Attic trusses - insulation question

Followup for clarification on at ICF home with attic trusses. I do plan to insulate the attic truss floor for two reason. !st is for noise reduction and the other is that this area will only ocassionally be occupied and will have reduced temps most of the time. Can I get away with spry foaming the roof trusses soffit to soffit with 2" and then putting in batt insulation to fill the cavity. I do plan to very soon finish this area so do I also need to insulated the side walls of the room if the rafters are already filled with insulation.

Jim

Asked by Jim McKay
Posted Nov 22, 2012 9:58 AM ET
Edited Nov 22, 2012 10:48 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Jim,
The R-value of 2 inches of spray foam depends on what type of foam you use. Two inches of closed-cell spray polyurethane foam has an R-value of R-12 or R-13. Your suggested approach is called "flash and batt." You proposed approach will only work if you live in climate zone 1, 2, 3, or 4C. If you live in climate zone 4A or 4B, or anywhere colder, you need more spray foam.

These provisions are detailed in section R806.4 of the 2009 IRC. Everything you need to know is explained in the article I linked to before, Creating a Conditioned Attic, which I suspect you may not have read. If you need more information on this issue, check out How to Build an Insulated Cathedral Ceiling.

Answered by Martin Holladay, GBA Advisor
Posted Nov 22, 2012 10:44 AM ET
Edited Nov 22, 2012 10:46 AM ET.

Other Questions in General questions

Step-By-Step Solutions Of World Of Tanks Gold Cheats Download

In Webinar Follow-up Q&A | Asked by Rhea Jay | Mar 29, 15

Cold climate (6) standing seam metal roof leak

In Energy efficiency and durability | Asked by David Metzger | Mar 28, 15

I need assistance with window/door install with 4" foam

In Green building techniques | Asked by tim brown | Mar 28, 15

How to insulate a condo concrete floor?

In Energy efficiency and durability | Asked by NORM DITTER | Mar 29, 15

Interior plywood for earthquake areas, can replace vapor retarder?

In General questions | Asked by Jan Verschuren | Mar 29, 15
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!