Is it okay to put an unvented hot roof under a wood shingle roof?

I have a wood shingle roof directly over tongue and groove sheathing. Can I put an unvented hot roof under the shingles? My plan is to put five inches of ISO directly on the underside of the sheathing. I cannot find anything on the Internet that discusses this issue. I live on Cape Cod. Thank you for your help.

Asked by Randy Aubrecht
Posted Jun 18, 2014 9:41 PM ET


5 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.

For the most long-lasting installation of cedar roof shingles, the shingles should be installed over skip sheathing, so that there is some air behind the shingles. This allows the shingles to dry from the back side as well as the top side.

If the shingles are installed over continuous board sheathing, you don't want any insulation on the interior side of the sheathing. You want the sheathing boards to be able to dry towards the attic.

So I don't think your plan is a good one.

The method you are proposing is called "cut and cobble." The cut-and-cobble method is not recommended for unvented cathedral roof assemblies. For more information, see Cut-and-Cobble Insulation.

Answered by Martin Holladay, GBA Advisor
Posted Jun 19, 2014 7:01 AM ET


Thank you Martin for your advice. I have two other questions. Would it make a difference if I put three inches of ISO and then spray two inches of closed cell foam over the top? Second would this technique work if I replaced the wood roof with fiberglass?

Answered by Randy Aubrecht
Posted Jun 19, 2014 9:35 PM ET


If you seal everything up with at least 2 inches of closed-cell spray foam, your roof assembly is less risky. But you still need a vent channel under the sheathing if you have cedar shingles.

You have several possible choices here. One method is to include a vent channel under the roof sheathing, connected to soffit vents and ridge vents. Another possibility, as you noted, is to use a different kind of roofing.

No matter what you do, you want to strive to install at least the minimum code required R-value, which is R-38 in your climate zone.

For more information on all of your options, see How to Build an Insulated Cathedral Ceiling.

Answered by Martin Holladay, GBA Advisor
Posted Jun 20, 2014 4:08 AM ET


Thank you for your help.

Answered by Randy Aubrecht
Posted Jun 20, 2014 5:33 AM ET


Massachusetts state building codes are based on IRC2009 & IECC2012, the latter of which specifies R49 as the code min for attics.



You have another 2 weeks before that takes effect.

Answered by Dana Dorsett
Posted Jun 20, 2014 6:22 PM ET
Edited Jun 20, 2014 6:25 PM ET.

Other Questions in General questions

Struggling with how to use foam on walkout over Canadian shield zone 7

In Green building techniques | Asked by tim brown | Aug 18, 15

Anyone familiar with Insultex house wrap?

In Green products and materials | Asked by Marcus Sheffer | Jul 31, 15

How is thermal bridging prevented?

In General questions | Asked by S. Schneider | Oct 5, 15

Solar hot water system with oil heat, one hot water tank or two?

In Mechanicals | Asked by Audrey Considine | Oct 5, 15

Wood burning stove below - what to do?

In General questions | Asked by Mary Schwaba | Oct 6, 15
Register for a free account and join the conversation

Get a free account and join the conversation!
Become a GBA PRO!