Open door zonal pressure test. Should both readings be done at 50 Pa?

Testing attic with home at 50 Pa and attic reading 40 Pa. Open scuttle hole until attic reads 20 Pa to see what the orginial hole size was. Does the blower door speed saty the same or ramp back up to 50 Pa when scuttle is open?

Asked by Anonymous
Posted Jun 11, 2010 10:16 PM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

If I understand you correctly, you are trying to use the "equivalent hole / pressure doubling" technique first popularized by my friend Jim Fitzgerald, but I think you have it a little confused. You would want to open the hatch large enough to approximately double the pressure between the attic and outside -- meaning that the dP would be about 30 house/attic and 20 attic/exterior with the hatch open (it sounds like you were planning the reverse). Then the size of the hatch opening you created would be about equal to the size of the existing leakage paths between house and attic. And yes -- you do need to bring the blower door back to 50pa to use this rough approach.

Answered by Michael Blasnik
Posted Jun 12, 2010 6:31 PM ET

Other Questions in GBA Pro help

Does anyone have experience with Zehnder ComfoFlex?

In Mechanicals | Asked by Trevor Fontaine | Feb 9, 16

How to work with a very deep truss in vaulted ceiling.

In Energy efficiency and durability | Asked by Barry Reicker | Jun 29, 16

Insulating above a garage roof

In General questions | Asked by Jeremy Turner | Jun 30, 16

Trying to source 3/4 inch thick coroplast in Maine

In General questions | Asked by kevin freeman | Jun 30, 16

woodshop super-ventilation: Any reason to air seal / insulate?

In General questions | Asked by Kevin Lynagh | Jun 30, 16
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!