I’m thinking something that would create a thermal break between concrete and tile floor. Anyone with ideas about what to use would be appreciated.. Thanks Rob

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. user-2310254 | | #1

    Rob,

    Where are you located? Is this new construction, and is the radiant going everywhere or only in an isolated area?

  2. Expert Member
    Dana Dorsett | | #2

    Is there going to be insulation under the slab, or is this a retrofit over a existing uninsulated slab?

  3. GBA Editor
    Martin Holladay | | #3

    Rob,
    The usual method would be to install a generous layer of continuous horizontal rigid foam under the slab, followed by polyethylene and a concrete slab with embedded PEX tubing. The tile is installed as usual. There is no need for a "thermal break" between the tile flooring and the concrete slab.