Venting Soffit / Overhang

I'm presently building a house with a flat TJI roof. Over the living space there is sloped foam that provides the R-value for the roof as well as the slope. Above the overhang is simply 5/8" T&G followed by torch on. Above the exterior wall separating the overhang space from the "attic" space is blocking sealed with DOW XPS and spray foam. The underside of the overhang will be stained T&G Pine.

My question is, does the overhang cavity need to be / should it be (or not be) vented?

Thank you for your help!

Brandon

Asked by Brandon Kennedy
Posted Apr 5, 2017 6:45 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Brandon,
It sounds like you are describing an unvented roof assembly. If I am guessing correctly -- it's a little hard to tell from your description -- then you don't need soffit vents (because the assembly is unvented).

I hope that your designer and roofer have installed enough insulation to at least meet minimum code requirements. Depending on your location, that usually means either R-38 or R-49 insulation.

For more information on these issues, see Insulating Low-Slope Residential Roofs.

-- Martin Holladay

Answered by Martin Holladay
Posted Apr 6, 2017 6:23 AM ET

Other Questions in GBA Pro help

Draining the Mega-Footing

In General questions | Asked by Kevin Spellman | Oct 19, 17

Blown mineral wool retrofit interior walls?

In Green products and materials | Asked by Chris B | Oct 23, 17

Rake flashing on a low slope roof.

In Energy efficiency and durability | Asked by Tommy87 | Oct 23, 17

Closed cell spray foam/cellulose combination

In Green building techniques | Asked by Steve Lenertz | Oct 21, 17

Forced hot air control question

In General questions | Asked by Lostedge | Oct 23, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!