0 Helpful?

8" of exterior mineral wool (Comfortboard 80)

I am in zone 7 (Northern Minnesota). Looking at building timber frame structure without SIPs. I love the idea of using Roxul Comfortboard 80 for exterior insulation. I want to avoid foam as much as reasonably possible even though I will most likely need to use it for the roof. Wall assembly would be 2x4s sistered onto outside of timber frame, exterior plywood, WRB (Delta Vent SA), 8" of Roxul Comfortboard 80, vertical furring strips and then siding.

I have not seen example of anyone using 8" of mineral wool on exterior wall. This would be 2 layers of 3" and 1 of 2". 8" would give me approximately R34. Adding mineral wool between 2x4s would give at least R40. The city of Vancouver in British Columbia has an excellent document http://www.victoria.ca/assets/Departments/Planning~Development/Permits~I... that details how to attach 8" of exterior mineral wool.

Besides worrying about hitting a stud through the furring strips, is there any reason why this wall would not be feasible or performant? Anyone used 8" of Comfortboard 80 on exterior?

Asked by David Bainbridge
Posted Mar 8, 2018 12:56 PM ET


4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.

Roxul has published a design guide with advice on continuous exterior mineral wool panels up to 12 inches thick (see table reproduced below).

Here is a link to the design guide: Residential Insulated Sheathing – Design Guide.

For more information, contact a technical help representative at Roxul. (The company now has a new name: Rockwool.)

For information on a project that included 6 inches of exterior mineral wool, see Wrapping an Older House with Rock Wool Insulation.

Roxul Comfortboard thickness table.jpg
Answered by Martin Holladay
Posted Mar 8, 2018 2:09 PM ET
Edited Mar 8, 2018 2:12 PM ET.


Thank you for that link! I find it somewhat difficult searching on their website.

Edit: After reviewing that doc I see they then reference another doc for fastening that I had to google: https://static.rockwool.com/globalassets/rockwool-na/downloads/technical...

Answered by David Bainbridge
Posted Mar 8, 2018 5:22 PM ET
Edited Mar 8, 2018 5:46 PM ET.


Found another excellent reference from the 15th Canadian Conference on Building Science and Technology in a paper titled "STRUCTURAL TESTING OF SCREWS THROUGH THICK EXTERIOR INSULATION" https://buildingsciencelabs.com/wp-content/uploads/2017/11/CCBST-2017-St....

The primary objective of the study was to evaluate the vertical load resistance of long screws through insulation as a cladding attachment technique with specific focus on relatively thick insulation layers of mineral wool (equivalent of Comfortboard 80 and 110).

They found that with a typical cladding load of 25 lb per fastener the deflection was less then 0.025" which is likely insignificant considering a one story wood-frame structure is expected to potentially have moisture shrinkage of 3/8".

Some key findings I noticed:
- deflection difference between 6" of XPS and 6" of mineral wool was 0.005". Basically no difference.
- the difference in deflection between using 6" of mineral wool and 12" of mineral wool was 0.007"
- when fasteners were installed into 3/4" plywood sheathing only it provided similar load deflection response to fasteners installed minimum 1" into stud framing.

This gives me confidence that even 9" of Comfortboard 80 will not be an issue, especially when using a Heco Topix screw.

Answered by David Bainbridge
Posted Mar 8, 2018 10:57 PM ET


Thanks for the second link.

Answered by Martin Holladay
Posted Mar 9, 2018 5:09 AM ET

Other Questions in Energy efficiency and durability

Thickness of Closed Cell Insulation in 2x4 Walls

In Energy efficiency and durability | Asked by Mike Spooner | Mar 18, 18

Proper WRB behind Boral Siding

In Energy efficiency and durability | Asked by user-7040235 | Mar 19, 18

Insulation and wall construction improvements for a groovy 70s partial-brick ranch

In Energy efficiency and durability | Asked by Steve Sloan | Mar 7, 18

How much interior insulation would be safe

In General questions | Asked by Smokey059 | Mar 19, 18

How to Reduce High Energy Costs for Ductless Minisplits

In Energy efficiency and durability | Asked by kazirode | Mar 16, 18
Register for a free account and join the conversation

Get a free account and join the conversation!