Basement wall insulation

I recently glued 2' 4x8 (XPS) rigid foam to my basement walls. I cut pieces to fit between the joists and along the rim joist. I put pieces on top of the cement wall, and then foamed around all those pieces, and the bottom of the 4x8 sheet. I then installed a 2x4 wall in front of and touching the rigid foam.
Do I need to put unfaced batts in the bays ?

Thanks

Asked by Deb Malloy
Posted Mon, 11/26/2012 - 12:55

Tags:

4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Deb,
If your XPS is 2 inches thick, it has an R-value of R-10. That meets the minimum code requirement (according to the 2012 IRC) for basement walls in Climate Zone 3 and Climate Zone 4 (except Marine Zone 4).

If you live in Marine Zone 4 or Climate Zone 5, 6, 7, or 9, you are supposed to install at least R-15 insulation on your basement wall.

I think it is best to avoid the use of fiberglass batts to insulate a basement wall, so I would quit if I were you. However, if you live in a cold climate zone, you could try to move the studs away from the wall so that you can install more insulation. Alternatively, you could install rectangles of R-5 rigid foam between each pair of studs. The perimeter of each piece of rigid foam should be sealed with canned spray foam or caulk.

For more information on this topic, see How to Insulate a Basement Wall.

Answered by Martin Holladay, GBA Advisor
Posted Mon, 11/26/2012 - 13:16
Edited Mon, 11/26/2012 - 13:31.

2.
Helpful? 0

Thanks for the reply. I live in Rhode Island, which I think is zone 5. I had been told that if I didn't put batts, I would get condensation.

Answered by Deb Malloy
Posted Mon, 11/26/2012 - 13:51

3.
Helpful? 0

Deb,
Condensation problems are much more likely in walls in walls with fiberglass batts than walls with rigid foam. Considering the fact that you have apparently installed R-10 foam, you won't have a condensation risk.

R-15 would have been better (because R-15 would have reduced the rate of heat loss compared to R-10), but condensation won't be a problem.

Answered by Martin Holladay, GBA Advisor
Posted Mon, 11/26/2012 - 14:27

4.
Helpful? 0

Putting in unfaced batts will not increase or decrease the condensation or rot risk in the stud bays in your climate, and would cut your heat loss out of the basement walls by half. If there is a history of bulk-water intrusions, keep the bottom of the batt above the high-tide mark. Rock wool batts would be a better choice than fiberglass (the blue box store carries R15s), but the long-roll R13 fiberglass would be fine too.

If you take the cut'n'cobble approach with rigid foam between the studs recommended by Martin you can use reclaimed roofing foam (available from several MA/RI vendors- search craigslist materials for "rigid insulation", or if you feel like driving to Framingham MA with a truck there's always insulationdepot.com) which could cost even less than virgin-stock R13 batts, but are more work to trim, seal & install. (I did my basement in central MA with reclaimed 3" roofing iso held in place by furring through-screwed to the foundation on which to hang the gypsum, no studwalls or batts.)

Answered by Dana Dorsett
Posted Mon, 11/26/2012 - 14:53

Other Questions in GBA Pro help

In Energy efficiency and durability | Asked by Noah Byler | Jul 23, 14
In General questions | Asked by Paul Nicholls | Jul 22, 14
In Mechanicals | Asked by Kevin Ummel | Jul 24, 14
In PassivHaus | Asked by Scott Tenney | Jul 24, 14
In General questions | Asked by Roger Berry | Jul 24, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!