Helpful? 0

Permability of building materials and good data on embodied energy

Wondering whether any of you could turn me on to good sources (books or websites) for finding out the permeability of building materials....and also a good site that discusses the embodied energy of building materials...for instance, the embodied energy of different types of spray foam insulation, which I hear has huge embodied energy. Thanks.

Asked by Ed Welch
Posted Wed, 11/11/2009 - 17:53
Edited Fri, 07/02/2010 - 16:25

Tags:

5 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

MATERIAL EE EE EE EE
MJ/kg BTU/lb BTU/cf per R-sf

Cellulose - dense packed 1.8 752 2257 49

Mineral Wool - loose fill 14.6 6277 9415 245

Mineral Wool - batts 14.6 6277 15692 311

Mineral Wool - drain board 14.6 6277 50216 973

Fiberglass – batts 30.3 13027 13027 345

Polyisocyanurate - rigid board 69.8 30009 60018 715

Polyurethane – sprayed 74.0 31815 63630 899

Icynene – sprayed 41.9 18000 9000 208

XPS - rigid board 117.0 50302 90543 1509

EPS - rigid board 117.0 50302 50302 1075

Answered by Riversong
Posted Wed, 11/11/2009 - 20:42

2.
Helpful? 0

Yup, I had a feeling the above chart would lose its formatting. If you can make sense of the data, the first number is Mj/kg, the second, BTU/lb, the third BTU/cf, and the fourth is BTU per square foot of R-1 (to compare the insulation types adjusted for R-value).

There's tons of data on the web. Try Googling. Or if you need specific data, feel free to ask as I've got it all on my hard drive.

Perm ratings are relatively consistent, since there are ASTM standards (ASTM E-96) for testing, but be sure you're comparing either dry-cup or wet-cup. There are actually 6 different testing methods covered under that one standard.

But embodied energy numbers are approximations, dependent upon geographic location, industrial production method, and other variables and assumptions. Be sure you're comparing EE per unit weight or EE per unit volume or EE per R-value equivalent. And much of the data is in metric units of Mj/kg or Mj/m3.

Answered by Riversong
Posted Wed, 11/11/2009 - 20:52

3.
Helpful? 0

Conrad,
Here's a link to a useful table from our friends at Building Science Corporation. The table includes vapor permeability data.
"Building Materials Property Table."

Answered by Martin Holladay, GBA Advisor
Posted Thu, 11/12/2009 - 03:46

4.
Helpful? 0

The BSC materials property table is one of the more useful available on the web, but be aware of some non-standard data that can be potentially misleading.

For instance, while the table is labled "material properties", the perm numbers for wood and vinyl lap siding, which are in quotes, are for as-built assemblies not materials. Sources give perm values for a 3/4" wood board of anywhere from 0.3 to 4.1, while BSC offers "35 perms" for wood lap siding and "70 perms" for vinyl lap siding, when vinyl itself has a perm of 0.05/in (perhaps 0.1 for the siding material).

The table also lists the water absorption of icynene as 0% because plastic doesn't absorb water, but tests conducted by the National Research Council of Canada, according to ASTM D2842-69 (water absorption of rigid cellular plastics) showed 34% by volume because of its open-cell structure. This is one of the examples of a non-hygroscopic material being formed into a hygroscopic matrix (like EPS).

Answered by Riversong
Posted Thu, 11/12/2009 - 09:19

5.
Helpful? 0

Thanks guys.....

Answered by Ed Welch
Posted Thu, 11/12/2009 - 11:41

Other Questions in GBA Pro help

In Energy efficiency and durability | Asked by albert rooks | Feb 13, 12
In Energy efficiency and durability | Asked by Litawyn Eco-Cottage | Feb 11, 12
In Green building techniques | Asked by Bennett Sandler | Feb 12, 12