How do published commercial and residential code requirements for combinations of continuous insulation and stud cavity insulation relate to in-wall condensation concerns?

The 2012 IECC includes minimum requirements for continuous insulation in combination with stud cavity insulation for wood stud walls. The requirements for these combinations differ between commercial and residential buildings. The required R values for continuous insulation are higher for residential buildings than for commercial. Considering cold climate applications, how do these requirements relate to in-wall condensation concerns?

Asked by Albert Russell
Posted May 13, 2014 3:16 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Albert,
Q. "Considering cold climate applications, how do these requirements relate to in-wall condensation concerns?"

A. They don't. Following minimum code requirements is no guarantee that you won't have a wet wall. These are minimum requirements, not optimal recommendations. To stay out of trouble, you sometimes have to exceed minimum code requirements for minimum foam thickness.

For more information, see Calculating the Minimum Thickness of Rigid Foam Sheathing.

Answered by Martin Holladay, GBA Advisor
Posted May 13, 2014 4:03 PM ET

Other Questions in Energy efficiency and durability

Skipping radiant floor heat in a passive house?

In PassivHaus | Asked by Jenz Yoder | Aug 25, 15

Minisplit or furnace?

In Mechanicals | Asked by Mark Buckingham | Aug 28, 15

Alpen vs Inline

In Green products and materials | Asked by David Mosijchuk | Mar 25, 15

Unvented Roof, 3B, Foam-Free

In GBA Pro help | Asked by Joe G | Aug 26, 15

Insulate cold water pipes

In General questions | Asked by Paul Deleon | Aug 28, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!