Open door zonal pressure test. Should both readings be done at 50 Pa?

Testing attic with home at 50 Pa and attic reading 40 Pa. Open scuttle hole until attic reads 20 Pa to see what the orginial hole size was. Does the blower door speed saty the same or ramp back up to 50 Pa when scuttle is open?

Asked by Anonymous
Posted Jun 11, 2010 10:16 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

If I understand you correctly, you are trying to use the "equivalent hole / pressure doubling" technique first popularized by my friend Jim Fitzgerald, but I think you have it a little confused. You would want to open the hatch large enough to approximately double the pressure between the attic and outside -- meaning that the dP would be about 30 house/attic and 20 attic/exterior with the hatch open (it sounds like you were planning the reverse). Then the size of the hatch opening you created would be about equal to the size of the existing leakage paths between house and attic. And yes -- you do need to bring the blower door back to 50pa to use this rough approach.

Answered by Michael Blasnik
Posted Jun 12, 2010 6:31 PM ET

Other Questions in GBA Pro help

Smart vapor retarder over open-cell SPF on underside of roof in Zone 4 (Washington, DC)?

In Energy efficiency and durability | Asked by Elizabeth Hilder | May 5, 16

Mini-split vs Forced air and attic insulation

In Green building techniques | Asked by Mike W | May 6, 16

Can someone explain the science behind a mid-wall vapor barrier on a double stud wall?

In Green building techniques | Asked by Adam Peterson | May 4, 16

How does efficiency in a mini-split vary over various operating levels?

In Mechanicals | Asked by david jensen | May 3, 16

Improvement on the Lstiburek Ideal Double Stud?

In Green building techniques | Asked by Burke Stoller | May 6, 16
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!