Green way to insulate cathedral ceilings?

After much debate, I've decided that spray foam is not an option I'm willing to explore. Too much room for error. Can I use cellulose on cathedral ceilings? What are my options? I will be making venting channels from the eaves to the ridge and putting something on top of that.

Thanks.

Asked by eggman | Mar 14

Tags:

8 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

I assume you mean you will be installing insulation below the vented channels.

What is your roof framing composed of - rafters (what size?), trusses (how deep?). Was eave clearance between wall top plate and roof deck created to allow full depth insulation (high heel)? And where are you located - what is your climate zone? This will determine minimum R-values.

I support your refusal to consider spray foam - it is problematic on a number of levels. And I support your decision to vent your roof - it improves both performance and durability in several important ways.

Cellulose is perfectly appropriate for a vented cathedral ceiling, as long as a tight air barrier separates the thermal layer from the conditioned space, and as long as the vent channels are built in such a way as to channel potential roof leaks down to the eaves and away from the insulation.

But, to get the required thickness and R-value, you may have to build a secondary ceiling frame with standoffs from the primary rafters. This is also an excellent way to reduce thermal bridging.

Answered by Robert Riversong - Mar 14 10

2.

Thanks for the reply. I will be installing insulation below the vented channels. Anybody sell 12' channels out there?

The rafters are 2x6. Ton's of eave clearance and fully vented soffet and ridge. All new rough sawn lumber roof deck and rafters under a black steel south facing roof that get's really hot. . I hope it never rots and wonder if I should protect it with something before I nail up the channels.

What types of cellulose? Loose so I can do it myself? What's is a good air barrier between the insulation and 3/4 T&G?

Answered by eggman - Mar 14 10

3.

You didn't say what climate zone you're in.

Answered by Robert Riversong - Mar 14 10

4.

I'm in the Northeast. 5a on the hardiness zone map. Thanks

Answered by eggman - Mar 14 10

5.

Hardiness zones are in reverse order from IECC climate zones (http://reca-codes.org/IECC%202006%20Climate%20Map.jpg), but it looks like you're probably in zone 5 in both cases.

The current IECC insulation standard for climate zone 5 is R-38 ceiling, so you'll need 10"-12" of densepack cellulose. That will require that you build a sub-rafter ceiling, suspended from the 2x6 rafters with either plywood or solid wood gussets that can be side nailed.

There are many manufactured roof vent baffles - Accuvent makes a nice set that includes a soffit baffle and extension lengths ( http://www.brentwoodindustries.com/spg/building-products/index.aspx), though you can also build them yourself from ¼" hardboard and 2" nailing strips.

You don't need to do anything to protect the rough-sawn roof decking - it's likely to be more durable than any plywood or OSB roof sheathing.

You have to have a blower to install cellulose, and a good one and the proper technique to get the prescribed density of at least 3 pcf.

The best air barrier for a wood cathedral ceiling is drywall. Install ½" DW with 4" gaps every 8' with window screen or filter fabric behind the DW at the gaps. Then cut holes in the screening to blow the cellulose and fill the gaps with 3/8" drywall and tape the seams. Make sure that the ceiling to wall corners are taped as well and all penetrations are sealed. Then install your wooden ceiling boards.

Answered by Robert Riversong - Mar 14 10

6.

Great advice.

I think I'm going to skimp a bit vs. the IECC standard and just screw the DW to the 10ft rafters, leave a 4in gap at the peak and blow the cellulose in using your screen idea. It's a small space with a big wood stove, so I should be ok. Just using it on the weekends. I'm going to forget about using T&G since I'm going with DW. Thanks!

Answered by eggman - Mar 14 10

7.

On March 10th Harold Orr presented a report on his retrofit of a 4 plex in Regina,SK to SESCI-NAC. He covered a low sloped roof (no room to get in appropriate insulation) with a poly vapor barrier and then built up a new roof decking with crisscrossed 2 - 2 x 6s and 2 x 4s which he covered with OSB, tyvec (?) and metal roofing. In other words he treated the roof like a vaulted ceiling without adequate space for insulation. Powerpoint slides are at www.solaralberta.ca/seminars.php .

Answered by Frank Hanlan - Mar 17 10

8.

Thanks Frank.

Answered by eggman - Mar 17 10

Post new answer

The content of this field is kept private and will not be shown publicly.
Discussion policy: The editorial staff at GreenBuildingAdvisor.com does review user submissions. Please be respectful of others. Inappropriate content will be removed.
  • Web page addresses and e-mail addresses turn into links automatically.
  • Allowed HTML tags: <a> <em> <strong> <cite> <code> <ul> <ol> <li> <dl> <dt> <dd> <blockquote>
  • Lines and paragraphs break automatically.

* required fields

Other Questions in Energy efficiency and durability

In Energy efficiency and durability | Asked by Hunter Dendy | Jul 30, 10
In Mechanicals | Asked by sheri | Jul 28, 10
In General questions | Asked by Susie Harrington | Jul 26, 10
In Green products and materials | Asked by Jesse Thompson | Jul 30, 10
In Green building techniques | Asked by Sandra Heiser | Jul 27, 10