0 Helpful?

What's the best WRB option when using foam to insulate your structure / sheathing?

I'm most concerned about the critical details around windows. I plan to use OSB or plywood sheathing coated with StoGuard as the building's air barrier. This will be covered by Tyvek Drainwrap, followed by two layers of taped foam insulation (XPS or Polyiso). Finally, I'll have an airgap between the foam and siding (i.e. furred fiber cement). What is the safest option for windows: 1) Use Drainwrap as WRB, flash windows to wrap, then use exterior trim? 2) Use foam as WRB, extend window box flush with foam, install and flash flanged windows to foam? 3) Install building paper on top of the foam, flash to this layer? (Note: Picton Brothers used this third option on their LEED house).

Asked by Anonymous
Posted Apr 24, 2010 12:15 PM ET

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

I forgot to provide a context for the project:

The location is the Shenandoah Valley, VA in a mixed-humid climate. It's in Zone 4, but near the border of Zone 5. The closest climate data point is Staunton, with 5447 HDD and 622 CDD (65 F base). The annual rainfall places it in the High exposure category.

I would like to hear from builders and designers that have hands-on experience with exterior foam insulation. I'm leary about the water management details with foam, leary about condensation potential without foam! I know these are no easy answers and the installation details can have a dramatic effect on whether any of these systems will be successful. That said, I would like to approach the project with the best possible strategy.

Answered by Daniel Ernst
Posted Apr 24, 2010 3:38 PM ET

2.

Looks like I may have found part of my answer here (this site has A LOT of material to sift through)!

http://www.greenbuildingadvisor.com/blogs/dept/musings/innie-windows-or-...

Answered by Daniel Ernst
Posted Apr 24, 2010 7:02 PM ET

3.

Daniel,
I'm glad you found a helpful blog.

Any one of your listed options will work, as long as you get the details right. It sounds like you're on your way to building a wall that will perform well. Good luck.

Answered by Martin Holladay
Posted Apr 26, 2010 8:11 AM ET

Other Questions in Energy efficiency and durability

Best practices for fastening lath / 3-coat stucco over rigid foam

In Green building techniques | Asked by Zane Bridgers | Jun 21, 18

Dirty electric from minisplit ductless heat and air conditioning

In General questions | Asked by Arleendv | May 30, 18

Thermal bridging solutions when closed cell foam is used?

In Green building techniques | Asked by Judy5 | Jun 21, 18

Vapor retarder for exterior walls Zone 4

In Energy efficiency and durability | Asked by Bob Harshman | Jun 21, 18

Need some unbiased input on these 2 proposals

In General questions | Asked by milhouse21386 | Jun 20, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!