I am planning on doing unfaced fiberglass batt insulation over spray foam plus continuous polyiso on the exterior of a small new house. The building code (R316.4) requires thermal barriers between the interior useable space and foam insulation and the prescribed way of meeting that is 1/2" gyp board. I was hoping to do wood interior walls and ceilings - plank, OSB or even metal and not do any gyp board. Does any one know of any test reports that I can give the building inspector that shows that an ignition barrier (OSB etc.) plus the noncombustible fiberglass meets the intent of the building code?
Its not uncommon for a plank ceiling to be installed on a cathedral ceiling and if you have rigid insulation above the sheathing then it does not meet code!

Asked by Timothy Gooding
Posted Fri, 11/09/2012 - 18:46

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

At 3" or more most spray-applied cellulose meets the spec, but not all fiberglass. IIRC any standard thickness/density rock wool of 3" or greater will makes it. If the product has ASTM E 119 the fire-rating greater than 15 minutes it should qualify but IIRC the letter of the code requires a further Evaluation Service Report indicating it passed a corner test variation on ASTM E 119 before it's fully qualified as an ignition barrier.

Unlike fiberglass, rock wool and cellulose are completely opaque to infra-red radiation, and low density fiberglass can cause it to fail the test. High density fiberglass often does though- JM Spider @ 1.8lbs density installation makes the lowered attic & crawlspace ignition barrier test at 2" thickness or higher, but probably doesn't in a 1lb density application:

http://www.specjm.com/files/pdf/T07-020JMSpiderIgnitionBarrierV2.pdf

Most wood prescriptively meets the ignition barrier spec @ 23/32" thickness or more, and that includeds 3/4" ply/OSB for walls. It would include 1x t&g or shiplap planking- not sure about planking with un-lapped edges. For roof decks even 15/32" and half-inch goods comply according to IBC section 2603.4.1.5 :

http://www.ibc-wiki.com/index.php?title=Chapter_26#.5B.5B2603_4_1_5.7CIn...

If batts, rock wool or cellulose at any density & thickness over 3" should make the grade in walls. But in a cathedral ceiling it may need to be damp-sprayed and have data showing that has passed the tests (the manufacturer should have the cert available if they did the test).

Answered by Dana Dorsett
Posted Fri, 11/09/2012 - 19:47

Other Questions in Building Code Questions

Steel frame home insulation

In General questions | Asked by J B | Oct 28, 14

Foundation sealing options?

In Energy efficiency and durability | Asked by Rob Shuman | Oct 30, 14

I am considering a double wall construction

In Energy efficiency and durability | Asked by Rick Fetter | Oct 30, 14

R-35 wall assembly for a 4C Marine climate zone

In Green building techniques | Asked by Jose Castro | Oct 29, 14

A very low addition...

In Energy efficiency and durability | Asked by ron letourneau | Oct 29, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!