Can Cellulose be Used in an Unvented Roof?
Without ridge or soffit vents, the concern is moisture accumulation
Blowing cellulose into rafter bays:
A question from a Portand, Maine, homeowner kicks off a discussion about whether dense-packed cellulose insulation can be used successfully in an unvented roof assembly.Dean Manoogian has a Cape Cod style house in Portland, Maine, and is puzzling over the best way to retrofit the roof with rigid foam insulation.
Working with both an insulation company and a roofing contractor, Manoogian has come up with a plan: apply 2-in. rigid foam on the interior of the dormered roof and then fill the rafter bays with dense-packed cellulose.
“My question,” he writes in this Q&A post at GreenBuildingAdvisor, “is the air/moisture permeability against the roof sheathingMaterial, usually plywood or oriented strand board (OSB), but sometimes wooden boards, installed on the exterior of wall studs, rafters, or roof trusses; siding or roofing installed on the sheathing—sometimes over strapping to create a rainscreen. /rafters.”
The roof has been built without ridge, soffit or gable vents. To protect the sheathing and rafters from moist air, mold, and possible decay, Manoogian proposes covering the underside of the roof sheathing and rafters with a peel-and-stick membrane before adding the foam and cellulose.
The rigid foam would be capped with 5/8-in. gypsum wallboard to meet fire codes.
Is Manoogian on the right track, or courting a problem? That’s the focus of this week’s Q&A Spotlight.
Not the most elegant solution
The plan has already won the city’s approval, but to GBAGreenBuildingAdvisor.com senior editor Martin Holladay, it has its drawbacks.
“No,” Holladay writes, “you can't solve the problem by adhering Ice & Water Shield to the underside of your roof sheathing and your rafters, for several reasons: the materials would be expensive, the work would be awkward, it's impossible to do a perfect job, and you would be creating a vapor-barrier sandwich with roof sheathing in the middle — a disastrous approach if you ever get a roof leak.”
RELATED MULTIMEDIA
Video: Lstiburek's Rules for Venting Roofs
RELATED ARTICLES
How to Install Cellulose Insulation
Forget About Vapor Diffusion, Stop Air Leaks!
There are only two reliable ways of keeping water vapor away from the roof assembly, says Holladay. One way is to spray closed-cell polyurethane foam on the underside of the roof sheathing. The second way is to install soffit vents, ridge vents, and ventilation baffles in each rafter bay, in order to vent the underside of the roof sheathing.
Because the roof has already been constructed, he adds, Manoogian may be forced to go ahead with his plan to install dense-packed cellulose in unvented rafter bays. But it’s not an approach that Holladay would recommend to other GBA readers.
No wait, it will work
Maine builder Dan Kolbert disagrees. “We have done many dense-packed unventilated roofs without incident (that we know of, at least),” he says. “It is indeed a controversial topic these days.”
Kolbert has discussed the issue with Bill Hulstrunk, the technical rep for National Fiber, a cellulose supplier based in Massachusetts, and while Hulstrunk comes from inside the industry he’s also seen more New England cellulose projects than anyone Kolbert knows and has a “vested interest” in their success.
“The short version is he hasn't seen any problems with well-installed insulation,” Kolbert says. “The full ice & water job on the roof is a bit of a drag, but I think you should be OK. And I too have had local code officers sign off on ‘hot’ roofs.”
Let it dry to the interior
Hulstrunk is next to weigh in, and he emphasizes two things: the roof assembly must be able to dry to the interior, and the density of the installed cellulose is crucial.
He recommends one of several rigid foam products that will allow moisture in the roof assembly to dissipate, including glass-faced polyisoPolyisocyanurate foam is usually sold with aluminum foil facings. With an R-value of 6 to 6.5 per inch, it is the best insulator and most expensive of the three types of rigid foam. Foil-faced polyisocyanurate is almost impermeable to water vapor; a 1-in.-thick foil-faced board has a permeance of 0.05 perm. While polyisocyanurate was formerly manufactured using HCFCs as blowing agents, U.S. manufacturers have now switched to pentane. Pentane does not damage the earth’s ozone layer, although it may contribute to smog. board, expanded polystyrene (EPSExpanded polystyrene. Type of rigid foam insulation that, unlike extruded polystyrene (XPS), does not contain ozone-depleting HCFCs. EPS frequently has a high recycled content. Its vapor permeability is higher and its R-value lower than XPS insulation. EPS insulation is classified by type: Type I is lowest in density and strength and Type X is highest.) and extruded polystyrene (XPSExtruded polystyrene. Highly insulating, water-resistant rigid foam insulation that is widely used above and below grade, such as on exterior walls and underneath concrete floor slabs. In North America, XPS is made with ozone-depleting HCFC-142b. XPS has higher density and R-value and lower vapor permeability than EPS rigid insulation.).
Avoid using a polyethylene vapor barrier, foil-faced polyios board or Ice & Water Shield on the interior, he says, because they will not allow the passage of moisture to the inside and “create the self-composting double vapor barrier situation.”
As important is the density of the cellulose. “The cellulose installed in enclosed building cavities including non-vented roof assemblies need to be dense packed at a density of 3.5 lbs/cu. ft. for a 2x6 increasing to about 4.0 lbs/cu. ft. for a 12 inch cavity to become self supporting and will not settle over time,” Hulstrunk says. “Cellulose loose blown in a flat attic will have some settling over time down to its settled density of about 1.4 lbs/cu. ft. These flat attics will need to be ventilated to the outside to prevent diffusional moisture from condensing on the underside of the roof.”
He adds that in buildings where the roof assembly will dry to the inside, the indoor relative humidity should be no higher than 50% during cooler months. That can be accomplished with either a heat-recovery or energy-recovery ventilator(ERV). The part of a balanced ventilation system that captures water vapor and heat from one airstream to condition another. In cold climates, water vapor captured from the outgoing airstream by ERVs can humidify incoming air. In hot-humid climates, ERVs can help maintain (but not reduce) the interior relative humidity as outside air is conditioned by the ERV. or even a continuous-duty bathroom fan on a timer.
“Although we would prefer having your non-vented roof assembly dry towards the exterior or even better yet be able to dry in both directions, there are thousands of examples of durable roof assemblies filled with cellulose that dry only towards the interior,” he adds. “We have eliminated the need for Ice and Water Shield products by insulating roof assemblies with insulation products that actually work.”
Our expert’s opinion
Peter Yost, GBA's technical director, added this:
While I agree with Hulstrunk that using a vapor permeable rigid insulation with dense-packed cellulose in the roof framing assembly will allow “everything” to the interior of the membrane to dry to the interior, I have two cautions:
- All building assemblies — but particularly “hot” roofs — require a dedicated, comprehensive air barrier. Dense-packed cellulose, while less air permeable than other loose insulation, is NOT airtight enough to qualify as the dedicated air barrier. Be sure that the rigid insulation used on the interior is air sealed to become a dedicated continuous air barrier. “Hot roofs” that are not fastidiously air sealed, particularly at the eaves, can fail.
- I find it hard to imagine how tedious and expensive it would be to wrap all of the framing and underside of the roof sheathing with peel-and-stick membrane. Since the roofing is vapor-impermeable and not back-vented — and since most of the roof sheathing has peel-and-stick membrane on the top side — the roof sheathing and framing would be encased between two vapor-impermeable membranes, with no drying potential at all.
Much to my surprise, when I was unable to find any vapor permeability information on three-tab asphalt shingles and I asked John Straube of Building Science Corp. what he used for their vapor permeability, he stated, “vapor impermeable.” What?
While the shingles themselves may be vapor impermeable, I felt sure that their installation would have enough nooks and crannies for air movement that their “equivalent” vapor permeability as a construction would be at least vapor semi-permeable. John stated that when he has tested assemblies, the sealant strips do a good enough job of sealing to render three-tab asphalt shingle roofs as essentially vapor impermeable.
I would be very carefully checking the underside of the roof deck for any evidence of bulk water leakage, past or present, before dense-packing the roof cavities with the cellulose.
Tue, 11/01/2011 - 18:36
Flash and batt?
by Jim Merrithew
Peter and Martin,
It would be very difficult to seal this roof assembly with Peel and Stick. Would a Flash and Batt application work here?
The text says Bill Hulstrunk suggests using EPS, XPS or Polyiso as a permeable rigid board insulation. My understanding from Martin's previous GBA blogs is that EPS is semi permeable, but XPS and Polyiso have low permeability.
Tue, 11/01/2011 - 19:01
Reponse to Jim
Jim,
Yes, flash-and-batt could work here, as long as the closed-cell spray foam was thick enough. That's why I wrote, "There are only two reliable ways of keeping water vapor away from the roof assembly. ... One way is to spray closed-cell polyurethane foam on the underside of the roof sheathing..."
Wed, 11/02/2011 - 17:08
Open cell on underside instead of closed cell?
by matt berges
But will the closed cell foam on the underside of the roof deck not also create sandwich of impermeability?
Please advise...I am installing 4" of poly iso over top of ice and water shield on the roof deck (then outside strapping/venting and another layer of osb under the metal roof).
On the inside I was considering any option that was vapor open (so not to create the impermeable sandwich)....for this reason (and my concern of cellulose settling) I was leaning toward open cell foam between the rafters, rather than the closed cell spray foam.
Wed, 11/02/2011 - 17:18
Flash & Batt
by Thomas Croasdale
Dean,
A cold roof in NE. is best all around .If your going to the trouble of applying rigid foam to the underside of the roof sheathing then you might as well create a ventilation channel by ripping 1x3 strapping in half ,apply these to the sides of the rafters and then nail the foam to these. Seal the edges with foam spray and then drill 3" or 4" vents into the soffit for for ventilation. Have the roofing contractor cut in a ridge vent and be done with it.
Wed, 11/02/2011 - 17:30
Vent-skin radiant barrier assembly alternative
by JOE MARTIN
I would agree that closed cell applied to the underside is reliable for as long as the roof is. I have seen the disastrous potential of internal moisture condensing on the underside of a cold roof deck, and I wouldn't want my cellulose anywhere nearby.
An alternate I would propose is a vent-skin assembly as follows:
3/4" plywood roof deck on 2x10 @ 16" O.C. w/ 1.5" vented air space created using furring strips and Astro-foil faced bubble wrap stapled to the underside of them. The radiant barrier heat is in this way vented from the soffit to the ridge. On the underside of the foil faced vapor barrier we will then apply the closed cell. I've done this successfully with techshield, plastic air baffles continuous, and 5.5" of open cell. It was simple and affordable - and allows you to see if there's a water problem at the bottom of each joist space outside the house (where you generally want the water to be). Comments please from all those much smarter than I.
Wed, 11/02/2011 - 17:51
Response to Matt Berges
Matt,
Either option -- cellulose or open-cell spray foam-- will work fine in your case.
Wed, 11/02/2011 - 17:56
a vapor intelligent membrane
by Ken Levenson
at interior side of cellulose - by Pro Clima - could do the trick.
No need to risk making sheathing a mud sandwich. Foam can be eliminated too.
The intelligence keeps the vapor out in winter and allows assembly to dry to interior in summer.
Full disclosure: we represent Pro Clima in America...a little googling can find us.
Wed, 11/02/2011 - 18:02
spay foam + high density cellulose + XPS?
by Hallie Bowie
For a retrofit situation with 2x6 rafters in zone 5, I've considered using 3 1/4" closed cell spray foam on the underside of the deck, plus high density cellulose to fill the remainder of the rafter bay, plus 2" XPS on the underside of the rafters. Is the XPS permeable enough to work in this situation? Since the air barrier is provided by the closed cell, is is necessary to seal the seams on the XPS? If you did seal the XPS on the interior to create an air barrier here, could you use less than 3 1/4" of closed cell spray on the under side of the roof sheathing?
Wed, 11/02/2011 - 20:08
Put the foam boardinsulation where it belongs . . .
by Ed Voytovich
. . . on top of the roof deck. No condensation, no peel-and stick wrapped around rafters, no ventilation issues, no muss, no fuss, and--to quote from a Monte Python skit that some may remember--"No Kangeroos!!!"
unvented cellulose
by Tim Johnson
Advanced Energy did a mockup of a roof several years ago that include 1/2" OSB, tarpaper and shingles. They got it wet and then turned on sunlamps to simulate the sun. The idea was to see if the sun would drive moisture through the roof assembly. In 4 seconds the humidity was coming through. .You have to worry about moisture also coming through the roof assembly. John Tooley as of 2 years ago was recommending closed cell foam only. An impermeable roofing membrane under the shingles might work. Use Membrane on the inside. 2" XPS has a perm rating of less than 1. Be careful of doing a vapor barrier sandwich. You must know the perm rating of what you are using.
Thu, 11/03/2011 - 00:04
Capes in Maine
by Erik North
This is a very pertinent question...I wish I could post a photo of my Portland neighborhood. About 50 Capes with no eaves or soffits and no possibility of retrofitting ventilation. This leads to folks doing things like punching holes into the kneewall spaces through the gables.
I often see folks use flash and batt or dense packed cellulose and, like Dan Kolbert said, without issues.
Thu, 11/03/2011 - 06:04
Response to Ed Voytovich
I agree completely: "Put the foam board insulation where it belongs . . . on top of the roof deck."
Thu, 11/03/2011 - 09:12
keep it simple
by john roy
I had the same issue last year with venting vs non venting a cathedral ceiling using dense pack cellulose insulation . In the end I opted for the time tested solution of ridge & soffit vents with baffles between the rafters. With all the back and forth opinions on whether I could or couldnt insulate with or without ventilation I choose the to vent and not worry about condensation issues down the road...
Thu, 11/03/2011 - 10:00
Rigid Foam Right Under the Deck.
by Justin Zeller
As long as the R-value of the foam, given its gradual decrease over time, is high enough to break the temperature differential between the interior and exterior, eliminating the potential of dew point, the rigid foam can be fit tight inside the joist bays and sealed into place with expanding foam. (There is a good explanation of thicknesses needed in "Why Flash And Batt Makes Sense", by Michael Maines, Fine Homebuilding 217.) If the roof is already installed, and the rigid is already bought, this is the most cost effective way of managing the hot roof. Cellulose can still be installed under the rigid foam, and then your ceiling of choice under that. Otherwise, I'd agree with Ed Voytovich, put the rigid on the exterior of the building, further increasing the foams effectiveness by eliminating the thermal bridging caused by the joists.
We've done a couple of crawl spaces with the first method, and it has increased the comfort level in the rooms above tremendously. I'll be including pictures and a write up on our blog soon. www.redhousecustombuilding.com Obviously, there is a lot more heat and humidity at the top of the house, but this is all the more reason to think about putting the proper R-value on the exterior of the roof sheathing.
Thu, 11/03/2011 - 16:14
Sealing the rigid
by Bohdan Boyko
I strongly second Peter Yost's recommendation of being painstakingly thorough in air sealing the rigid foam before densepacking. Although the densepacked cellulose is almost air tight, it is still very vapor permeable and moisture could see a cold roof deck via gaps. Remember the SIPS roof fiasco in Juneau?
Thu, 11/03/2011 - 16:21
interior Vapor barrier required
by Matthew Amann
For dense pack cellulose to be used successfully in an unvented roof, an interior side (warm side in wettest season)vapor barrier must be used IMHO.
Tue, 11/08/2011 - 11:26
Unvented roofs & the Code
by Christopher Vlcek, Littlewolf Architecture
The 2009 IRC (section R806.4) makes explicit the requirement for impermeable insulation (eg rigid foam board or closed cell spray) above permeable insulation (eg blown cellulose or fiberglass). The R-value of the impermeable layer depends on climate. R25 is required for climate zone 6 in Maine. So, for an UNVENTED roof, either rigid board on the outside to keep the sheathing warm, or closed cell on the inside to keep the sheathing cold but inaccessible to warm interior air. Then fill your remaining cavity with cellulose.
For a recent retrofit, we obtained a lot of 3" poly-iso board for no cost, and installed it between the rafter bays, sealing all gaps with expandable foam. A labor-intensive approach, but OK for DIYers.
Alternately, for a VENTED roof, you can skip the foam. Cross strap the ceiling for added insulation and use cellulose - a friendlier product for the environment. The effort to 'retro- vent' the top of the rafters shouldn't be too bad, through the soffit or frieze board.