Best insulation for a mix of brick & wood?

There's a lot to be found about insulating brick, and about insulating wood...but what's the best solution for interior insulation for a combination of both? This is for a wall in a multi-wythe brick home, and this particular area has some wood framing in it (the wood frame goes to the roof of a portico). (See photo)

My instinct is to use rigid foam, pressed up as close as possible to close conductive loops. But clearly, there will still be lots of air in the wood-framed area.

What's your take on this?

photo.JPG89.1 KB
Asked by Kimberly Howell
Posted May 21, 2014 12:01 PM ET
Edited May 21, 2014 1:02 PM ET

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

This photo may be easier to decipher.

.

Brick wall with wood - 2.jpg
Answered by Martin Holladay, GBA Advisor
Posted May 21, 2014 12:41 PM ET

2.

Kimberly,
This type of wall is best insulated on the exterior -- for example, with EIFS. If you want the exterior of your house to remain unchanged, you will probably have to just swallow hard and pay the energy bills required to keep these bricks and timbers dry.

My article on old brick buildings (Insulating Old Brick Buildings) addresses the problem of embedded joists and embedded beams. Your problem is similar.

Answered by Martin Holladay, GBA Advisor
Posted May 21, 2014 12:46 PM ET

3.

Thanks, Martin. I was afraid that would be the answer. We're in a landmark district, so changing the outside is a non-starter.

And as for that article--I've read it several times, and it's one of the major guidelines in planning our renovation. Thanks for sharing your knowledge so freely.

Answered by Kimberly Howell
Posted May 21, 2014 12:54 PM ET

Other Questions in Energy efficiency and durability

Unvented roof underlayment and rafter bay insulation

In Energy efficiency and durability | Asked by Adeeb Hattar | May 27, 15

Add exterior foam -- but (woops) poly sheeting?

In Green building techniques | Asked by Kyle Hollasch | May 27, 15

is cellulose fiber insulation treated for mold/water infiltration.

In Energy efficiency and durability | Asked by Alice Onaga | May 27, 15

No footing, no drainage?

In Building Code Questions | Asked by Michael McArdle | May 27, 15

Building wrap as an air barrier above a cathedral ceiling?

In Energy efficiency and durability | Asked by Justin Smith | Apr 2, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!