I am working on a single family house in Climate Zone 5 in New York State.

The first floor is a suspended concrete slab with radiant heat over wood framing. The basement is totally buried with the exception of the top 6". It's covered in 2" of rigid insulation. It will be heated but to a lower temperature than the first floor.The only opening into the basement is a bilco door.

I had originally specified 1" white Dow to be used under the first floor joists but am wondering if I can specify instead one of the radiant barrier materials in the interests of economy. Thanks.

Asked by Linda Gatter
Posted Feb 7, 2013 4:08 PM ET

Tags:

2 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Linda,
If you install a radiant barrier instead of insulation, there will be more heat flow from the heated floor into your basement. Unless the basement is finished space -- and it doesn't sound like it is -- you probably don't want downward heat flow. So I advise that you install a layer of insulation.

If you want the best of both worlds, install a layer of foil-faced polyisocyanurate. Two inches would be better than 1 inch. The foil facing is a radiant barrier.

Make sure to install the rigid foam in an airtight manner. Tape the seams of the rigid foam with a high quality tape.

Incidentally, foil-faced polyisocyanurate is much easier to tape than white EPS foam.

Answered by Martin Holladay, GBA Advisor
Posted Feb 8, 2013 7:27 AM ET

2.

Thanks......I meant to say 1" Thermax, which is polyiso. Sounds like I should stick with that and increase the thickness.

Answered by Linda Gatter
Posted Feb 8, 2013 9:39 AM ET

Other Questions in Energy efficiency and durability

aged care facilities

In Green building techniques | Asked by Lela Buckmaster | Jan 21, 17

Smartphone Shopping Offers Large Opportunities In Indonesia

In Green building techniques | Asked by Emily Nesbit | Jan 21, 17

How To Use Siri Speech To Words On IPhone and IPad To Dictate Articles And

In Green building techniques | Asked by Maxie Broun | Jan 21, 17

Tim Cook Thanks a lot Indian Fans ONCE AND FOR ALL Response On IPhone 7 Series Launch

In Green building techniques | Asked by Concepcion Binion | Jan 21, 17

How To Consider A Screenshot With Universe S Vibrant

In Green building techniques | Asked by Ezequiel Hanton | Jan 21, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!