Will a wall furnace meet the energy code if heating many rooms?

A mechanical contractor suggests heating a 1,000 sq. ft. 3-bedroom condo with a wall furnace installed in the main room. The heat will be transferred to other rooms by the installation of through-the-wall fans. There will be one thermostat on the furnace. Will this meet any kind of energy code? This is in Massachusetts.

Asked by Anonymous
Posted Sat, 03/13/2010 - 17:15
Edited Sun, 03/14/2010 - 08:56

Tags:

6 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Energy codes specify the thermal efficiency of the envelope, not the heating plant. If it's a direct-vent, sealed-combustion unit that's sized for the design heat load of the space, then it should be adequate. If you're running fans continuously for heat distribution, make sure they're extremely efficient and quiet like the computer fans often used for this purpose. And make sure there's a return path for the air, such as undercut doors or transoms.

Answered by Riversong
Posted Sat, 03/13/2010 - 17:31

2.
Helpful? 0

Joe,
I thought this was an interesting question.
I live in a mixed climate and the forced air HVAC systems that we typically use are costly, big honkin "monsters".

I would think that a well designed(sun friendly) home with a good enclosure could provide comfort with one or two ductless minisplits combined with some type of strategy that provides distribution of conditioned air.

The distribution might be accomplished with efficient room to room fans as Joe is considering and/or...
distributed with the(fresh air) ventilation air stream.(Passivhaus-like ventilation)

Of course as Robert says.. there must be a path.

Is anyone else doing this or considering this?

Answered by John Brooks
Posted Sun, 05/16/2010 - 05:37

3.
Helpful? 0

John,
I've lived that way for over thirty years.
One woodstove in the living room heats a house with three bedrooms and a home office.

Answered by Martin Holladay, GBA Advisor
Posted Sun, 05/16/2010 - 13:39

4.
Helpful? 0

Martin,
I believe I remember you bringing up your setup once before.
(I can not remember which blog)
And I believe you also said that your bedrooms tend to get cold if you do not leave the doors open.
Did I remember that right?
Do you have door transoms, transfer grilles or some type of jump ducts?

Answered by John Brooks
Posted Sun, 05/16/2010 - 13:49

5.
Helpful? 0

Martin,
I located the blog
http://www.greenbuildingadvisor.com/blogs/dept/musings/heating-tight-wel...
Your comments were from Nov 12

I also noticed that I brought up this subject at least once before.
Man, I really do want to get rid of the big honkin HVAC

Answered by John Brooks
Posted Sun, 05/16/2010 - 14:12

6.
Helpful? 0

John,
I could easily install passive floor registers (holes in the floor) if I wanted to.

The bedrooms are sometimes (when outdoor temperatures are between 5°F and -40°F) cool, not cold.

Everyone in my family likes to sleep cool, so we've never cut holes in the floor.

Answered by Martin Holladay, GBA Advisor
Posted Mon, 05/17/2010 - 04:31

Other Questions in Energy efficiency and durability

In Energy efficiency and durability | Asked by Litawyn Eco-Cottage | Feb 11, 12
In Green building techniques | Asked by Bennett Sandler | Feb 12, 12
In Energy efficiency and durability | Asked by Bruce Miller | Feb 12, 12
In Energy efficiency and durability | Asked by Jayne Masternak | Feb 11, 12
In Mechanicals | Asked by David Meiland | Feb 10, 12
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!