I live in a 1350 sq. ft. tightly constucted home in Pinewood Springs, Colorado, at elevation 6,700 ft.

I, one person, live in a 1,350 sq. ft. tightly constructed home in Pinewood Springs, Colorado, at elevation 6,700 ft.

Heat is provided by a wood stove and electric baseboard heat.

Do I really need an HRV or ERV, or are there simple ways to achieve appropriate ventilation?

I have no ductwork except for 2 bathroom fans and range exhaust

Thanks

Asked by stuart cohen
Posted Thu, 08/07/2014 - 17:14
Edited Fri, 08/08/2014 - 03:37

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Stuart,
The answer depends on at least two factors: (1) The tightness of your building, and (2) Details about your lifestyle.

If the house is extremely tight (Passivhaus tight, meaning 0.6 ach50 or tighter), most experts would advise you to install a mechanical ventilation system.

Even if your house isn't Passivhaus-tight, some lifestyle choices -- especially damp habits, like frequent showers, keeping lots of houseplants, maintaining several aquariums full of tropical fish -- require mechanical ventilation.

Fortunately, you don't need sophisticated testing to figure this out. Instead, ask yourself two questions:

1. Does my house seem smelly when I return to the house after being away all day?

2. Are there signs of excessive condensation on the interior of my windows during the winter?

If the answer to either of these questions is "yes," then you may need to improve your ventilation.

The easiest way to do this would be to leave one of your bathroom exhaust fans on for 24 hours a day, or to install a timer to control one of your bathroom exhaust fans to operate it intermittently. For more information, see Designing a Good Ventilation System.

Answered by Martin Holladay, GBA Advisor
Posted Fri, 08/08/2014 - 03:45

Other Questions in Energy efficiency and durability

New Home Build

In Energy efficiency and durability | Asked by C. Maglio | Dec 8, 14

Foam insulation and vented attic

In Green products and materials | Asked by Heidi Hicks | Dec 16, 14

Solar thermal systems for heating water

In Mechanicals | Asked by aj builder, Upstate NY Zone 6a | Dec 15, 14

Will my generator run a minisplit safely?

In Mechanicals | Asked by stephen sheehy | Dec 13, 14

B&G's low flow Vario ECM circulator - stupid efficient pumps

In General questions | Asked by flitch plate | Dec 16, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!