Compartmentalization in Multifamily Buildings
In a large residential building, you don't want any air leaks between apartments
When a smoker who lives in an apartment building cracks a window, where does the smoke go? The smoker may be hoping that the smoke will go out the window — but in many cases, cracking a window simply allows exterior air to enter the apartment. This makes it easier for the smoke to travel to adjacent apartments.
Image Credit: All images: Sean Maxwell — Graphs: Steven Winter Associates
At some point in our lives, we’ve all been in an apartment building or a hotel and smelled cigarette smoke or cooking odors from a neighbor. Or maybe you’ve heard an argument (or other things) going on next door that you didn’t want to hear. Let’s face it: living in apartment buildings is not without annoyances.
Fortunately, there are simple ways to alleviate some of these problems: by sealing up the gaps in the walls between apartments. This is “compartmentalization.”
Many people still have the mistaken impression that air leakage is good for health. But when they say that “Yeah, sealing is good, but you don’t want to make it too tight,” what they are really saying is, “Don’t forget about air quality.” I agree — air quality is important. Moreover, research has shown the link between airtightness and ventilation performance. When I worked at Steven Winter Associates (SWA) in Connecticut, we found that ventilation systems work better with tighter apartments.
In this article, I’m going to lay out some of the arguments for compartmentalizing buildings. In an upcoming article, I’ll describe inexpensive ways to test a building to save energy, improve fire safety, and improve health, and I’ll discuss a proposed change to the International Energy Conservation Code.
Stack effect and ventilation
Building scientists have been talking for years about “stack effect” — the tendency of temperature differences between the inside and outside of tall buildings to create pressure differences and drive air infiltration. It’s one of the first concepts covered in building science courses, and it’s been in ASHRAE Fundamentals for a long time. We’ve heard over and over that dividing larger buildings into smaller airtight blocks by compartmentalizing cuts down on stack effect. The idea is that if you cut the vertical distance over which the driving forces of stack effect can act, then you can reduce the rate of infiltration.
But many benefits of compartmentalization don’t have anything to do with saving energy, at least not directly. Take the example of an apartment building. Speaking generally, well-sealed apartments inhibit the passage of secondhand smoke, smells, and other pollutants; reduce sound transmission; and impede the passage of pests and vermin between neighbors. They are also safer in a fire, because they help prevent the passage of hot gases that make fires spread and smoke that suffocates people.
In addition, compartmentalized apartments make buildings more resilient to changes in building operation. During research that I was involved in at SWA, studying buildings in New York City, we found many benefits of compartmentalized apartments, and a lot of the benefits had to do with controlling indoor air quality. In short, the better sealed your apartment is, the better it functions in real life.
Pressures in real buildings change all the time in response to changes in temperature, opening and closing windows and doors, changes in HVAC operation, and changes in wind and direction. With these changes in pressure come changes in how air flows into and out of apartments.
The most common ventilation strategy in multifamily buildings — constant exhaust from apartments, either centrally or individually — often doesn’t work like it’s supposed to. One reason is that central ventilation systems are often very poorly designed and constructed. Not enough thought goes into designing them, and often the registers are simply way bigger than they need to be. And not enough care goes into building ducts. They’re often extremely leaky, and most building codes don’t require testing of low-pressure exhaust ductwork. Both these issues lead to pressure loss, very poor balance, and sometimes vastly different airflow from apartments.
Exhaust-only ventilation may work just fine in single-family homes. The exhaust fans put the home under negative pressure, and as exhaust is pulled out, fresh makeup air comes in through gaps and cracks in the exterior envelope (ideally not from the attic or basement) and balances the flow. But in apartment buildings, SWA found that makeup air for exhaust-only systems is often more likely to come from your neighbor who smokes or from the hallway than it is from “clean” outside air. Furthermore, those flows may be reversed by any of the changes to the building pressure regime noted above.
Even supplying makeup air straight from identified sources faces difficulties. Supply air direct from a rooftop ERV/HRV must have well-designed, well-sealed ductwork, and it probably should have self-balancing dampers (for example, CAR damper by American Aldes). In-unit supply fans like the through-wall heat exchanger Lunos, and small fans fitted to fan-coil units or PTACs, must be powerful enough to overcome stack forces in all parts of the building at all times. In laboratory conditions, these fans may move the specified amount of air, but if you place them throughout a real building under winter conditions, with high positive pressure at the top of a building and negative pressure at the bottom, each fan must compete with a different pressure regime. The result is that some of the apartments get more fresh air than others.
The unwanted gift from your neighbor
By doing long-term monitoring of pressures in apartments, SWA was able to visualize which way the air moves in a building over time with several different ventilation systems. We also put sensors on windows and doors to know when they were opened. And in one building, we could see a major change in the pressure regime of a group of apartments when someone opened a window.
I often use the following example to illustrate what happens.
Suppose you live in an apartment building and your neighbor is a chain smoker. Being very considerate of others in the apartment, your neighbor opens the window with every cigarette and smokes next to it, blowing the smoke outside. The problem is, because your building is built with constant exhaust ventilation, when your neighbor opens the window, the forces described by building science conspire to distribute that smoke around the building.
When your smoking neighbor opens the window, the pressure in that apartment drops to virtually zero with respect to outside — the open window allows air to move in and out freely. But your apartment and the rest of the building is still under negative pressure because your windows are closed and the exhaust vents are still sucking. What happens to the neighbor’s smoke?
It gets pulled into the hallway, and into the other neighbors’ apartments, including yours, because the slight negative draw caused by the exhaust system in your apartment pulls it there. (See Image #1 at the top of the page.)
We know this happens because we can look at the pressure monitoring data from different buildings. In that building, on that floor, during that weather, with the windows in that particular configuration, air flows out of the neighbor’s apartment, into the hallway, and into yours. But why is it that you can only smell the smoke on some days? Because all those variables mentioned — windows, doors, HVAC operation, temperature, wind — are all changing all the time, and only sometimes do they line up to deliver that gift from your neighbor.
There are some options to help ensure that makeup air comes from intended sources, like passive vents in the exterior envelope. For example, trickle vents are small slotted vents often mounted in a window frame; they are common in the U.K., and some U.S. builders use them as a low-cost solution to providing makeup air. Other devices include small vents in through-wall HVAC systems and even engineered holes straight through the wall.
All these strategies rely on two usually false premises: that the vents are the largest hole in the apartment envelope, and therefore the most likely path for makeup air; and that the apartment is reliably under negative pressure. Unfortunately, this is almost never true, at least not for all parts of the building at the same time. Passive vents, which ultimately are simply expensive holes in the wall, are often dwarfed by the size and number of other possible leakage pathways in the apartment, most obviously gaps and cracks around the door to the hallway. Check Martin Holladay’s article that nicely sums up the research that we did (“Passive Air Inlets Usually Don’t Work”).
In order to make sure that makeup air comes from only where we want it to in an exhaust-only building, SWA research found that many apartments would probably need to be sealed to less than 0.1 CFM50 per square foot of enclosure (0.51 L/s @50Pa per m2). For a one-bedroom apartment, that might be 80 CFM50 (38 L/s @50Pa) total, including leakage from the apartment door. In case you don’t have any point of reference, that’s insanely tight and not likely to be achieved without some help from a magic bullet.
Still, you can see the difference in the measured pressure response of two apartments sealed to different levels. I’ll greatly simplify here, but the first apartment (see the graph directly below) was sealed very tight, while the second apartment was sealed only moderately well.
The pressures in the tight apartment fluctuate with operation of fans, opening of trickle vents, etc., while the pressures in the leaky apartment (see the graph below) can hardly be manipulated. In other words, the tight apartment allows you to gain supremacy over the pressure so that you can control where the air comes and goes. The leaky apartment? It’s as unpredictable as the wind.
Old Mrs. McGillicuddy
Airflow patterns in most buildings are much more dependent on the weather than any of us would like to admit. Old buildings with no ventilation system at all are subject to this cruel reality even more than new buildings with ventilation systems, because people in old buildings use “double-hung thermostats” (a.k.a. windows) to get fresh air and control the heat.
Andy Padian, the guy who hired me at SWA, used to tell the story of old Mrs. McGillicuddy, who lives on the first floor of an equally old apartment building in New York City. One night during a snowstorm, this building is toasty warm, even overheated, which is common for New York buildings. That’s just fine with old Mrs. McGillicuddy, who’s always cold. But the residents on the top floor are so hot they are about to pass out, so they open the windows for relief. This is opening the flood gates for the chimney effect. Relief does come to the top floor — not through the open window, but through the gap around the hallway door. Air rushes up from the lower floors and floods into the top-floor apartments, cooling them off. Much better.
But poor Mrs. McGillicuddy on the first floor begins to suffer because the makeup air for that upward draft comes through the gaps and cracks in her walls and windows. She gets cold, rings up the building superintendent, and screams at him to turn up the heat, gosh darn it. He begrudgingly obliges, not wanting to feel her wrath any more tonight, and the whole building gets hotter. Thus, the cycle continues and the heating bill skyrockets.
Two things are at play here: one is heating system imbalance, which we all know is bad. The other is that apartments are far too well-connected to each other and the common spaces.
Occupants are unpredictable
I have to admit that the data that we got from our research was sometimes messy. The hard thing about doing research in occupied buildings is that they contain occupants; and occupants, no matter how much you instruct them to not touch your sensors or open the windows, will do whatever they please.
But to me this was instructive. We had a hard time figuring out which way the air was flowing in the building because people were always opening doors and windows and messing it up! A true working ventilation system in a multi-unit building must be able to deal with this. Herein lies the lesson.
Let them open the windows! Let them control the heat! If they are too hot, give them a thermostat in every room to shut off the heat. If they need fresh air, let them open the window. If you want to save energy, put a sensor on the window that reduces the heat when the window is open.
There is quite a lot of wisdom in unitizing HVAC systems and controls. Ductless minisplit systems are a great example of this. In fact, many experts believe that individual electric systems will be the way of the future in a post-fossil-fuel world. But you can’t really count apartments as unitized until you seal them from each other.
Sean Maxwell formerly worked as a senior energy consultant at Steven Winter Associates in Norwalk, Connecticut. He now lives in Australia.
6 Comments
  1. Katy_Hollbacher | | #1
    Great read for multifamily developers!
    Thank you for this topic--very well put and explained, am hopeful it will help our multifamily clients understand the importance of compartmentalization.
    I have been in strong support of the compartmentalization prerequisites of LEED Midrise (.30 CFM50/sf) and ENERGY STAR Highrise (.22) in thinking they were setting a reasonably high and very important bar--but I'm shocked by the relatively poor performance of the "Apartment Sealed to .27 CFM50/sf" in your case study discussed above. Given these results, should we be setting the bar much higher, like .1 CFM50/sf as you mentioned above?
  2. user-4739854 | | #2
    Party Wall Gets Short Shrift
    Sean,
    Your article was timely - thank you - and confirms what we observe in the field too; air tight envelopes are less susceptible to Environmental Tobacco Smoke (ETS). I was recently ask to diagnose ETS pathways and make recommendations on remediation for an detached and also a semi-detached house.
    In a nutshell, there's no downside to making an dwelling airtight if there's a balanced ventilation system running - unfortunately, it's usually suck-only ventilation. I'm wondering if you ever used pressure to prevent infiltration from adjacent units? We wrestle with recommending pressurization of units, but then you have to tap a clean air source and we run the risk of forcing conditioned air through the envelope causing condensation. Like I said if it's air tight to begin with, you stand a fighting chance. We strongly advocate air sealing and testing all buildings and our advice to any semi-detached home owner is to air seal the party wall when doing a gut-reno; you never know who's going to move in next door.
    I joked with both victim home owners that it might actually be cheaper to get the offending neighbor hooked on e-vape cigarettes...
  3. BobConnor | | #3
    Disney Contemporary Resort an example?
    The idea of sealing apartment off from each other, might the Disney Contemporary Resort be like that? The frame of the building was built first, then the rooms were assembled off site and then placed into the frame like drawers into a chest. Maybe if apartments were built like that it might be possible to isolate the individual apartments, maybe each with its own HRV. Though I found out that the CR has settled over the years, sealing in the individual rooms and the place probably leaks terribly because Disney charges so much, why do they have to save energy at all?
  4. GBA Editor
    Martin Holladay | | #4
    Response to Robert Connor
    Robert,
    Just because a builder uses modular construction techniques, doesn't mean that the builder understands the importance of air sealing. To continue your "drawers in a dresser" analogy: If each of the drawers is leaky, and if the electrician drills a bunch of holes in the sides of the drawers, than you don't have compartmentalization.
  5. BobConnor | | #5
    But maybe it could work
    Martin, why be so negative? After all, it might be possible to build the rooms in a factory like they do with mobile homes and the electrician and the plumber can do all the drilling then before the unit is sealed up and then just have the connections for plumbing and electric as one connection and have that sealed, an idea like this could work. I don't know why anyone today has not tried to do something like that. It could be done well sealed, probably easier than if site built.
    Then again, I understand why should a landlord renting out apartments care about energy consumption? After all, the tenants pay for the energy, so why spend money for more insulation? What incentive is there for the builder? Just like why should Disney save energy, because after all their guest pay for their utilities and people who can afford $400 a night room don't care how much they should keep the light on.
    Of course, back in 1971, builders did not care about energy and Disney was in a hurry to open the Magic Kingdom so I am sure the Contemporary resort leaks a lot. Worse yet, on our last trip, I went to the California Grill on top of the building and there is what amounts to a big bonfire under a huge hood to cook their fancy steaks, The exhaust fan has to be huge, so the stack effect must really be strong. Some of the Polynesian resort was built like that too but when that was expanded, Disney chose conventional construction, as they have with all later resorts.
  6. GBA Editor
    Martin Holladay | | #6
    Robert,
    You wrote, "But maybe it [the modular construction approach] could work." I agree with you; I never said it couldn't.
    One company that has proven that the modular construction approach "could work" is Unity Homes of Walpole, N.H. Stay tuned: next Friday's blog will be a report from a Unity Homes job site.