Air sealing CMU walls that are exposed inside and out in tropical climate

I'm looking for an effective membrane and/or application to air seal a home with walls made up entirely of exposed CMU.

I'm working on the mechanical systems design and spec for the home and advising the builder to lower the infiltration so we can keep latent loads to a minimum. I am not interested in R-Value.

The 5,000 s.f. home is located on a very small private island just north of Exuma, Bahamas, and it is surrounded by ocean. The interior and exterior finish of the home is exposed CMU.

Design temperatures range is between 60 F and 90 F, and the RH range is between 50 and 90%. I'm using "Nassau AP New, BS" weather station as a basis, if this helps, and adjusting it for more exposed conditions that's about 150 miles south by southeast (slightly higher temp and RH).

There are many good options that I'm already aware of, but I just want to know if I'm missing an opportunity with something more appropriate to this application and location.

Thank you all, in advance.

Asked by Chris Laumer-Giddens
Posted Jul 8, 2014 6:29 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
0 Helpful?

Chris,
The standard material for air sealing CMU walls is plaster. It can be installed on the interior (in which case it is usually called plaster) or on the exterior (in which case it is usually called stucco) or both.

Fortunately, construction workers in the Caribbean and nearby islands are very familiar with stucco.

Exterior stucco is usually cementitious (Portland-cement-based), but you can use a synthetic stucco if you prefer. Interior plaster can be cemetitious or plaster-based.

If you need an on-site consultant or surpervisor for construction work in the Bahamas, my per-diem rates are reasonable.

Answered by Martin Holladay, GBA Advisor
Posted Jul 8, 2014 6:53 AM ET
Edited Jul 8, 2014 6:55 AM ET.

Other Questions in GBA Pro help

Poly on interior wall

In Energy efficiency and durability | Asked by Nicholas C | Jan 31, 15

Adding A/C to 1918 built home

In Mechanicals | Asked by Brian Forney | Jan 31, 15

How do I keep my sheathing dry?

In Energy efficiency and durability | Asked by David Baerg | Jan 30, 15

Freeze risk for a heat pump water heater in an unconditioned garage

In Mechanicals | Asked by Nathaniel G | Jan 31, 15

Does code require fireproof caulk around electrical boxes & light switches?

In Building Code Questions | Asked by Robert Hallenbeck | Jan 31, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!