Helpful? 0

Bathroom Exhaust Fan drafts...

Hello-

I was wondering if folks had any suggestions as to how to reduce cold air infiltration/drafts from bathroom exhaust vents.

I've found that in some of my bathrooms, cold air is coming into the bathroom from the overhead ceiling exhaust fan. When I go outside, I see that the exhaust pipe has a simple damper on it. I imagine that when the wind blows, it can easily get up and into the exhaust duct and the damper doesn't stop it.

Are there products that can help resolve this issue?

Thanks!

Asked by Morris Scott
Posted Wed, 02/20/2013 - 10:37

Tags:

10 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Morris,
If air is leaking backwards through your bathroom exhaust fan, it's possible that your house is under negative pressure with respect to the outdoors.

This can happen (a) when you operate a powerful exhaust fan (like a range hood fan) elsewhere in the house, or (b) if you have an unbalanced forced-air heating system with leaky ductwork (especially if there is a supply system leak in a duct located outside of the thermal envelope -- for example, in a crawl space or attic).

Answered by Martin Holladay, GBA Advisor
Posted Wed, 02/20/2013 - 11:01

2.
Helpful? 0

Morris,
Please take a look at the following link as it might prove helpful.
http://www.larsonfan.com/

Answered by Milan Jurich
Posted Wed, 02/20/2013 - 21:00

3.
Helpful? 0

OK, a quick look at that site.... claims some healthy energy savings just by blocking fan drafts. They must have done some tightly controlled studies to come up with those numbers, eh?

Answered by David Meiland
Posted Wed, 02/20/2013 - 22:14

4.
Helpful? 0

Morris, Martin is correct about some of the possible causes, and it can also happen because of wind blowing against the wall where the wall cap is installed. You can install a better wall cap like a Seiho, or you can install an inline damper in the duct (I've used butterfly dampers for this with good success). The inline damper will reduce your airflow somewhat, so you don't want to do that if the airflow is already marginal.

Answered by David Meiland
Posted Wed, 02/20/2013 - 22:28

5.
Helpful? 0

David, If you mouse over the "larsonfan" example -- it appears to be a popup lid that seals the vent. Just a different form of a damper.

I'd also suggest that sometimes the simple dampers work pretty well - if they are cleaned of the grease, lint and muck that collects on them over the years. If they don't swing freely - they will never seal. If you have access to the damper clean it...

If it is an old shaded pole motor (like the motors from old phonograph players -- remember them), then it might be time to replace the bathroom vent with a newer more efficient vent like one of the Panasonic Q series fans.

Answered by Dennis Heidner
Posted Wed, 02/20/2013 - 23:42
Edited Wed, 02/20/2013 - 23:43.

6.
Helpful? 0

Can someone explain how the Larson fan works, the web site is not self-explanatory.

The damper seems to be a pressure activated "plug" as opposed to a gravity and/or a spring mechanism.

Answered by Oak Orchard
Posted Thu, 02/21/2013 - 09:27

7.
Helpful? 0

Thanks Martin. I will check my home for the possible causes you mention!

David, thank you for your suggestions as well. The vent in question is on the side of the house that gets a ton of wind pushing against it. To that end, does Seiho make a version that can go under eaves?

Answered by Morris Scott
Posted Thu, 02/21/2013 - 17:45

8.
Helpful? 0

Morris, you mentioned that the problem is with "some" of your bathrooms...
Is your house 2 story?
If so....are the "problem" bathrooms on the first floor?
The reason I ask .... perhaps your house has a high Neutral Pressure Plane.

Answered by John Brooks
Posted Thu, 02/21/2013 - 18:06

9.
Helpful? 0

Morris, the stuff that Seiho makes for exterior use is mostly or entirely sidewall... http://www.seiho.com

Answered by David Meiland
Posted Thu, 02/21/2013 - 18:06

10.
Helpful? 0

David- Thanks for clarifying on Seiho. The exhaust vents in question are under the eaves and so I'd need to find something appropriate for that. I will keep looking!

John- To answer your question, the house has a basement, ground floor, 2nd floor and finished attic. The problem bathroom vents are on the first/ground floor and a bit on the 2nd floor.

Answered by Morris Scott
Posted Thu, 02/21/2013 - 19:31

Other Questions in Energy efficiency and durability

Quarter Round on Rammed Earth

In Green building techniques | Asked by Terry Lee | Dec 18, 14

Is this furnace venting/leaking problem as bad as it looks?

In Mechanicals | Asked by Nathaniel G | Dec 20, 14

Wet OSB - how much water can it take?

In General questions | Asked by colleen1 runyen | Dec 17, 14

Polyiso for basement

In Green building techniques | Asked by sr kod | Dec 20, 14

Solar thermal systems for heating water

In Mechanicals | Asked by aj builder, Upstate NY Zone 6a | Dec 15, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!