Roof venting

We are building a 3/12 shed roof with parallel trusses North of Ottawa (zone 6-7). The roof is sloping to the South. We're wondering about potential for venting problems during winter with North and NE winds, as we think the wind catching the North wall will disrupt the normal venting of the roof. The site is fairly protected but these winds will blow on and off throughout the winter.

Asked by 415irwin
Posted Nov 23, 2012 10:53 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Jessie,
As long as your roof assembly is well built -- with appropriate insulation that is installed well, and a ceiling that is fairly airtight -- there is no reason to worry.

If you are depending on the effectiveness of its ventilation layer to keep your roof assembly from failing, something is probably wrong with the quality of your work or your choice of materials. Roof ventilation is much less important than most people think.

For more information on this topic, see How to Build an Insulated Cathedral Ceiling.

Answered by user-756436
Posted Nov 24, 2012 5:27 AM ET

Other Questions in General questions

SIP roof issues

In General questions | Asked by Matt Melton | Feb 17, 17

Roxul Comfortboard to create cathedral ceiling baffle?

In Green building techniques | Asked by Blake Cote | Feb 23, 17

National Fiber in Belchertown, Mass.

In Green products and materials | Asked by Scott Mangold | Feb 21, 17

Installing LP Smartside over foam and 24 inch centers

In Green building techniques | Asked by William Costello | Feb 17, 17

New home wall assembly

In Energy efficiency and durability | Asked by Michael Winn | Feb 11, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!