I am working on a single family house in Climate Zone 5 in New York State.

The first floor is a suspended concrete slab with radiant heat over wood framing. The basement is totally buried with the exception of the top 6". It's covered in 2" of rigid insulation. It will be heated but to a lower temperature than the first floor.The only opening into the basement is a bilco door.

I had originally specified 1" white Dow to be used under the first floor joists but am wondering if I can specify instead one of the radiant barrier materials in the interests of economy. Thanks.

Asked by Linda Gatter
Posted Feb 7, 2013 5:08 PM ET

Tags:

2 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Linda,
If you install a radiant barrier instead of insulation, there will be more heat flow from the heated floor into your basement. Unless the basement is finished space -- and it doesn't sound like it is -- you probably don't want downward heat flow. So I advise that you install a layer of insulation.

If you want the best of both worlds, install a layer of foil-faced polyisocyanurate. Two inches would be better than 1 inch. The foil facing is a radiant barrier.

Make sure to install the rigid foam in an airtight manner. Tape the seams of the rigid foam with a high quality tape.

Incidentally, foil-faced polyisocyanurate is much easier to tape than white EPS foam.

Answered by Martin Holladay, GBA Advisor
Posted Feb 8, 2013 8:27 AM ET

2.

Thanks......I meant to say 1" Thermax, which is polyiso. Sounds like I should stick with that and increase the thickness.

Answered by Linda Gatter
Posted Feb 8, 2013 10:39 AM ET

Other Questions in Energy efficiency and durability

Hot water heating

In General questions | Asked by Dean Sandbo | Apr 13, 16

insulating floor of mudroom before closing it off

In General questions | Asked by joseph moore | Apr 29, 16

Using below grade SIP for full basement

In Energy efficiency and durability | Asked by Steve Lenertz | Apr 12, 16

Is this my best foundation choice?

In Plans Review | Asked by Ken Hodge | Apr 29, 16

Green Building Advisor Q&A

In General questions | Asked by KEVIN ZORSKI | Apr 29, 16
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!