Insulation and air sealing on attic side of bonus room

I live in southeastern NC in zone 3. I have a bonus room above my garage. The room does not have typical knee-walls. The pitch of the A-frame was raised to pull most of it out of the room. What I have now is a bonus room that is essentially a normal room with a nearly 8' ceiling. when the house was built, batts were installed in the stud cavities of the bonus room but were not enclosed on the attic side. So I have batts that are open to the attic with no air barrier of any kind. My understanding is that this is not ideal and the batts should be enclosed on all six sides. My first question is would it be okay to use thermo-ply to sheath or enclose all of the walls on the attic side and seal the seams with foam or tape to air seal? Are there any concerns about trapping moisture if I do this? What is the correct way to go about this?

Asked by Jason Dennis
Posted Jun 13, 2018 4:41 PM ET

Tags:

2 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Here's an image showing what I meant by non-typical knee walls.

Bonus room outline showing non-typical knee walls
Answered by Jason Dennis
Posted Jun 13, 2018 4:48 PM ET

2.

Jason,
Q. "My first question is would it be okay to use Thermo-ply to sheathe or enclose all of the walls on the attic side and seal the seams with foam or tape to air seal?"

A. Yes.

Q. "Are there any concerns about trapping moisture if I do this?"

A. No.

Q. "What is the correct way to go about this?"

A. More information here: “Two Ways to Insulate Attic Kneewalls.”

Answered by Martin Holladay
Posted Jun 13, 2018 6:06 PM ET

Other Questions in Energy efficiency and durability

Air Barrier Location

In Energy efficiency and durability | Asked by Dan C | Aug 6, 17

Re-sealing failing SIP roof panels

In GBA Pro help | Asked by Passagyrs | Jun 19, 18

Dirty electric from minisplit ductless heat and air conditioning

In General questions | Asked by Arleendv | May 30, 18

Carbon monoxide detectors in a fuel-free house?

In Mechanicals | Asked by Trevor Lambert | Jun 20, 18

Do I need an HRV/ERV for a house built in 1947?

In Mechanicals | Asked by Will82 | Jun 14, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!