I am doing a finished basement that has a perimeter drain (see photo). To clarify, I want to put a stud wall along the edge of the perimeter drain. I purchased some 2.5-inch felt backed poly-iso and had intended to stud against it. Do I put the 2.5-inch rigid foam on the cinder block wall (it would be over the drain), and then add the stud wall to meet the rigid foam? Would dimple membrane be needed or would any condensation run down the foam board into the french drain to the sump? Walls are painted with drylock; no water problems in basement with sump working in heavy rain. I need advice on best method. Thanks for any suggestions.

RJ

20170317_115105.jpg1.63 MB
Asked by Rasheed Warith
Posted Nov 14, 2017 7:25 PM ET

Tags:

5 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Rasheed,

Where are you located? Advice is often climate-specific.

Answered by Steve Knapp CZ 3A Georgia
Posted Nov 14, 2017 7:38 PM ET

2.

Sorry. I'm located in Cleveland, Ohio area (Climate Zone 5A)

RJ

Answered by Rasheed Warith
Posted Nov 15, 2017 8:20 AM ET

3.

Hi Rasheed,

You would not want to apply the polyisocyanurate directly against the wall since it can absorb moisture and the perimeter drain suggests you have an ongoing water management issue.

There are a number of threads on GBA that discuss using dimple matt to create an air space between the foam and the wall. Search on terms such as wet basement and dimple matt. Here is a link to get you started: http://www.greenbuildingadvisor.com/community/forum/green-building-techn...

Answered by Steve Knapp CZ 3A Georgia
Posted Nov 15, 2017 8:48 AM ET

4.

Steve,

Thanks you so much for your help. Your recommendation makes sense. Walls being dry today don't guarantee tomorrow during a 100 yr storm. With a basement finishing project to follow, it is certainly better to be safe than sorry and for a 200 sf basement the extra cost is worth the peace of mind.

RJ

Answered by Rasheed Warith
Posted Nov 16, 2017 7:50 AM ET

5.

Resheed,
I agree with Steve. If you have an interior drain, the dimple mat is a good idea.

Answered by Martin Holladay
Posted Nov 19, 2017 9:29 AM ET

Other Questions in General questions

Rim Joist External Insulation and Air Barrier - How To?

In Energy efficiency and durability | Asked by Lance Peters | Jan 21, 18

Radon 9.3 pCi/L even after radon mitigation-is this OK??

In GBA Pro help | Asked by hotandhumid | Jan 22, 18

Where can I get a forced air heating wall vents that can be 100% sealed shut?

In Green products and materials | Asked by Bryce Nesbitt | Jan 22, 18

Header hangers vs. jack studs: Thermal bridging?

In Energy efficiency and durability | Asked by Lance Peters | Jan 21, 18

Finishing a finished basement

In General questions | Asked by Mark F | Jan 23, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!