What is the smartest way to insulate a finished attic?
Hi. I am a newby on this site and am looking for advice on how to correctly insulate the living space in my attic.
I believe in a vented roof so I vented the rafter bays with 1" Dow Tuff R rigid insulation spaced 2" off the underside of the roof sheathing. It is sealed all the way down to the floor and it ends about 6 inches above the collar ties. I sealed all the edges with foam and I taped all the seams.
The rafters are 2x10 and the collar ties are 2x8. I live in northern New Jersey in IECC zone 4. The rigid insulation is R6.5.
I have space in the ceiling for R38 fiberglass batts but I am not sure what I should do with the slanted sections of the roof that will have sheet rock attached to it. Having used the rigid insulation to create my vent chutes, I am not sure how this affects what kind of vapor barrier(or retarder) I should use.
I am planning to insulate the knee walls for added R value. What am I doing right, what am I doing wrong and what am I supposed to do?
Thanks for your help.
Posted Mon, 05/07/2012 - 15:54
Edited Tue, 05/08/2012 - 06:13
Other Questions in GBA Pro help
Yahoo
Technorati
Google
Facebook
Delicious
Digg
StumbleUpon
Reddit

Randy,
1. You live in climate zone 4; according to the 2009 IRC, you need a minimum of R-38 in your ceiling.
2. Your 2x10 rafter bays are 9.25 inches deep. You have already installed a ventilation chute and rigid foam that take up 3 inches of that depth, leaving you 6.25 inches.
3. Your rigid foam has an R-value of R-6.5, so you have to figure out a way to add an additional R-31.5 in your roof assembly. If you want to put it all between your rafters, that means you need an insulation product that performs at R-5 (or better) per inch. The only insulation product that would do that (other than rigid foam, which is hard to install) is closed-cell spray polyurethane foam.
4. If you supplement the insulation you install between your rafter bays with a layer of rigid foam under your rafters, you could install fiberglass batts or cellulose between your rafters.
5. More information here: How to Build an Insulated Cathedral Ceiling.
Posted Tue, 05/08/2012 - 06:11
Thank you Martin for your response. If I decide to use rigid foam for cost reasons, do I need to seal each piece of foam board? It is difficult to get a perfect fit between the rafters.
Randy
Posted Tue, 05/08/2012 - 08:42
Randy,
Q. "If I decide to use rigid foam for cost reasons, do I need to seal each piece of foam board?"
A. Yes.
Posted Tue, 05/08/2012 - 09:21