Sealing PEX and PVC pipe penetrations

I am reposting this to the Code section; not getting an answer in General Questions.

What do I use to meet code-required fire blocking and good weatherizing/air sealing for the circumferential individual tube/pipe and ganged tubes (a cluster of tubes), penetration gaps for PEX-to-wood (and plywood) and PEX-to-PVC pipe, and for PVC-to-wood, and PVC- & PEX-to-drywall?

With manifold distribution and multiple zoning of (1) HW heating supply and return (wall hung rads), and (2) potable water supply, there are a lot of penetration points.

As well, rigid PVC drain and vent pipe penetrates plates and the roof deck, passes from exterior wall cavities into conditioned spaces, all-season spigots penetrate the siding; etc.

I am cautioned that PVC and PEX expand and contract such that they may tear away from foam sealants and some caulks. Also, PEX and PVC squeal and squeak, crackle and pop when heating up and it gets worse when they are tighly anchored, rounding bends, rubbing against each other, against wood framing; etc

What the problem looks like:

Viega Manablock Parallel Water Distribution Manifold: http://www.viega.net/4741.htm

Pex leaving and returning to mechanical space passes through walls, floors, plates: http://tiny.cc/fgh4sw

According to http://huduser.org/portal/publications/pex_design_guide.pdf:

Do not allow (PEX) tubing to come in extended contact with commonly encountered construction materials - This list is not complete:

Pipe thread sealing compounds
- Fire wall penetration sealing compounds. Exception: water soluble, gypsum-based caulking or other sealants approved by the PEX tube manufacturer
- Petroleum-based materials or sealants such as: Kerosene, Benzene, Gasoline, Solvents, Fuel - Oils, Cutting Oils, Asphaltic Paint, and Asphaltic Road Materials, Acetone, Toluene, and/or Xylene
- Do not place any PEX tubing in heavily contaminated soils or other heavily contaminated environments.
- Petroleum-based caulks or sealants should not come in direct contact with PEX.

Look at this list … these materials and solvents are everywhere and in most tool boxes and used without much thought as to what might be compromised by them. We use PVC caulking and Great Stuff foam for weatherizing the plywood and framing joints; but they are strictly not to be used with PEX and; then there are the clean up solvents (mineral spirits, et al) and asphalt based window and panel sealing will also harm PEX.

Asked by Oak Orchard
Posted Wed, 02/27/2013 - 12:28
Edited Wed, 02/27/2013 - 12:30

Tags:

9 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Well, I think it should be more obvious what to use in is this case than can be divined from searching the fine print. People run PEX and people need to install air/fire blocking and if commonly used materials are incompatible with what is being used, then I think it should be spelled out.

I, myself, used foam backer rod around the PEX and caulked with 3M Fire Barrier Sealant (the blue stuff). If it doesn't work, i guess I will find out in a couple of decades.

I could, also, have wrapped the PEX with tape THEN either sprayed fire barrier foam or sealant.

Answered by Robert Sanders Jr
Posted Wed, 02/27/2013 - 21:32

2.
Helpful? 0

Contact the pipe manufacturer.

There are special gaskets for fire protection.

Answered by Hein Bloed
Posted Thu, 02/28/2013 - 08:43

3.
Helpful? 0

Its not just for fire blocking. Fire is a low-risk and unexpected eventuality. The main issue is air sealing. It is the PEX and the PVC that create a network of pathways for condensation and wetting and undoing all the good works of external weatherizing, internal air sealing, vapour retarders/airtight walls, etc.

I see repeated references, videos and photos of spray foams and other chemically volatile and solvent-sensitive compounds as well as flammable materials being recommended/demonstrated for fire blocking and air sealing.

The fact that I am having a hard time getting an answer to this quesiton on this site is worrysome.

Answered by Oak Orchard
Posted Thu, 02/28/2013 - 13:03

4.
Helpful? 0

duplicate deleted

Answered by Jerry Liebler
Posted Thu, 02/28/2013 - 15:47
Edited Thu, 02/28/2013 - 15:51.

5.
Helpful? 0

For air sealing nothing beats EDPM boots. PVC is pretty tough stuff & resists most foams & sealants well. PEX is certainly more touchy but rarely needs to cross the "primary pressure boundary" in houses at least.

Answered by Jerry Liebler
Posted Thu, 02/28/2013 - 15:47
Edited Thu, 02/28/2013 - 15:50.

6.
Helpful? 0

Latex foam or caulk is allowed per Pex Supply, and silicone and polyurethane foam:

http://pexsupply.blogspot.com/2009/01/sealing-your-pex-tubing-in-place.html .

I don't know if the HUD doc considers these "petroleum based" or otherwise prohibited.

Answered by K Willets
Posted Thu, 02/28/2013 - 16:49

7.
Helpful? 0

Gents ... regular latex caulk will definitely NOT work, but the high end fire blocking latex caulks are approved. Regular latex will shrink and separate from the plastics. No VOC's allowed to touch PEX.

While PVC plumbing pipe is tough stuff, it does expand and contact, as PEX, lengthwise; and so it can shed a sealant that is not adhering well and has insufficient stretch.

PEX leaving a conditioned boiler room to pass through walls and plates is passing through the primary pressure boundary. I have a small 4 zone situation with 32 rads. That's a minimum of 64 penetrations in the pressure boundary. PEX out of a basement through a plate and into exterior walls and into partitions and retruning is passing the pressure boundary.

Anyway, even if you don't consider air sealing an issue, the CODE requires fire block sealant at each penetration. That has much higher adhering and non-shrinking standards than air sealing caulks.

You can't put EPDM collars on PEX and PEX bundles. Every time it heats up, PEX squeals like a banshee if it is forced through EPDM, wood and plastic.

Here' were PEX Supply got its info:
http://plasticpipe.org/pdf/tn-39_application_of_pesticides_termiticides_...

DOW says NOT to use its polyurethane foam on PEX. And polyurethane foam will not hold a seal on expanding/contracting tubing.

What do we use to clean up expanding foam? Petroleum products (solvents). Not advised for PEX.

Answered by Oak Orchard
Posted Thu, 02/28/2013 - 22:04

8.
Answered by K Willets
Posted Fri, 03/01/2013 - 01:11

9.
Helpful? 0

Oak,
For years, many builders have sealed plumbing vent pipes that penetrate top plates with an ordinary roof boot (roof flashing for pipes). It's designed to be watertight, but it also happens to be airtight. The rubber flashing seals the penetration.

For walls, you can use flashing from Quickflash designed for just that purpose, or you can use Kaflex flashing from Four Seven Five.

Answered by Martin Holladay, GBA Advisor
Posted Mon, 03/04/2013 - 16:56

Other Questions in Building Code Questions

In Green products and materials | Asked by JOSEPH POLAND | May 19, 13
In Energy efficiency and durability | Asked by Scott West | May 11, 13
In Green building techniques | Asked by Andy Chappell-Dick | May 18, 13
In Energy efficiency and durability | Asked by Dan Kolbert | May 17, 13
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!