Roof venting

We are building a 3/12 shed roof with parallel trusses North of Ottawa (zone 6-7). The roof is sloping to the South. We're wondering about potential for venting problems during winter with North and NE winds, as we think the wind catching the North wall will disrupt the normal venting of the roof. The site is fairly protected but these winds will blow on and off throughout the winter.

Asked by jessie pratt
Posted Nov 23, 2012 11:53 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Jessie,
As long as your roof assembly is well built -- with appropriate insulation that is installed well, and a ceiling that is fairly airtight -- there is no reason to worry.

If you are depending on the effectiveness of its ventilation layer to keep your roof assembly from failing, something is probably wrong with the quality of your work or your choice of materials. Roof ventilation is much less important than most people think.

For more information on this topic, see How to Build an Insulated Cathedral Ceiling.

Answered by Martin Holladay
Posted Nov 24, 2012 6:27 AM ET

Other Questions in General questions

Dense Packing Cellulose with the Krendl 425

In Energy efficiency and durability | Asked by Joe Duchek | May 23, 17

Average lighting, appliance and plug loads for PV sizing?

In Mechanicals | Asked by Burke Stoller | May 23, 17

Opinions on my exterior options

In Energy efficiency and durability | Asked by Jeremy Archer | May 15, 17

Sealing PT sill plate to concrete slab ?

In Energy efficiency and durability | Asked by Mark McFarlane | May 20, 17

How to deal with duct-work that installed in unconditioned attic and a powered attic ventilator?

In Energy efficiency and durability | Asked by TedLiu | May 22, 17
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!