Rigid Foam Polystyrene under Wood Floating Floor

Hello,
I have a room above my garage that is always cold (or hot), I'm in Southern NH. I had a quote from an insulation company to take down the drywall ceiling of the garage (and insulation) and replace it with spray foam for $2,000.00 (gulp). Since this is way out of our budget I thought I could tackle the problem from the floor of the room since we have to replace the carpet. I was thinking of adding a layer of Rigid Foam Polystyrene (taped seams) over the existing plywood floor and then using an engineered wood floating floor above the Foam?? Can I use a floating floor above the Foam??

I will also be adding blown insulation into the knee walls and ceiling of this room and using spray foam around top plates, sill plates and around any vent openings or cracks.
Thank You!!!

Asked by Mary Ostberg
Posted Wed, 12/21/2011 - 12:30

Tags:

11 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Mary,
I advise you to check with the flooring manufacturer, but my understanding is that most manufacturers of floating flooring require a layer of OSB or plywood to be installed on top of the rigid foam before installing the flooring.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 12/21/2011 - 14:41

2.
Helpful? 0

okay thank you Martin!
I would then have to float the plywood too because I couldn't nail it to the Foam, right?

Answered by Mary Ostberg
Posted Wed, 12/21/2011 - 14:54

3.
Helpful? 0

Mary,
It's certainly possible to fasten plywood over foam by using long screws through the foam to the floor joists or subfloor below.

Answered by Martin Holladay, GBA Advisor
Posted Wed, 12/21/2011 - 15:02

4.
Helpful? 0

Great, I will look into that! Thank you! Happy Holidays!

Answered by Mary Ostberg
Posted Wed, 12/21/2011 - 15:08

5.
Helpful? 0

Mary: I would suggest using a higher density foam, in the order of 40 or 60 psi. That is just a gut feeling, though; no data. This has been discussed on http://www.diychatroom.com/ if you care to read there. I see zero problems w/ your plan. Subfloors are not supposed to deviate more than about 1/8" in 10' from "perfectly flat", according to the two manufacturers I consulted when I did a similar job. The point is, make sure your subfloor is as good as you can get it.

Answered by John Klingel
Posted Wed, 12/21/2011 - 18:35

6.
Helpful? 0

One question is how thick will your foam will be over the subfloor. You are not going to get sufficient R value in New Hampshire unless you use 3 inches or more of foam... and think about what this will do to your thresholds, ceiling height, window heights, etc.

My suggestion is to get some more spray foam quotes and hopefully you can get a better price. Plus, there will be benefits to sir sealing from underneath and spraying the rim joists and ends of the joist cavities.

You also could add some polyiso foam boards, taped, on the garage ceiling before you put up drywall.

Billy

Answered by William Geary
Posted Thu, 12/22/2011 - 00:27

7.
Helpful? 0

Thanks John and Billy, your advice is much appreciated!!!

Answered by Mary Ostberg
Posted Thu, 12/22/2011 - 06:16

8.
Helpful? 0

You could also take down the garage cieling and put batt insulation between the joists, then rigid foam under the joists, then strapping and drywall.

Answered by william goodwin
Posted Thu, 12/22/2011 - 07:26

9.
Helpful? 0

Mary, I would cut into the drywall and look at existing insulation. If there is space above insulation by the subfloor, then you could cut a strip of drywall to access blowing in a dense pack of insulation. Then do your foam layer, standard foam is fine, and lay floating floor right on it since your budget is tight. A customer of mine has done something similar.

Answered by aj builder, Upstate NY Zone 6a
Posted Thu, 12/22/2011 - 08:20
Edited Thu, 12/22/2011 - 08:21.

10.
Helpful? 0

The reason I started this question was that I didn't want to take the garage ceiling down so I was trying to insulate from the floor side instead of the Garage ceiling side...even though I know it's better to insulate the ceiling.

Answered by Mary Ostberg
Posted Thu, 12/22/2011 - 08:20

11.
Helpful? 0

Lastly, add window ac unit and a small room heater w tstat to supplement your existing system. Your existing system most likely has not enough supply ducting to the space, happens often.

Answered by aj builder, Upstate NY Zone 6a
Posted Thu, 12/22/2011 - 08:26

Other Questions in GBA Pro help

In Building Code Questions | Asked by michael maines | May 23, 12
In Energy efficiency and durability | Asked by Victor Burgos | May 23, 12
In Energy efficiency and durability | Asked by David Slade | May 21, 12
In General questions | Asked by Robert Hronek | May 23, 12
In General questions | Asked by Holger Herrmann | May 23, 12
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!