QA-spotlightheader image
0 Helpful?
Can Bathroom Fans Be Used to Distribute Heat?
An owner-builder looks for a simple way of getting heat to the bedrooms in a one-story house
Posted on Oct 16 2017 by Scott Gibson
Debra's new house in southwestern Virginia will be a one-story design of 1,344 square feet with half the space devoted to a single, open room and the remaining area divided into two bedrooms, two baths, and a utility room. The main source of heat will be in the open room, and in the absence of a conventional forced air heating system, Debra's quandary is how to distribute the heat evenly.
Heating loads for this Climate Zone 4A house are relatively modest — about 14,000 BtuBritish thermal unit, the amount of heat required to raise one pound of water (about a pint) one degree Fahrenheit in temperature—about the heat content of one wooden kitchen match. One Btu is equivalent to 0.293 watt-hours or 1,055 joules. per hour. Between small baseboard heaters and leaving doors open, the bathrooms and utility room should have enough heat. It's getting heat to the bedrooms that's looking more problematic.
In a post at the Q&A forum, Debra wonders whether low-output bathroom fans can be used for heat distribution.
"We are interested in using a couple of Panasonic bathroom fans to send warm air from the main room to each bedroom, using 6-inch metal ducts going straight about 15 feet (within the building envelopeExterior components of a house that provide protection from colder (and warmer) outdoor temperatures and precipitation; includes the house foundation, framed exterior walls, roof or ceiling, and insulation, and air sealing materials.)," she writes. "The fans have adjustable speeds, and at the highest speed of 150 cfm they could change over the air in each bedroom in just 7 minutes (which might be too much).
"Seems like that could do a fairly decent job of evening out the heat between the main room and the bedrooms," she continues. "I don't care if the bedrooms are a few degrees cooler, though."
This simplified heat distribution system would let Debra skip baseboard heaters and programmable thermostats for the bedrooms. But will it work?
That's the topic for this Q&A Spotlight.
Sorry, the plan won't work
GBAGreenBuildingAdvisor.com senior editor Martin Holladay gives Debra two reasons why this is not a good idea.
"The first relevant factor is the specific heat of air, which is relatively low. In other words, a cubic foot of air can't hold much heat," Holladay writes. "The specific heat of air is 0.0182 Btu/cf/°F.
"The amount of heat that a fan can move is calculated using this formula:
"Heating BTUs = (cfm of the fan) x (delta-TDifference in temperature across a divider; often used to refer to the difference between indoor and outdoor temperatures.) x 1.08
"It isn't much."
There's another reason, he adds, and that's the relatively low delta-T (the difference in air temperature between the main room and the bedrooms). Holladay explains it this way:
"It's really hard to raise the temperature of a 65°F room using 72°F air. It's a lot easier to do that with a furnace, because the furnace has access to 150°F or 160°F air." Plus, a furnace would have a much more powerful fan, one capable of moving 800 cfm, not the 150 cfm that's possible with a bathroom fan.
"The bottom line: Install a ductless minisplit in the main living area," Holladay says. "Your bedrooms will probably be comfortable if your house has a good thermal envelope, and if your bedroom windows aren't very big. If you are worried, install a small electric heater in each bedroom. You probably won't need to turn on the electric heater very often, if at all."
Still, the fans would help
Holladay's formula suggests to Debra that bathroom fans, while maybe not a perfect solution, would certainly help. She thinks they could provide at least half the heat the bedrooms would need when doors are closed at night ("one of us snores loudly," she explains).
"So, the fans would reduce how cold the rooms will get," she says. "And the baseboard heaters would supplement that, if needed. I might not mind bedroom temperatures down to 60°F."
"We'll leave the bedroom doors open during the day," she says. "We can't afford a second minisplit for the bedrooms, but are seriously considering using one for the main living area."
Jon R adds that a 150 cfm fan will move about one-half the heat provided by an open door. If Debra does decide to use fans, he suggests installing them in pairs — one for supply and one for exhaust.
Could bath fans help keep air fresher?
If using low-volume bathroom fans won't solve the heat distribution problem, Bill Dietze wonders, wouldn't they at least help keep air in the bedrooms seem fresher?
"If the doors were shut at night or a teenager wanted the door shut all the time, then it seems to me that an extra 30 to 50 cfm per bedroom might be nice," he writes.
If fresh air is the goal, Holladay replies, the best approach would be a mechanical ventilation system — ideally a balanced system that both exhausts stale air and blows in fresh air from the outside. Either a heat recovery or energy recovery ventilator would work.
"If you have odors," he says, "the idea is to remove stale air from the smelly rooms, and introduce some fresh outdoor air."
The ducted minisplit solution
Given Debra's estimated heating loads, Dana Dorsett suggests a 1.5-ton Fujitsu Halcyon would work, or possibly even the smaller 1-ton unit.
Unlike a wall-mounted ductless minisplit head, a ducted minisplit distributes conditioned air to nearby spaces via a fan and dedicated ducts. But the units are not nearly as powerful as a conventional air handler, and duct layout is crucial.
"The layout matters, and don't put the ducts up in an unconditioned attic," Dorsett says. "The miniduct cassette need not be placed in the utility room. They're pretty small, and can be installed in the ceiling of a closet or in a small drop-down soffit, but it has to be planned for. Unlike their competitors, the Fujitsu units can be mounted vertically in a small side-compartment to a closet or wall, making access for maintenance and service pretty easy.
"These things aren't nearly as powerful as bigger-deal air handlers, and these systems take some amount of careful design and installation competence, but it seems like the 'right' solution to your house," Dorsett adds. "Mounting it somewhat central to the house with very short duct runs helps. Doing the traditional duct-designer's approach of running the ducts all the way to the exterior walls placing the register under/over a window probably won't work."
A vertically mounted ducted unit was described in a similar thread last year by John Semmelhack, Dorsett notes. In that thread, Dorsett cautioned that finding an HVAC(Heating, ventilation, and air conditioning). Collectively, the mechanical systems that heat, ventilate, and cool a building. installer who could design ducts for such a system might prove tough.
In Debra's case, Dorsett says that assuming heating loads in the rooms that will be closed off from the rest of the house are very low, they could still be kept comfortable with the heat provided by a wall-mounted minisplit in the main area. "But," he adds, "that usually involves limiting the window sizing in the bedrooms and using triple-pane glazingWhen referring to windows or doors, the transparent or translucent layer that transmits light. High-performance glazing may include multiple layers of glass or plastic, low-e coatings, and low-conductivity gas fill. in those rooms."
Where to run the ducts
Semmelhack agrees that a Fujitsu system would be a good fit for Debra's new house, as long as the air handler and the ducts are located entirely within a conditioned spaceInsulated, air-sealed part of a building that is actively heated and/or cooled for occupant comfort. . He could imagine several ways of accomplishing this in a one-story house in Virginia, including putting the equipment in a conditioned crawl space.
Debra is planning on a vented attic and a conditioned crawl space, but she doesn't think that putting any equipment in the space below the house is a good idea.
"I'll have a vented attic, and a closed conditioned crawl space," she writes. "But I'm a bit concerned about installing the air handler even in a conditioned crawl space, as I'm rather hyper reactive to mold and still paranoid about exposure to crawl spaces. That's one reason I'm considering installing the interior fans, to help circulate the bedroom air back to the main room for conditioning and dehumidifying."
A dropped ceiling in a 15-foot-long interior hallway might provide enough room for the equipment, she says, but it would require 8-foot duct runs to reach both the bedrooms and the main living area. "Not exactly very short runs," she says.
That's a question a Manual D calculation would answer, Jon R replies, although he imagines that the Fujitsu could handle duct runs much longer than what Debra is considering.
Our expert's opinion
GBA technical director Peter Yost adds this:
I wish I could say I have a conclusive answer to this question: Can you use exhaust fans to create adequate distribution and mixing in bedrooms that are not served by a central ducted system?
My own perspective: By the time you purchase two quality fans that are quiet enough, energy-efficient enough, and easily adjusted, you might as well go with a dropped-soffit, ducted hallway solution. Additionally, we need to let go of concerns around installing equipment in properly detailed, conditioned crawls and attics; it’s an irrational bias based on our history of thoroughly confused and dysfunctional “vented” crawls and attics.
But I am no HVAC expert, so as I usually do, I checked in with, first, a local HVAC expert — Mark Russwick of ARC Mechanical and then with someone I respect who has actually deployed this type of distribution solution — Carl Seville at SK Collaborative.
First, Mark Russwick:
“I’m not a fan, no pun intended, [but] will this work in Virginia? Yes, most likely, but the bedrooms are slaves to whatever is happening in the main room and I find bath fans noisy. It’s too bad that someone doesn’t make a single-zone, down-flow air handler, heat pumpHeating and cooling system in which specialized refrigerant fluid in a sealed system is alternately evaporated and condensed, changing its state from liquid to vapor by altering its pressure; this phase change allows heat to be transferred into or out of the house. See air-source heat pump and ground-source heat pump. split system.”
Second, Carl Seville (based on comment #18 in the original Q&A thread and this GBA blog of Carl’s):
“It works quite well. When there are no guests we leave all upstairs bedrooms doors open and the [minisplit] head in the hallway conditions the upstairs fine including the master suite — we don't even turn on the head in the master under those conditions.
"When we have guests and close the bedroom doors, we use a 190 cfm exhaust fan located above the hallway minisplit that is ducted into the two front bedrooms. It is on a relay that turns it on whenever the minisplit is on with an override switch that allows us to turn if off when we don't want to use it. (We keep it off most of the time.) We will also turn on master bedroom head as well when doors are closed.
"The front bedrooms have jumper ducts to the hallway to equalize pressure when the doors are closed and the fan is running. We have found that without the fan, the bedrooms will be noticeably warmer or cooler or more humid than the rest of the house if doors are closed. This summer my wife was ironing in one room with the door closed and the fan off and it was about 10 degrees hotter than the rest of the house. With that tight an envelope (0.88 ach50) even an iron can heat up a room.”
My parting perspective: Carl’s home, its performance, and the configuration of his exhaust fan solution all are significantly more honed than the dual exhaust fan approach that Debra is proposing. Carl’s solution isn't really evidence that contradicts my or Mark’s concerns; rather, I think it supports the need for a more sophisticated approach.
Tags: , , , ,
Image Credits:
  1. John Semmelback
1.
Oct 16, 2017 10:06 PM ET
Active systems
by Malcolm Taylor
Carl's system sounds like it works for Carl - who like many denizens of GBA has an intense interest in his house. Most people don't. If the only way to effectively equalize the temperatures is through an active system that needs the inhabitants to monkey with the controls depending on who is home or what the weather is like, it generally won't get used.
2.
Oct 17, 2017 8:38 AM ET
Response to Malcolm Taylor
by Martin Holladay
Malcolm,
There are lots of off-grid houses and active solar houses from the 1970s that have secret valves, secret dampers, and secret switches. The owner-builder makes all kind of seasonal adjustments, and knows exactly what to do.
When the owner-builder has to go away on a business trip, he has to show his spouse a three-ring binder full of instructions. "If the monitor on the living room wall shows 17.4, go to the basement and open the valve with the red handle near the south window."
If you've got a house with this kind of manual, your house is too complicated. Ask me how I know.
3.
Oct 17, 2017 2:23 PM ET
My House
by Carl Seville
Malcom - My house doesn't require any special actions - if the person living here wanted to leave the fan in the on position - it would distribute air into the bedrooms whenever the mini split turns on. I choose to keep it turned off as I don't need it when the doors are open. That is the only option available - no detailed operation instructions other than how to use the thermostats, which can be set to auto switchover from heat to cooling. I choose to fiddle with things, but if someone in this house chose to never touch a control, the house would operate just fine, albeit probably use a bit more energy that I choose to.
4.
Oct 17, 2017 3:37 PM ET
Carl
by Malcolm Taylor
"I choose to fiddle with things, but if someone in this house chose to never touch a control, the house would operate just fine"
A perfect combination then. Room for the enthusiast and the laymen too. I took you description as describing what was necessary, as opposed to what you do because you enjoy tinkering.
Martin's "secret valves" reminds me not only of those early 70's house though, but also the new smart-function enabled ones. The only difference is you can tinker at a distance.
5.
Oct 18, 2017 11:46 AM ET
Too little emphasis on the building enclosure
by Li Ling
Bath fans are one side of the heat transfer battle that takes place in indirectly-heated parts of the house: how fast does the heat make its way there versus how fast does the heat get lost to the outside. (Obviously applicable to cooling and dehumidification energy - I'm writing from the North.) Slow heat loss to the outside and the bedrooms could easily stay at 60 deg and above. I think humidity is a bigger deal, so a great building enclosure AND some air circulation into those rooms sounds like a winner.
As an aside, in our -11 deg design load climate we have homes with just a mini-split in the living room. A ventilation system that also circulates air within the house delivers about 20 cfm to the bedrooms, and they stay within 3 degrees of the main body of the house.
6.
Oct 18, 2017 6:13 PM ET
Another way to look at it.
by Kevin Camfield
I'm almost afraid to do the math here as there is a good chance of me messing it up somewhere along the line, but here goes.
Debra's house sounds very similar to the one we are designing in terms of heat load. Both are in zone 4 and both have a peak load of about 10 btu/hr per square foot of living space. The heat load calculations on our house (passive house software) also show an across the year average head load of only about 1 btu/hr/sq.ft.
Using Martin's equation a 100 cfm fan can move 108 btu/hr of heat with a 1 degree delta T. So on a temperate day a 100 cfm fan should be able to keep a 100 sq. ft. room in our zone 4 houses within 1 degree of the room it is drawing air from. On the coldest day of the year that same room would be 9 degrees cooler. This of course assumes a lot of things including that the bedrooms have the same average heat loss as the rest of the house.
If one uses an efficient, 100 cfm fan at say 10 cfm/watt and runs it continuously it will consume the equivalent energy of about 35 btus/hr. Assuming a COP of 2.5, it costs the equivalent of 45 btus/hr for the heat pump to produce 108 btu/hr of heat. So conceivably the total power consumption would be 80 btus/hr for 108 btus/hr of heat. An inexpensive, small flush mounted electric heater could produce that same heat using the equivalent of 108 btus/hr. That difference of 28 btus/hr would only cost $7 per year at our electric rates of $0.10/kwh. It seems like the simpler system would function better at a lower installed cost and a very small up-charge in operating cost.
We are looking at using the horizontal ducted units in our house based on Dana's recommendations, working through cost and ducting now. It is hard to get anyone to do the ducting design. The HVAC contractors I have talked to just want to come to the job site after the house is built.
7.
Oct 19, 2017 11:44 PM ET
Debra doesn't mention cooling...
by David Butler
In Z4A Virgina, how does this house not have an actionable cooling load? You can sometimes get away with indirect heat distribution in cold (heat-only) climates because folks are more tolerant or even prefer lower temps in bedrooms. But when you have a cooling load, especially in bedrooms, you gotta deliver supply air to where the load is. A ducted mini would seem to be the best solution, based on the information provided.
With metal ducts, length isn't much of an issue, which is why it's misleading to say a ducted mini can only handle x feet of duct. It's the elbows and other fittings that disrupt airflow. The Fujitsu ducted mini can handle a whole house with a carefully thought-out layout.
Among the small models (1.5 tons and under), Daiken has the least powerful blower (0.12 IWC), followed by Mitsubishi (0.20 IWC), whereas the Fujitsu can handle 0.35 IWC external static, more than enough for a well-designed metal duct system.
For a hallway drop ceiling scenario, my preference is a fabricated 'extended plenum' reduction trunk with curved branch take-offs, where the branch duct serves as the boot for over-the-door supply registers. Thus no elbows. On the return side, in lieu of factory filter, I specify an over-sized filter box at the butt end of the blower with filter sized to about 175 cfm/ft2.
I find the biggest challenge is meeting the required left-side service access clearance. Most halls aren't wide enough for unit width plus side clearance. However, if there's an adjacent laundry or closet on the left side of the hall, you can shift the unit all the way to that side and put a drop ceiling and access panel on the immediate other side of the wall.
8.
Oct 20, 2017 7:51 PM ET
No local Fujitsu contractor
by Debra
Our home (the one under discussion here) will be located in the mountains of SW Virginia, which is considerably cooler than most of the rest of the state. But the summer humidity levels still make some amount of AC desirable (and/or a small dehumidifier - though I hate the noise level of those).
Our sensible cooling load is about 9600 and latent cooling load around 2300 (depending on how much ventilation we are using). I usually tolerate the heat relatively OK, but hate the sticky humidity levels.
Unfortunately, there are no authorized Fujitsu contractors anywhere near us, as we are far from any cities. So that doesn't look like a feasible option.
9.
Oct 20, 2017 9:58 PM ET
then consider the obvious...
by David Butler
I agree 100% with Peter Yost's sentiment, that not wanting to install HVAC in a sealed crawl is "an irrational bias based on our history of thoroughly confused and dysfunctional vented crawls and attics." In fact, to the extent that your crawl could still be at risk for mildew or mold, installing a conventional ducted system down there, with a small supply vent, would further reduce the risk.
Regarding Fujitsu... unless Fujitsu has changed it's policy, any contractor can sell and install Fujitsu systems. The 'authorized contractor' designation is simply a way to steer prospective customers to contractors who make a commitment.
10.
Oct 26, 2017 2:20 PM ET
David's Comments
by Kevin Camfield
David,
We are planning to use Fujitsu horizontal ducted units because they are a little more efficient, but mainly because of the stronger distribution fans. I'm having a hard time figuring out where to position the units and how to run the ducting before the house is built (when I can still make adjustments to the framing cheaply). Your comments on placement and access were helpful.
Since I can't seem to find an HVAC contractor who wants to engage on the topic of planning the layout and ducting, would you be able to point me to information available to help me plan the system myself? Placement of the units will mostly be above lowered ceilings in closet areas with the ducting running either in conditioned attic space, between floor joists, or in wall cavities. The conditioned attic area is shallow space between the lower and upper cords of scissor trusses. The top cord with a 5:12 pitch and the lower with a 2.5:12 pitch. I have from 6" to about 30" to work with up there. The floor joists are 11 1/2" I-joists.
Any pointers or recommended sources of information would be appreciated, from David or from others.
Become a GBA PRO!