Is it necessary to tape joints in under-slab insulation?

I'm putting recycled 4" XPS under my slab. Zone 6. Do the joints need to be sealed with anything? I'll put poly on top, under the concrete.

Asked by stephen sheehy
Posted Mon, 08/11/2014 - 20:08
Edited Mon, 08/18/2014 - 04:57

Tags:

5 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Nope- the taping would have negligible value at best. The amount of thermal bypass air movement under the slab is miniscule, and the poly layer makes it air & water-vapor tight.

Answered by Dana Dorsett
Posted Tue, 08/12/2014 - 10:10

2.
Helpful? 0

Thanks, Dana-That's what I hoped was the case. Your explanation makes sense.

Answered by stephen sheehy
Posted Tue, 08/12/2014 - 10:19

3.
Helpful? 0

You doing one layer of 4" or 2 layers of 2"? Good to have staggered seams.

Answered by Dan Kolbert
Posted Tue, 08/12/2014 - 19:42

4.
Helpful? 0

Dan-we're using 4".

Answered by stephen sheehy
Posted Wed, 08/13/2014 - 08:21

5.
Helpful? 0

I used 3" XPS under my basement floor and didn't tape the seams, we did however ensure we taped the seams of the poly vapor barrier extremely well.

Answered by Anthony Hughes
Posted Mon, 08/18/2014 - 11:54

Other Questions in Energy efficiency and durability

Is a gas fireplace blower fan an energy efficient investment

In General questions | Asked by W. Timothy Ward | Dec 20, 14

Mechanical room size

In Mechanicals | Asked by Corey B | Dec 20, 14

Solar thermal systems for heating water

In Mechanicals | Asked by aj builder, Upstate NY Zone 6a | Dec 15, 14

Wet OSB - how much water can it take?

In General questions | Asked by colleen1 runyen | Dec 17, 14

Meanwhile at BSC ... PHIUS draft standard

In General questions | Asked by Jin Kazama | Dec 12, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!