Helpful? 0

Does the facing of polyiso insulation matter when mechanically attaching to a block wall?

The 2009 IRC allows for unvented crawl spaces. To acheive the R-10 for my zone (Maryland) I plan on using recycled 2" polyiso roof insulation attached with Tapcon screws to the CMU walls. 85% of the CMU is below grade. The facing of the roof insulation I intended to use has a heavy tar paper facing both sides. Does this facing preclude using this roof insulation in this application?

Asked by Paul J
Posted Mon, 07/11/2011 - 21:38

Tags:

2 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Paul,

This is probably okay if the wall has effective waterproofing and stays dry. The polyiso will be nearly impermeable, but you don't really want moisture to migrate into the insulation. You just need to be sure there's no wetting of the block, or water could collect under the polyiso, and probably end up dripping out onto the floor. The worst thing you can do is add insulation to the warm side of a wet wall.

Answered by TJ Elder
Posted Wed, 07/13/2011 - 01:05

2.
Helpful? 0

Thank you for your reply.

Answered by Paul J
Posted Thu, 07/21/2011 - 21:00

Other Questions in Building Code Questions

In Building Code Questions | Asked by michael maines | May 23, 12
In Energy efficiency and durability | Asked by Victor Burgos | May 23, 12
In Energy efficiency and durability | Asked by David Slade | May 21, 12
In General questions | Asked by Robert Hronek | May 23, 12
In General questions | Asked by Holger Herrmann | May 23, 12
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!