T&G cathedral ceiling air barrier question

We are located in the Finger lakes region of NY and are considering T&G cathedral ceiling. Roof assembly would be Zip Roof Sheathing, un-vented roof with 7" of closed cell foam (R-49). I found a company that uses Lapolla Foam Lok 2000 4G foam with climate-friendly blowing agents. Based on this assembly, I am assuming that I would not need a dry wall layer under the T&G; am I correct?

Asked by Nina in CNY
Posted Mar 20, 2017 9:47 PM ET
Edited Mar 21, 2017 8:40 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Nina,
You won't need an interior air barrier, but you are still required by code to have an interior thermal barrier (to protect the spray foam insulation from fire).

Check with your local code inspector (your local building department) to determine whether your tongue-and-groove boards would be approved as a thermal barrier in your jurisdiction. You may be required to install 1/2-inch drywall as a thermal barrier.

-- Martin Holladay

Answered by Martin Holladay
Posted Mar 21, 2017 5:14 AM ET

Other Questions in Energy efficiency and durability

Airtight electrical boxes in masonry house?

In General questions | Asked by davor radman | Apr 27, 17

Building a new home in Climate Zone 5 — Need insulation help

In GBA Pro help | Asked by NKoenig | Mar 26, 17

Exterior wall installed on perimeter of osb floor yet rest of room is a cement slab?

In General questions | Asked by frugalmumma | Apr 26, 17

1974 construction retrofit

In Energy efficiency and durability | Asked by Mark Walker | Apr 25, 17

Manufactured foundation drains, e.g. Z-Drain

In Green building techniques | Asked by William Costello | Apr 26, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!