Open door zonal pressure test. Should both readings be done at 50 Pa?

Testing attic with home at 50 Pa and attic reading 40 Pa. Open scuttle hole until attic reads 20 Pa to see what the orginial hole size was. Does the blower door speed saty the same or ramp back up to 50 Pa when scuttle is open?

Asked by Anonymous
Posted Jun 11, 2010 10:16 PM ET


1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.

If I understand you correctly, you are trying to use the "equivalent hole / pressure doubling" technique first popularized by my friend Jim Fitzgerald, but I think you have it a little confused. You would want to open the hatch large enough to approximately double the pressure between the attic and outside -- meaning that the dP would be about 30 house/attic and 20 attic/exterior with the hatch open (it sounds like you were planning the reverse). Then the size of the hatch opening you created would be about equal to the size of the existing leakage paths between house and attic. And yes -- you do need to bring the blower door back to 50pa to use this rough approach.

Answered by Michael Blasnik
Posted Jun 12, 2010 6:31 PM ET

Other Questions in GBA Pro help

Air sealing attic: materials and fire safety

In Energy efficiency and durability | Asked by Sam Smith | Oct 25, 16

Foam sheathing insulation on basement block walls

In Energy efficiency and durability | Asked by david schreiber | Oct 23, 16

What causes a bathroom vent fan to drip water?

In Mechanicals | Asked by Steve Mindel | Oct 26, 16

Covering and insulating the exterior floor of a raised pier/beam home

In General questions | Asked by Brian Jackson | Oct 26, 16

Low profile cans /speakers below closed cell in a flash and batt roof.

In Energy efficiency and durability | Asked by Chris B | Oct 26, 16
Register for a free account and join the conversation

Get a free account and join the conversation!
Become a GBA PRO!