My first question is.... can anyone recommend a home energy expert local to me in San Francisco Bay Area (zone 3c)?

My 1100 sqft flat roof has both roof joists and ceiling joists with blown-in cellulose filling the ceiling joist cavity, and about 15" of space between joists. I have 2 soffits (about 6x12" each) on one side of the house, one skylight is permanently vented and overlaps with attic space, and there is a louvre vent in an interior closet (which doubles as access hatch).

From reading GBA, I need better attic venting. From reading this site, I need less (zero) venting and stay away from foam. I have plans to re-roof this year or next, probably with SPF, so I'd like to get venting taken care of before that happens.

Asked by DAVID BIANCO
Posted Jun 7, 2018 12:24 PM ET

Tags:

5 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

David,
The anti-foam bias reflected on the website of 475 High-Performance Building Materials is based on tenuous arguments, not building science. You should make your own decision concerning rigid foam insulation. Especially if you choose to use reclaimed (recycled) rigid foam, it's an environmentally responsible choice.

For information on whether or not flat roofs should be vented, and instruction in ways to insulate a flat roof with rigid foam above the roof sheathing, see this article: Insulating Low-Slope Residential Roofs.

Answered by Martin Holladay
Posted Jun 7, 2018 12:42 PM ET
Edited Jun 7, 2018 12:43 PM ET.

2.

Thanks for the quick reply. As a consumer trying to educate myself, its hard to know who is "right". I'm a fan of GBA, but I don't have a reference point. Similar, some sites say 1:300 for roof venting, others say 1:150. (Hence my desire to talk to someone local)

The article Martin linked was one I had read before, and I should have linked in my orig post. One question, is there any pro/con to buying one of these vents from home depot [LINK] vs building a 2x2' doghouse with rectangular vents?

Answered by DAVID BIANCO
Posted Jun 7, 2018 7:53 PM ET
Edited Jun 7, 2018 7:54 PM ET.

3.

David,
Without wading into the debate as to what approach works best, can I suggest you first evaluate the alternatives in terms of whether they meet your building code. Some flat roof assemblies, which may work perfectly well, don't meet present codes.

Answered by Malcolm Taylor
Posted Jun 7, 2018 8:42 PM ET

4.

The 1:150 and 1:350 rates come straight from the 2015 Residential Code. The default requirement for vented attics is 1:150. For attics that have vapor retarders facing the conditioned space and have balanced low and high ventilation (ridge and soffit venting), you can use 1:300.

Answered by Peter Engle
Posted Jun 7, 2018 9:18 PM ET

5.

David,
Q. "Some sites say 1:300 for roof venting, others say 1:150."

A. The 1:300 ratio is for roofs with soffit venting and ridge venting. The 1:150 ratio is for roofs with soffit venting only. For more information on code requirements for attic venting, see "All About Attic Venting."
Q. "Is there any pro/con to buying one of these vents from home depot [LINK] vs building a 2x2' doghouse with rectangular vents?"

A. The link you provided shows a mushroom vent. You definitely want a well-built doghouse (vented cupola), not a mushroom vent. Mushroom vents are associated with poor performance and water-entry problems -- which is precisely why Lstiburek recommends the doghouse approach.

Answered by Martin Holladay
Posted Jun 8, 2018 9:21 AM ET

Other Questions in General questions

Plumbing too close to edge of slab

In Project management | Asked by Hugh Stearns | Jun 18, 18

Do I need an HRV/ERV for a house built in 1947?

In Mechanicals | Asked by Will82 | Jun 14, 18

Building code requirements for stacked window headers, bracing, and stucco over foam

In Building Code Questions | Asked by Zane Bridgers | Jun 17, 18

Brick house insulation

In Green building techniques | Asked by Sebastian Smith | Dec 29, 17

HVAC duct size versus grille size

In Mechanicals | Asked by Richt1022 | Jun 18, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!