Open Cell roof deck or attic floor

Done my research, open cell foam is my preferred choice. Building a 3,300 sf house in Fort Worth TX. Pitch of roof is steep 12@12. House is single story. Considering the following two foam options, would appreciate feedback. Additional info, going with two a/c units (4 and 2 ton, both units are two stage. Also using erv air exchange to supply fresh air.

Option A) Open cell foam 5.5 inches under the roof deck, 3.5 in walls, both hvac blowers are in attic. This will provide the closed envelope conditioned attic model. However because of roof slope, creating more surface area for roof deck foam than normal, translates to more $ for foam. Roof deck will be standard OSB.

Option A Benefits:
HVAC running in conditioned space.

Option B) Open cell foam 5.5 inches on attic floor, and 3.5 in walls. Same scenario with hvac blowers (in attic). Non-conditioned attic here, but on this option I'll go with "OSB-radiant foil backed" for roof deck to help keep attic temperatures down. This option also give me the ability to add 5-10 inches of blown in cellulose on top of attic floor foam if I feel necessary in future.

Option B Benefits:
All ducts, vents and electrical housings cut at ceiling drywall are sealed with foam
Less expensive to foam attic floor than roof deck
I'm not having to condition my attic space.

Ok guys, A or B?


Asked by Jeff Bailey
Posted Dec 29, 2012 8:25 PM ET
Edited Dec 29, 2012 8:45 PM ET


4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.

Option A is clearly better, by a wide margin.

Here's how you can improve the performance of Option A: Include some way to address thermal bridging through the rafters, either by increasing the thickness of the rigid foam (so that it covers the bottom of the rafters), or by installing a continuous layer of rigid foam on top of the roof sheathing before you install your roofing.

Answered by Martin Holladay, GBA Advisor
Posted Dec 30, 2012 7:38 AM ET


Can you explain further why Option A is clearly better?

Answered by Jeff Bailey
Posted Dec 30, 2012 9:50 AM ET



Answered by John Brooks
Posted Jan 1, 2013 7:41 AM ET


Keeping your HVAC equipment and ducts within the conditioned space is extremely important. The penalty for leaving the equipment and ducts outdoors varies quite a bit, but can easily amount to 20% of your energy use. Most air handlers leak at the seams, as delivered from the factory, and are hard to seal well because of the need for panels to be removable for servicing.

For more information, see Keeping Ducts Indoors.

Answered by Martin Holladay, GBA Advisor
Posted Jan 1, 2013 9:04 AM ET

Other Questions in Energy efficiency and durability

Taped Zipwall or sheathing with Ice & Water Shield on a REMOTE/PERSIST roof?

In General questions | Asked by Brad Hardie | Oct 20, 16

Replace fiberglass batts with cellulose or just add more insulation on top?

In General questions | Asked by Bill Bertera | Oct 21, 16

Bottom edge of rigid foam on basement wall

In Green building techniques | Asked by Nicholas C | Oct 18, 16

Zola window screen mounts... anyone found a fix?

In Green products and materials | Asked by Steve Hengeveld | Oct 21, 16

Double backdraft damper needed for bathroom fan?

In Energy efficiency and durability | Asked by Jeremy Turner | Oct 19, 16
Register for a free account and join the conversation

Get a free account and join the conversation!
Become a GBA PRO!