I'm in a climate zone 5 area and have a 3' crawlspace with close to 6" of closed cell spray on the interior of the rim joists. I'm about to re-side possibly with Hardipanels, and insulate from the outside- planning on 2 layers of 1-1/2" of reclaimed polyso, held on with 3/4" furring strips over Tyvec for a rainscreen, well secured , enough to hold the Hardiboard. My intent is to run the siding roughly 1' below the top of the cement block. My question is- where do I end the polyso? I believe layering exterior polyso over top of what is already spray foamed from the interior could create moisture problems in the rim joist area. I'm also curious about what to do with the 3 & 3/4" (poly & furring strips) sticking out past the concrete block foundation. Is there a detail drawing that covers this?

Asked by stu m
Posted Wed, 07/09/2014 - 14:35

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Stu,
You wrote, "I believe layering exterior polyso over top of what is already spray foamed from the interior could create moisture problems in the rim joist area."

You would be creating a so-called "foam sandwich," with OSB or plywood sandwiched between two impermeable layers of foam. That's not ideal. If you had to do it again, it would have been better to use open-cell spray foam on the interior rather than closed-cell spray foam.

However, your sandwich will probably be OK, as long as the OSB or plywood sheathing and the rim joist are dry on the day that you cover them up with rigid foam. Choose a dry, sunny day for the work; you don't want to trap any more moisture in the sandwich than necessary.

Answered by Martin Holladay, GBA Advisor
Posted Thu, 07/10/2014 - 08:28

Other Questions in Energy efficiency and durability

Sealing meeting point of brick wall and asphalt driveway

In General questions | Asked by Jon Haque | Oct 22, 14

Spray foam over XPS on external wall

In Energy efficiency and durability | Asked by Jeff M | Oct 22, 14

Radon Mitigating Systems june / july 2014 pg 86 -87 holes on pipe

In General questions | Asked by karl neemann | Oct 23, 14

Double wythe CMU vs. Thermomass

In Green building techniques | Asked by leo kloop | Oct 22, 14

Window U-value comparison to wall R-value and window replacement

In General questions | Asked by Keith Miller | Oct 20, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!