Where in the IRC 2009, Chapter 11, is the cathedral ceiling limited to 500 square feet or 20%?
I can find no reference to 20%. This requirement is, I read it, for ceilings that can't meet the specified thermal resistance and are allowed to downgrade. Obviously this limit would not apply if the ceiling is fully insulated.
Asked by Anonymous
Posted Tue, 12/08/2009 - 17:01
Edited Wed, 12/09/2009 - 11:03
Posted Tue, 12/08/2009 - 17:01
Edited Wed, 12/09/2009 - 11:03
Tags: Building Code Questions
Other Questions in Building Code Questions
In Energy efficiency and durability | Asked by Litawyn Eco-Cottage | Feb 11, 12
In Green building techniques | Asked by Bennett Sandler | Feb 12, 12
In Energy efficiency and durability | Asked by Bruce Miller | Feb 12, 12
In Energy efficiency and durability | Asked by Jayne Masternak | Feb 11, 12
In Mechanicals | Asked by David Meiland | Feb 10, 12
Yahoo
Technorati
Google
Facebook
Delicious
Digg
StumbleUpon
Reddit

You're right, this does not limit any kind of ceiling that meets the prescriptive requirements for your zone. But it falls within the exemptions from prescriptive measures:
■ 500 ft² or 20% of ceiling area of cathedral ceiling, whichever is less, is allowed to have R-30 insulation
Posted Tue, 12/08/2009 - 17:47
Peter,
I don't have a copy of the 2009 IRC, but in the 2006 IRC the cathedral ceiling limitations are in N1102.2.2.
Posted Wed, 12/09/2009 - 05:21
Peter, and all,
The 20% limitation is in the IECC in Chapter 4 (Residential Energy Efficiency). The IECC is, of course, an option for the builder. So, if they select that code, they would need to comply with THAT requirement. If they use the prescriptive requirements of the IRC (Chapter 11), they could avoid this requirement. Sorry for the confusion. It allows me a chance to make a good point: Remember this may change ... again. The 2012 Code may reverse this exception or add the requirement to the IRC. Keep your eyes open.