Potential problems regarding the use of ZIP System's new R-sheathing?

Does anyone see any potential problems using ZIP System's new R-Sheathing? The product comes in either 1/2" or 1" polyiso on the back of the sheathing between the sheathing and the studs. http://www.zipsystem.com/zip-system/rsheat.aspx.

Once again I am trying to figure out less costly ways to combat thermal bridging, create an air seal, and provide a rainscreen. I would be using the product with no interior vapor barrier therefore reducing the possibility for trapping moisture in the wall cavity.

However, is there the chance you would be creating a place for condensation to build between the foam and the studs? If I were to use the product I would use a product such as Rainslickr as a rainscreen for the ease and speed of installation.

Asked by cascobaybuilders
Posted Aug 1, 2012 10:47 PM ET
Edited Nov 30, 2012 9:08 AM ET

Tags:

5 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

That same question has been answered several times in this website. Do a search.

Answered by Acobo
Posted Aug 1, 2012 11:09 PM ET

2.

Jason,
1. We need to know your climate.

2. Read this article: Calculating the Minimum Thickness of Rigid Foam Sheathing.

Answered by user-756436
Posted Aug 2, 2012 4:40 AM ET

3.

Does it make a difference that the foam is to the interior of the sheathing? Typically, when rigid on the exterior of a wall is discussed, it involves the rigid being placed to the exterior of the wood sheathing, which is why thickness matters, because you want to keep the sheathing warm.

But in the ZIP sheathing case, how is it different than just adding additional insulation to the cavity, as the exterior of the sheathing is still exposed as in a typical wall? The perm rating for the 1" foam product is around 2 perms.

Thanks

Answered by chrish7763
Posted Nov 30, 2012 8:50 AM ET

4.

Chris,
As long as you don't install a low-perm siding, it should be fine. (Examples of claddings that limit outward drying include adhered manufactured stone veneer and stucco with acrylic admixtures.)

Anyone who is worried about the ability of the sheathing to dry outwards should install a ventilated rainscreen gap between the siding and the sheathing. (Something that is always a good idea, by the way.)

Answered by user-756436
Posted Nov 30, 2012 9:01 AM ET
Edited Nov 30, 2012 9:11 AM ET.

5.

Thanks Martin
We would be using cedar shingles probably over home slicker cedar breather.

Answered by chrish7763
Posted Nov 30, 2012 9:42 AM ET

Other Questions in GBA Pro help

Sub slab drainage details

In Green building techniques | Asked by William Costello | Feb 22, 17

Min. continuous insulation thickness vs fastening requirements

In General questions | Asked by Inger Peters | Feb 22, 17

Pink Sill Foam vs Green Treated Lumber

In Building Code Questions | Asked by Peter L | Feb 22, 17

Roof insulation for a West Baltimore row house

In Energy efficiency and durability | Asked by Timothy Werner | Feb 20, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!