Potential problems regarding the use of ZIP System's new R-sheathing?

Does anyone see any potential problems using ZIP System's new R-Sheathing? The product comes in either 1/2" or 1" polyiso on the back of the sheathing between the sheathing and the studs. http://www.zipsystem.com/zip-system/rsheat.aspx.

Once again I am trying to figure out less costly ways to combat thermal bridging, create an air seal, and provide a rainscreen. I would be using the product with no interior vapor barrier therefore reducing the possibility for trapping moisture in the wall cavity.

However, is there the chance you would be creating a place for condensation to build between the foam and the studs? If I were to use the product I would use a product such as Rainslickr as a rainscreen for the ease and speed of installation.

Asked by Jason Macdonald
Posted Wed, 08/01/2012 - 23:47
Edited Fri, 11/30/2012 - 10:08

Tags:

5 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

That same question has been answered several times in this website. Do a search.

Answered by Armando Cobo
Posted Thu, 08/02/2012 - 00:09

2.
Helpful? 0

Jason,
1. We need to know your climate.

2. Read this article: Calculating the Minimum Thickness of Rigid Foam Sheathing.

Answered by Martin Holladay, GBA Advisor
Posted Thu, 08/02/2012 - 05:40

3.
Helpful? 0

Does it make a difference that the foam is to the interior of the sheathing? Typically, when rigid on the exterior of a wall is discussed, it involves the rigid being placed to the exterior of the wood sheathing, which is why thickness matters, because you want to keep the sheathing warm.

But in the ZIP sheathing case, how is it different than just adding additional insulation to the cavity, as the exterior of the sheathing is still exposed as in a typical wall? The perm rating for the 1" foam product is around 2 perms.

Thanks

Answered by Jill Neubauer Architects
Posted Fri, 11/30/2012 - 09:50

4.
Helpful? 0

Chris,
As long as you don't install a low-perm siding, it should be fine. (Examples of claddings that limit outward drying include adhered manufactured stone veneer and stucco with acrylic admixtures.)

Anyone who is worried about the ability of the sheathing to dry outwards should install a ventilated rainscreen gap between the siding and the sheathing. (Something that is always a good idea, by the way.)

Answered by Martin Holladay, GBA Advisor
Posted Fri, 11/30/2012 - 10:01
Edited Fri, 11/30/2012 - 10:11.

5.
Helpful? 0

Thanks Martin
We would be using cedar shingles probably over home slicker cedar breather.

Answered by Jill Neubauer Architects
Posted Fri, 11/30/2012 - 10:42

Other Questions in GBA Pro help

Zone 5 - Cathedral Ceiling

In Plans Review | Asked by Paul Szymanski | Sep 30, 14

How do you insulate cob or earth bag walls in the Northeast?

In Green building techniques | Asked by Aaron B | Sep 27, 14

Grid-tied without independence … what’s the point?

In General questions | Asked by flitch plate | Sep 29, 14

Windows for my Pretty Good House

In Green products and materials | Asked by Matt Mesa | Sep 29, 14

Please tell me why I have to put so much insulation / outsulation at the roof/celing?

In Energy efficiency and durability | Asked by leo kloop | Sep 30, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!