Strapping for dense pack cellulose

Looking for recommendations on the correct strapping spacing (12" or 16") to help prevent bulging with a dense pack cellulose installation on walls. We will be using Insulweb over 8" cavities, 16" on center framing.

Asked by jessie pratt
Posted Tue, 02/25/2014 - 10:57

Tags:

6 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Jessie,
Most people who install dense-packed cellulose in a wall cavity don't bother to install strapping; they just staple the heck out of the InsulWeb.

For more information, see How to Install Cellulose Insulation.

That article is an interview with Bill Hulstrunk. Here is an excerpt:

Q. How should air-permeable netting — for example, InsulWeb — be attached to the studs?

Hulstrunk: The best technique is to staple it with a pneumatic stapler right to the face of the stud. By ‘face,’ I mean the 1½-inch-thick edge of the stud facing the room. The staples have to be less than 1 inch apart, so you’ll go through a good number of staples.

Some installers prefer inset stapling or “lip stitching” — they put the staples at the corner of the studs, wrapping the InsulWeb a little bit around the corner as they staple. But that really isn’t necessary. I don’t like the lip-stitch method, because I want the insulation to be close to the sheetrock. Installers who use lip-stitching are usually worried about bulges, but we’ve found that an aluminum roller works well to eliminate any bulges.

There’s another method of installing the InsulWeb: using glue. First, you tack the InsulWeb up quickly. Then you apply watered-down Elmer’s glue to the studs through the InsulWeb, using a trim roller — you roll through the InsulWeb to push in the glue. It gets the InsulWeb really tight and nice. By the time you get to the last wall in the house, the first wall you glued is usually dry enough to start blowing cellulose. It’s best to wait at least 6 hours for the glue to dry.

Q. What do you do about bulges?

Hulstrunk: After you’re done blowing the walls, the material will be bulged out a little bit between the studs — maybe out an inch or so in the middle. So you take an aluminum roller — it’s about 1 foot long, maybe 3 inches in diameter, and sold specifically for this purpose — and you roll the bulge really quickly. If you do it right, it will leave the cellulose flat, and a long metal straightedge will touch the studs. We recommend that owners or builders include this language in their wall insulation specs: “The material will be rolled flat, ready for drywall.”

Answered by Martin Holladay, GBA Advisor
Posted Tue, 02/25/2014 - 11:25

2.
Helpful? 0

Good advice. When done right, sheetrock installation is only a bit harder than normal. You don't need (or want) strapping.

Answered by David Meiland
Posted Tue, 02/25/2014 - 11:43

3.
Helpful? 0

Thanks for steering me to that article Martin. In our area it has been difficult to find a contractor that is familiar with blowing cellulose in at a density greater than 3 lbs/cubic foot and express concern with bulging if the cellulose is installed at a greater density. They have recommended strapping to deal with the bulging. But it sounds like it is totally unnecessary... Great!

Answered by jessie pratt
Posted Tue, 02/25/2014 - 16:28

4.
Helpful? 0

You can make things a bit easier by using 5/8" drywall, but it's by no means necessary.

Answered by David Meiland
Posted Tue, 02/25/2014 - 17:27

5.
Helpful? 0

Jessie,
I just finished dense packing my new home about a month ago - 10" double stud walls. Definitely face staple to the 1-1/2" dimension of the stud and be sure staples are very close together and the netting is tight. I started by lip stitching the staples to the side of the studs and it was very fussy and ultimately not needed. I would not plan to strap walls as it provides a chase for air movement in the walls. You really want the back of the drywall to be in direct contact with the cellulose to minimize air movement. Instead, plan for 5/8" drywall on the exterior insulated walls to address the bulging. My drywall sub only charged me the material cost difference between 1/2" sheets and 5/8" sheets. For a 2,000sf house that came to be $250+/-. You will need the roller that Martin and Bill Hulstrunk mention. I would highly recommend working with National Fiber and Bill Hulstrunk if possible.

Answered by Christopher Vernott
Posted Tue, 02/25/2014 - 19:07

6.
Helpful? 0

A services chase behind the drywall would be ideal, strapping is OK....don't ya think? Nothing wrong with air behind the drywall if your insulation and air sealing is done right. No penetrations makes for an airtight wall.

Answered by T Shepp
Posted Tue, 02/25/2014 - 21:22

Other Questions in GBA Pro help

In Energy efficiency and durability | Asked by Matthew Michaud | May 2, 14
In General questions | Asked by Guillaume Dumont | Sep 1, 14
In Green building techniques | Asked by Silas Hoeppner | Sep 1, 14
In Green building techniques | Asked by Mark McKenzie | Sep 1, 14
In General questions | Asked by Jeannette Sirois | Sep 1, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!