Has anyone had to retrofit a building with single wythe masonry walls?

I am working on a property in Detroit that has, as a wall system, a single wythe of 6 inch brick masonry with sheetrock installed on 1 5/8ths furring strips. So, as you might imagine, air and water runs through the building. Can we build a rain screen from the inside or clad the outside? Or gently push it in the river. I heard an architect say he had seen other buildings constructed this way so I was wondering if anyone had any sources for ideas on how to approach.

Thanks for any help.

Asked by julie klump
Posted Nov 3, 2009 6:08 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Julie,
1. There is no way to build a rainscreen from the inside, although it might be possible to come up with details for interior insulation and finish materials.
2. Yes, you could "clad the outside" — although this would probably require an entire new shell (including framing, windows, insulation, sheathing, and siding) with costs similar to new construction.

Answered by Martin Holladay, GBA Advisor
Posted Nov 4, 2009 5:24 AM ET

Other Questions in GBA Pro help

ZIP R-Sheathing Climate Zone 5?

In GBA Pro help | Asked by Joseph Yount | May 12, 15

Relative value of air sealing at exterior sheathing

In Energy efficiency and durability | Asked by Hugh Stearns | Jul 1, 15

Geothermal nightmare

In GBA Pro help | Asked by Colleen Nicholson | May 30, 13

Attic is hot after closed-cell spray foam was installed

In GBA Pro help | Asked by Mark Hippchen | Jun 27, 15

Boiler upgrade recommendation?

In Mechanicals | Asked by Joe Pavia | Jul 1, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!