HRV or ERV or neither?

we are building a small 600 sq' house in valemount, b.c.. we are planning to make it airtight via the plywood sheathing. should we use an hrv or erv or exhaust-only with passive air inlets? anyone care to recommend a cost-efficient manufacturer? also, interested in a detail of a ground loop for the intake air...thanks
other site info: 800 metre elevation, 5623 HDD

Asked by erik olofsson
Posted Mon, 08/13/2012 - 14:40
Edited Mon, 08/13/2012 - 15:17

Tags:

8 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Eric,
Have you read these two articles?

Designing a Good Ventilation System

HRV or ERV?

Answered by Martin Holladay, GBA Advisor
Posted Mon, 08/13/2012 - 15:16

2.
Helpful? 0

martin, we have installed a couple of hrv's in the town where we are presently building. my father, the plumber, and the heating guy still debate the merits of the system to this day. i am NOT a HVAC contractor nor are there any around where we are building so that is why i am hoping some of the guys at gba might be able to help me chose a model. does it make any sense to duct the cold intake air through the ground before it reaches the hrv? i am referring to a really low-tech detail here...

Answered by erik olofsson
Posted Mon, 08/13/2012 - 17:16

3.
Helpful? 0

Erik, low tech that works equals using a Panasonic bath fan when needed either semi automatically or manually. All other ideas cost more and are more complicated and some ideas sound good but are horrible in practice too often such as ground tubes.

Keep it simple, to keep it functioning, and cost effective.

Answered by aj builder, Upstate NY Zone 6a
Posted Mon, 08/13/2012 - 17:55

4.
Helpful? 0

Eric,
Q. "i am hoping some of the guys at GBA might be able to help me chose a model."

A. If you read the article I linked to -- "HRV or ERV" -- you'll see that I recommended two possibilities. I wrote, "If energy efficiency is your most important criterion — and I believe it should be — choose either the UltimateAir RecoupAerator 200DX ERV (which draws 40 watts to deliver 70 cfm, or 1.75 cfm/watt) or the Venmar EKO 1.5 HRV (which draws 24 watts to deliver 49 cfm, or 2.04 cfm/watt)."

Q. "Does it make any sense to duct the cold intake air through the ground before it reaches the HRV?"

A. No. To understand why, see Belgian Passivhaus is Rendered Uninhabitable by Bad Indoor Air.

Answered by Martin Holladay, GBA Advisor
Posted Mon, 08/13/2012 - 18:11

5.
Helpful? 0

does anyone have any experience with hrv's made by eneready..?

Answered by erik olofsson
Posted Sat, 08/18/2012 - 23:19

6.
Helpful? 0

Panasonic Whispercomfort FV-04VE1

Answered by aj builder, Upstate NY Zone 6a
Posted Sun, 08/19/2012 - 12:51

7.
Helpful? 0

Martin,
It's time to update your data on ERV- HRV performance image!
http://www.renewaire.com/images/stories/Literature/ecm_manual.pdf
For example the EV450 with ECM motor simply blows away the competition in CFM / watt with 200CFM on 60 watts ( 3.33 CFM/watt) with 0.2" wc duct loading. This is normally a "commercial unit & designed to move 450CFM but can be operated at 200 CFM. Even at 450CFM if duct resistance is 0.16" WC it only draws 327 watts or 1.38 CFM/watt. This unit needs to flow at least 200 CFM, if less is needed it must be done by 'duty cycle' so any less than 200 CFM is still 3.33CFM/watt.

Answered by Jerry Liebler
Posted Wed, 08/22/2012 - 19:52
Edited Wed, 08/22/2012 - 20:19.

8.
Helpful? 0

Jerry,
That's a commercial unit, and is seriously oversized for most homes. You're right that it can be operated with a timer, so that (for example) it comes on for 20 minutes each hour -- an option that is worth considering for those who like the cfm/watt rating.

Answered by Martin Holladay, GBA Advisor
Posted Thu, 08/23/2012 - 05:29

Other Questions in General questions

Is a gas fireplace blower fan an energy-efficient investment?

In General questions | Asked by W. Timothy Ward | Dec 20, 14

Wet OSB - how much water can it take?

In General questions | Asked by colleen1 runyen | Dec 17, 14

Mechanical room size

In Mechanicals | Asked by Corey B | Dec 20, 14

Polyiso for basement

In Green building techniques | Asked by sr kod | Dec 20, 14

Solar thermal systems for heating water

In Mechanicals | Asked by aj builder, Upstate NY Zone 6a | Dec 15, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!