Cause of water within an unconditioned space?

I have a situation in an existing building where water is building up on the underside of an exterior steel pan/concrete tread stair. The space below is an enclosed, unconditioned storage room. I'm assuming the water is from condensation due to the temperature differential between the exterior and interior surfaces.

I'm thinking of insulating the underside of the stair but want to confirm this is the best solution. Or, are there other ideas, such as vapor retardant paint which could work as well.

Asked by Bruce Scott
Posted Mon, 01/13/2014 - 14:34
Edited Mon, 01/13/2014 - 15:43

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Bruce,
It's hard for me to visualize. Does this room have a ceiling? Or is the room exposed to the sky?

Is the steel stairway the only ceiling on this room?

If the steel stairway is the room's ceiling, and there is no insulation under the stair treads and risers, then your suggested solution will work. You need to install some foam insulation to separate the cold risers and treads from the room below.

Answered by Martin Holladay, GBA Advisor
Posted Mon, 01/13/2014 - 14:45

Other Questions in General questions

In General questions | Asked by Robert Kohaus | Sep 1, 14
In General questions | Asked by Jin Kazama | Aug 28, 14
In General questions | Asked by Jeff Watson | Jul 12, 14
In Energy efficiency and durability | Asked by Matthew Michaud | May 2, 14
In GBA Pro help | Asked by Pamela Davidson | Aug 31, 14
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!