GBA Logo horizontal Facebook LinkedIn Email Pinterest Twitter Instagram YouTube Icon Navigation Search Icon Main Search Icon Video Play Icon Plus Icon Minus Icon Picture icon Hamburger Icon Close Icon Sorted

Community and Q&A

Would this insulation method work?

matterbt | Posted in Energy Efficiency and Durability on

I notice all the pictures of exterior rigid foam is overhanging the concrete foundation by the thickness of the foam. Is there any reason why it can not be installed flush with the concrete foundation,(the area where the bricks would normally go) and to just have the 1×4 strapping and siding overhang the foundation wall?
This way if you used metal flashing and insect screen it could be caulked right to the concrete foundation.
Also I read many posts you can only have foam insulation on 1 side of the wall .What if you have 4″ of exterior insulation, omit the osb sheathing (brace the walls with other approved methods) then flash & batt the 2×6 wall.
This way would go a long way for air sealing the walls also.

GBA Prime

Join the leading community of building science experts

Become a GBA Prime member and get instant access to the latest developments in green building, research, and reports from the field.

Replies

  1. GBA Editor
    Martin Holladay | | #1

    Bert,
    If you want your rigid foam wall sheathing to be co-planar with the exterior of your concrete foundation, you can certainly install it that way. However, you still need to be sure that there is a good air seal at this transition, and there is more of a risk that you won't have good continuity of your thermal barrier.

    Ideally, the wall foam hangs lower than the sill-seal. That way the foam helps reduce air leakage at the bottom of your rim joist, and keeps the top of your concrete warm.

    If you do it your way, make sure you do a good job insulation your concrete wall on the interior. You need to include insulation at the top of your concrete wall.

    Q. "What if you have 4 inches of exterior insulation, omit the OSB sheathing (brace the walls with other approved methods), and then flash & batt the 2x6 wall?"

    A. You could do that. There are no building science reasons why that approach wouldn't work.

Log in or create an account to post an answer.