Open Cell roof deck or attic floor

Done my research, open cell foam is my preferred choice. Building a 3,300 sf house in Fort Worth TX. Pitch of roof is steep 12@12. House is single story. Considering the following two foam options, would appreciate feedback. Additional info, going with two a/c units (4 and 2 ton, both units are two stage. Also using erv air exchange to supply fresh air.

Option A) Open cell foam 5.5 inches under the roof deck, 3.5 in walls, both hvac blowers are in attic. This will provide the closed envelope conditioned attic model. However because of roof slope, creating more surface area for roof deck foam than normal, translates to more $ for foam. Roof deck will be standard OSB.

Option A Benefits:
HVAC running in conditioned space.

Option B) Open cell foam 5.5 inches on attic floor, and 3.5 in walls. Same scenario with hvac blowers (in attic). Non-conditioned attic here, but on this option I'll go with "OSB-radiant foil backed" for roof deck to help keep attic temperatures down. This option also give me the ability to add 5-10 inches of blown in cellulose on top of attic floor foam if I feel necessary in future.

Option B Benefits:
All ducts, vents and electrical housings cut at ceiling drywall are sealed with foam
Less expensive to foam attic floor than roof deck
I'm not having to condition my attic space.

Ok guys, A or B?

Thanks.

Asked by Jeff Bailey
Posted Sat, 12/29/2012 - 19:25
Edited Sat, 12/29/2012 - 19:45

Tags:

4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Jeff,
Option A is clearly better, by a wide margin.

Here's how you can improve the performance of Option A: Include some way to address thermal bridging through the rafters, either by increasing the thickness of the rigid foam (so that it covers the bottom of the rafters), or by installing a continuous layer of rigid foam on top of the roof sheathing before you install your roofing.

Answered by Martin Holladay, GBA Advisor
Posted Sun, 12/30/2012 - 06:38

2.
Helpful? 0

Can you explain further why Option A is clearly better?

Answered by Jeff Bailey
Posted Sun, 12/30/2012 - 08:50

3.
Helpful? 0

bump

Answered by John Brooks
Posted Tue, 01/01/2013 - 06:41

4.
Helpful? 0

Jeff,
Keeping your HVAC equipment and ducts within the conditioned space is extremely important. The penalty for leaving the equipment and ducts outdoors varies quite a bit, but can easily amount to 20% of your energy use. Most air handlers leak at the seams, as delivered from the factory, and are hard to seal well because of the need for panels to be removable for servicing.

For more information, see Keeping Ducts Indoors.

Answered by Martin Holladay, GBA Advisor
Posted Tue, 01/01/2013 - 08:04

Other Questions in Energy efficiency and durability

Detail for stone veneer

In Green building techniques | Asked by Robert Holland | Nov 16, 14

Mid Roof Edge Vents / Ice Dams

In Energy efficiency and durability | Asked by Robert Eaton | Nov 23, 14

Blower door testing by floor or room?

In PassivHaus | Asked by Ryan Griffin | Nov 21, 14

Help with Green Addition and hyrdonic heat demo

In Green building techniques | Asked by Michael McArdle | Nov 23, 14

Super insulating and soundproofing

In Green building techniques | Asked by Ryan Griffin | Nov 22, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!