Air sealing CMU walls that are exposed inside and out in tropical climate

I'm looking for an effective membrane and/or application to air seal a home with walls made up entirely of exposed CMU.

I'm working on the mechanical systems design and spec for the home and advising the builder to lower the infiltration so we can keep latent loads to a minimum. I am not interested in R-Value.

The 5,000 s.f. home is located on a very small private island just north of Exuma, Bahamas, and it is surrounded by ocean. The interior and exterior finish of the home is exposed CMU.

Design temperatures range is between 60 F and 90 F, and the RH range is between 50 and 90%. I'm using "Nassau AP New, BS" weather station as a basis, if this helps, and adjusting it for more exposed conditions that's about 150 miles south by southeast (slightly higher temp and RH).

There are many good options that I'm already aware of, but I just want to know if I'm missing an opportunity with something more appropriate to this application and location.

Thank you all, in advance.

Asked by Chris Laumer-Giddens
Posted Jul 8, 2014 7:29 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Chris,
The standard material for air sealing CMU walls is plaster. It can be installed on the interior (in which case it is usually called plaster) or on the exterior (in which case it is usually called stucco) or both.

Fortunately, construction workers in the Caribbean and nearby islands are very familiar with stucco.

Exterior stucco is usually cementitious (Portland-cement-based), but you can use a synthetic stucco if you prefer. Interior plaster can be cemetitious or plaster-based.

If you need an on-site consultant or surpervisor for construction work in the Bahamas, my per-diem rates are reasonable.

Answered by Martin Holladay, GBA Advisor
Posted Jul 8, 2014 7:53 AM ET
Edited Jul 8, 2014 7:55 AM ET.

Other Questions in GBA Pro help

Basement slab perimeter insulation

In General questions | Asked by Nicholas C | May 28, 15

Spaceloft my only option?

In GBA Pro help | Asked by Jan Verschuren | May 29, 15

Insulation and mechanical upgrades

In Mechanicals | Asked by Jeffrey S | May 29, 15

How to air seal from interior with pine siding?

In Green building techniques | Asked by christian routh | May 29, 15

Minisplit in tandem with a conventional heat pump?

In Mechanicals | Asked by Dean Wiley | May 27, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!