Batt insulation for bonus room... installed correctly?

ok. I live in the South (Lower Alabama) and my bonus room above my garage, gets warm during the summer. I went in the attic today to see how the insulation was installed and I noticed that it is Paper towards the room (insulation towards the hot attic space). I read a few articles where basically is states that it doesn't matter (or depends) on which way the paper faces.

The biggest issue I have is that the insulation is extending past the joists into the attic space. I also think that the paper is not installed up against the drywall of the bonus room. Do either or both of these issues matter? Would it be better if I turn all the insulation around and staple it back to the joists to ensure that it stays flush with the joist to ensure a tight fit. Right now I don't think there is a tight fit because the insulation does extend past the joists into the attic.

Thanks
Nate

Asked by Nathan Jones
Posted Aug 8, 2014 7:47 PM ET
Edited Aug 9, 2014 5:14 AM ET

Tags:

2 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Nathan,
You are probably right in your hunch that your insulation was not installed correctly.

First of all, fiberglass batts are the worst-performing insulation material available. Most fiberglass batts are poorly installed. To learn more, see Installing Fiberglass Right.

To answer a few of your questions:
1. It doesn't really matter which way the kraft facing is installed in your climate.
2. Any insulation (but especially fiberglass) should be installed so that it touches the drywall, without an air space between the drywall and the insulation.

The main problem with fiberglass batts is that they are usually installed with no attention to airtightness. Especially when it comes to bonus rooms, the installer has to have a clear understanding of where the air barrier is, and has to pay a considerable amount of attention to sealing all penetrations and transitions from ceiling to wall to floor, to make sure that there are no air leaks. A common problem, for example, is a lack of blocking between the floor joists in a location where blocking is warranted.

Finally, it should be pointed out that the best insulation above a horizontal drywall ceiling is usually cellulose. To do it right, (a) seal all air leaks, and (b) install a thick layer of cellulose.

Answered by Martin Holladay, GBA Advisor
Posted Aug 9, 2014 5:12 AM ET

2.

Thank you. i was able to take some pictures this morning

IMG_20140809_093150.jpg IMG_20140809_093250.jpg
Answered by Nathan Jones
Posted Aug 9, 2014 11:17 AM ET

Other Questions in Energy efficiency and durability

Flogging the half dead vapor barrier horse…

In General questions | Asked by L. M. | Jul 26, 15

We were looking to replace our front door which has 2 flanking sidelights

In Energy efficiency and durability | Asked by Christian Rodriguez | Jul 27, 15

Insulate ducts in conditioned basement?

In Energy efficiency and durability | Asked by Jeremy M | Jul 27, 15

Proper way to detail bottom edge of rigid foam next to sill plate

In Green products and materials | Asked by Nicholas C | Jul 25, 15

How much more efficiently does a ductless mini-split perform below peak demand?

In Mechanicals | Asked by Jeff Cooper | Jul 27, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!