We live outside Philadelphia and have had a very cold winter. We had a mini split uint installed in a newly expanded room and blocked the two forced air ducts from the old portion of the room. The floor temperature is vastly different than that coming out of the unit.
A few details. Home was built in 1954. Half of the room (old section) is over an inaccessible crawl space. I has a flat ceiling and a ceiling fan. It has one outside wall.
The new half of the room is over an insulated slab, well insulated 2x6 walls and a cathedral ceiling with a ceiling fan on a 24" down rod. All walls are exposed. Total room size is 270 sq.ft. including a 3x12 foot closet.
This is a guest room but we have a desk and TV so it is used a few days a week.
The Carrier mini split is located in the new section close to the old section. More recently we have been running the unit 24 hours a day. We also have the fans running on low speed. The temperature difference at coffee table height is about 8 degrees lower than the unit. On the floor is is about 12 degrees or colder on extreme days.
The bottom floor is the floor is cold. Should we increase the fan motion or are there other suggestions for this situation.
Thanks for any advice.

IMG_2172.JPG86.83 KB
Asked by Bob Whitemarsh
Posted Feb 10, 2018 12:39 PM ET
Edited Feb 11, 2018 5:49 AM ET

Tags:

7 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

View of Mini Split

IMG_3849.JPG
Answered by Bob Whitemarsh
Posted Feb 10, 2018 12:43 PM ET

2.

The fan only induces wind chill, requiring temperatures to be higher for the same comfort levels. If you're cold, turn it off.

If the floor is cold it's probably due to lack of foundation insulation on the crawlspace walls, &/or air leakage on the first floor &/or air leakage out of the top levels of the house somewhere. As lighter warm air escapes out the top, it pulls cold air into leaks further down. Air sealing and insulating the foundation can make huge difference, as can stopping the air leaks out the top floor ceiling, or leaky fireplace flues, plumbing chases that extend from the basement or crawlspace to attic, etc.

It's pretty normal for the temperatures detected at the head to be considerably different than at floor or coffee-table during the heating season when it's mounted high on the wall like that. Directing the vanes to blow more downward or setting the blower speed higher helps with the stratification issues, but there will still be an offset. Just turn it up until you're comfortable, and don't think about the number on the remote control relative to the number on the thermometer on the coffee table. If it bothers you, there may be a compatible wall thermostat for that unit. (If not Carrier, Gree, the likely manufacturer of that unit may have something.)

Answered by Dana Dorsett
Posted Feb 10, 2018 3:04 PM ET
Edited Feb 10, 2018 3:04 PM ET.

3.

In my experience stratification is a significant comfort issue. I've found that here in HZ5 in houses with heat coming from ceiling registers, the air around my head feels stuffy and hot while overall I feel cold. I'm worried because the house I'm planning will be heated with a wall mounted mini-split. Is the issue moot if the house is insulated and sealed to high performance standards? Also, since my design has vaulted ceilings I'm counting on fans to reduce stratification. In my experience, if the fans are set to "winter mode", i.e. blowing upward, I do not feel any drafts.

Douglas Higden

Answered by thrifttrust
Posted Feb 10, 2018 3:46 PM ET

4.

0check out the bottom of that door, sweeps fail quickly and an air leak under the door will cause the whole floor to be cold

Answered by Keith Gustafson
Posted Feb 10, 2018 5:19 PM ET

5.

ASHRAE standards confirm that that much stratification is a comfort problem.

You can check if infiltration is an issue by pressurizing the room via the interior doorway (ie, a makeshift blower door).

Floor insulation can be checked by comparing IR temps at different places (with the fan off).

Or check for both issues with a thermal camera.

I don't know - perhaps stratification needs to be kept in mind as a drawback to mini-splits for heating.

> fans are ... blowing upward, I do not feel any drafts.

I agree, but I don't think they will do a good job of de-stratification that way - airflow needs to reach the floor. On the other hand, it should be possible to build something to pull air from the floor level and exhaust it horizontally at the ceiling - creating no detectable draft for occupants. Bob might put it in the closet.

Answered by Jon R
Posted Feb 10, 2018 6:17 PM ET
Edited Feb 10, 2018 6:18 PM ET.

6.

Bob,
My instincts tell me that this isn't a minisplit problem. This is an air sealing problem.

There is a good chance that this room has holes near the ceiling allowing interior air to escape, and holes near the floor allowing cold air to enter.

If the room had a good air barrier and adequate insulation, you wouldn't be getting the stratification you are reporting.

Answered by Martin Holladay
Posted Feb 11, 2018 5:20 AM ET

7.

What Martin said- fix the air leakage and the stratification will be less. If there's truly an 8-12F difference in temp between the floor and ~8' level where the wall coil's air intake it almost has to be an uninsulated crawlspace that also leaks copious amounts of air. (Measure the temperatures with air thermometers, not the thermistor inside the mini-split, and not an infra-red thermometer.)

The room in the picture looks like it's no more than 11-12' from the floor to the highest point in the gable, not some 20-25' "great room" tower, that might need mechanical de-stratification.

Answered by Dana Dorsett
Posted Feb 11, 2018 2:02 PM ET

Other Questions in General questions

How exterior air seal at chimney to wall interface? Chimney spalling.

In Energy efficiency and durability | Asked by Mike McLaine | Feb 18, 18

Fiberglass window choices for new build in Colorado

In General questions | Asked by LYDIA SEGAL | Feb 19, 18

Innie/outie window operation

In Plans Review | Asked by Ethan T | Feb 20, 18

Lessons learned from exterior basement insulation retrofit

In Green building techniques | Asked by Mike McLaine | Feb 3, 18

Insulation upgrades

In Energy efficiency and durability | Asked by Justin Brown | Jan 22, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!