Venting Soffit / Overhang

I'm presently building a house with a flat TJI roof. Over the living space there is sloped foam that provides the R-value for the roof as well as the slope. Above the overhang is simply 5/8" T&G followed by torch on. Above the exterior wall separating the overhang space from the "attic" space is blocking sealed with DOW XPS and spray foam. The underside of the overhang will be stained T&G Pine.

My question is, does the overhang cavity need to be / should it be (or not be) vented?

Thank you for your help!

Brandon

Asked by Brandon Kennedy
Posted Apr 5, 2017 6:45 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Brandon,
It sounds like you are describing an unvented roof assembly. If I am guessing correctly -- it's a little hard to tell from your description -- then you don't need soffit vents (because the assembly is unvented).

I hope that your designer and roofer have installed enough insulation to at least meet minimum code requirements. Depending on your location, that usually means either R-38 or R-49 insulation.

For more information on these issues, see Insulating Low-Slope Residential Roofs.

-- Martin Holladay

Answered by Martin Holladay
Posted Apr 6, 2017 6:23 AM ET

Other Questions in GBA Pro help

Airtight electrical boxes in masonry house?

In General questions | Asked by davor radman | Apr 27, 17

venting a roof framed over a roof

In General questions | Asked by user-6801629 | Apr 27, 17

Am I ok to lay down my plywood subfloor at 19% Moisture content?

In General questions | Asked by Grey wolf | Apr 27, 17

Vented and Unvented Attic space

In Green building techniques | Asked by espy1 | Apr 27, 17

Compact Re-roof, polyiso over spray foam?

In Green building techniques | Asked by GreenStoneHome | Apr 27, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!