be used as a drop in replacement for polyiso on the interior side of an exterior concrete basement wall, followed by an empty stud wall and drywall?