Atticat expanding blown-in insulation

we are considering using blown fibreglass for the attic insulation in our r2000 project. the small village where our project is located has tje atticat system. another town 1.5 hours away has the blown cellulose system. basically, for the price of 24" deep cellulose we could get 36" of fibreglass. from what i have read on the gba, i would guess the majority of the gba folk prefer cellulose over fibreglass. i'm tempted to go with the fibreglass...opinions? is 36" too thick for fibreglass?...thanks again! p.s., the attic floor is 5/8" t+g osb and is flat. an energy heel allows minimum r40 above the walls.

Asked by erik olofsson
Posted Mon, 01/28/2013 - 19:02
Edited Mon, 01/28/2013 - 19:36

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Erik,
As you probably know, Atticat is a brand name for blown-in fiberglass insulation. In general, cellulose does a better job of limiting convection currents than blown-in fiberglass. But if you can't get a good price on cellulose, and if you are able to install a full 36 inches of fiberglass insulation, the fiberglass should work fine.

As with any insulation job on an attic floor, it's important to seal any air leaks in the ceiling before installing the insulation.

For more information on this topic, see:

GBA Encyclopedia: Blown-In or Loose-Fill Insulation

Blown Insulation for Attics: Fiberglass vs. Cellulose

Answered by Martin Holladay, GBA Advisor
Posted Tue, 01/29/2013 - 08:47

2.
Helpful? 0

If the energy heels are only tall enough to allow ~12" .R40 at the edges there's very little additional benefit to heaping a full 36" in the middle- the heat loss will be dominated by the attic area near the eaves. If you can get the full 36" all the way out to the edges over the tops of the studwall plates, by all means, go for the full 36!

Answered by Dana Dorsett
Posted Tue, 01/29/2013 - 16:49

3.
Helpful? 0

At R 60, cellulose generally has a settled R value about 25% greater per inch than blown fiberglass. I don't have tech references for greater depths, but would guess that 36" deep cellulose would have about 30% greater R value per inch (extrapolating wildly from existing data).

Answered by Jesse Smith
Posted Tue, 01/29/2013 - 19:27

Other Questions in General questions

ThermoCore Roof SIPs - 8" Panels

In Green products and materials | Asked by Peter L | May 5, 14

Looking at using black sheathing for air sealing /baffles cathedral roof

In Green building techniques | Asked by Geoff Frood | Nov 26, 14

Insulating a cathedral ceiling

In Energy efficiency and durability | Asked by jon cypert | Nov 25, 11

Poly under slab and over sill ?

In Energy efficiency and durability | Asked by Jocelyn Smith | Nov 25, 14

Most sesible heating system for a new house build on Vancouver Island

In Mechanicals | Asked by Blake Klopfenstein | Nov 26, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!