Roxul comfort board in basement?

I spoke to someone at the Roxul company the other day who recommended the following basement insulation. First, tyvek or similar against the concrete basement wall, then 1 1/4 " roxul comfort board for a thermal break, then a stud wall filled with roxul batts--- sheetrock. Do you see a real problem with water condensing on the concrete with the comfort board and tyvek there? Still seems like too much work but I am curious performance wise.

I read the article about roxul board as a foam alternative under siding. It seems like such a solid long term product compared to foam.

Hopeful for cost effective foam alternatives for basement--- no luck yet.

Asked by Nyle Phillips
Posted Thu, 09/27/2012 - 11:50

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Nyle,
I strongly advise you not to use this approach.

Your concrete basement wall is in contact with the soil and is usually cool or cold. When humid indoor air contacts this cold concrete, condensation will form.

If you install insulation on the interior side of the concrete, you will ensure that the concrete stays cold.

If you install an air-permeable insulation like Roxul, the humid indoor air will have easy access to the cold concrete (or the cold Tyvek). You don't want that.

Instead, you want a type of insulation that is air-impermeable. I suggest that you install rigid foam board or closed-cell spray polyurethane foam.

Answered by Martin Holladay, GBA Advisor
Posted Thu, 09/27/2012 - 12:55

Other Questions in Energy efficiency and durability

Sill slope? Sealant tape?

In General questions | Asked by Graham Fisher | Sep 16, 14

The differences between mass and insulation

In Green products and materials | Asked by Nathaniel G | Sep 15, 14

Retrofit heating system

In Mechanicals | Asked by Carole Florman | Sep 15, 14

Out-sulation vs Double Stud Walls

In Energy efficiency and durability | Asked by Rob Shuman | Sep 16, 14

Effectiveness of roxul "flash and batt" - irregular ccSPF causing air gaps

In Green building techniques | Asked by Chuck Swanberg | Sep 16, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!