I would describe it as a lean-to roof against the tall side side of a shed building. We have just acquired this building and are faced with high energy costs and ice dams. [More information in Comment #1.]

Asked by walt ott
Posted Fri, 01/03/2014 - 22:57
Edited Sat, 01/04/2014 - 06:46

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

At present it is insulated with fiberglass batts between the ceiling joists, there is no venting.
HVAC is in the attic as is a large blower that vents the kitchen stove and dishwashers. I would like to;
1) seal HVAC ducts with metalized tape
2) seal air leaks into attic
3) put cardboard "walls" along the side of HVAC ducts to add blown in fiberglass
4) add blown fiberglass over batts
5) add venting

I don't know how to vent this roof or what I should do with the stove vent
thanks for any help
w

AttachmentSize
RB ceiling 2.pdf 109.38 KB
Answered by walt ott
Posted Fri, 01/03/2014 - 23:22

2.
Helpful? 0

Walt,
1. Since your attic includes HVAC ducts, the best approach is to insulate the roof assembly (the sloped rafters) so that you bring the attic inside the conditioned envelope of your building. There are two ways you can do this: you can either install closed-cell spray foam insulation on the underside of the roof sheathing, or you can install rigid foam above the roof sheathing. (If you take the second approach, you will need an additional layer of roof sheathing above the rigid foam, and new roofing.)

For more information, see Creating a Conditioned Attic.

2. The product you want to use to seal the HVAC duct seams is mastic, not metalized tape. For more information, see Sealing Ducts: What’s Better, Tape or Mastic?

3. If you install blown-in fiberglass insulation on top of your ducts, the ducts can sweat during the summer (assuming that the building is air-conditioned). That's because the fiberglass insulation doesn't stop the humid attic air from reaching the cold ductwork. The result is condensation and wet ceilings.

Answered by Martin Holladay, GBA Advisor
Posted Sat, 01/04/2014 - 07:09
Edited Sat, 01/04/2014 - 07:10.

3.
Helpful? 0

Thanks. Creating a conditioned attic would be my first choice too, The problem there is to find a knowledgeable installer and of course cost.
this building is a nature center in SE WI. The building was in disrepair when we acquired it and needed a new roof immediately so rigid foam on top would be destroying a new roof.

this is the design on half of the building the other half is a cathedral ceiling with some rigid foam in place ( i cannot tell how much) one room hasNO insulation. As best I can tell it is 5/8 decking on 2x6 tongue & groove ceiling. Can we install 5.5 inches of rigid foam on the inside of that then 6 inch car-siding over that.? Foil faced polyiso?

Thanks again for your help

RB ceiling 1.jpg
Answered by walt ott
Posted Sat, 01/04/2014 - 12:21

Other Questions in Energy efficiency and durability

In Energy efficiency and durability | Asked by maggie wilbur | Apr 19, 14
In Mechanicals | Asked by Kent Jeffery | Apr 16, 14
In General questions | Asked by RobertBolf RobertBolf | Apr 20, 14
In Mechanicals | Asked by Peter L | Apr 19, 14
In Energy efficiency and durability | Asked by Erik Schmitt | Apr 19, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!