Why no "ridge vents" for walls?

I've been thinking about wall insulation vs. attic insulation. Why is it that ventilation is not needed in wall assemblies using fiberglass or cellulose insulation in the same way that it is needed for roof assemblies. I certainly know this is true, but discover I'm not clear on the science behind it. For old 2x4 walls, I think it might be because the insulation is thin enough so the dew point isn't reached within the assembly. But what about double stud walls and other higher insulation assemblies?

Asked by Hallie Bowie
Posted Jan 10, 2013 4:37 PM ET
Edited Jan 10, 2013 4:59 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Hallie,
The short answer to your question: if you are building a double-stud wall, you should definitely include ventilation. The ventilated air gap between the siding and the wall sheathing is usually called a rainscreen gap.

I have been recommending the practice for thick walls for some time; for example, see How Risky Is Cold OSB Wall Sheathing?

Answered by Martin Holladay, GBA Advisor
Posted Jan 10, 2013 4:58 PM ET

Other Questions in Energy efficiency and durability

Sun Pump solar heat pump

In Mechanicals | Asked by Peter Schonherr | May 19, 16

Stamped concrete patio near foundation

In GBA Pro help | Asked by Ryan Lambert | Mar 19, 16

Fan Coils and Return Air From Framing Voids

In Mechanicals | Asked by Dan Cullen | May 23, 16

Metal roof and wall assembly in Los Angeles

In Green building techniques | Asked by Claire L. | May 23, 16

Has anyone ever kept sheathing warm and saved labor costs this way?

In Green building techniques | Asked by sean stewart | May 22, 16
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!