Which method for re-insulating a skylight shaft?

I got some basic ideas from Martin's fine article here: http://www.finehomebuilding.com/design/departments/energy-smart-details/...

Armed with that information, I am contemplating some various methods to re-insulate and seal several skylight shafts in my attic. These shafts were originally insulated using faced fiberglass batts that were somewhat haphazardly installed. After 18 years the strapping has deteriorated, and some of the batts have turned away from the sheetrock. And as can be seen in the photos, there are areas where the exposed sheetrock is clearly visible.

One thing that makes it all a bit disturbing is that the framing for the shafts were done "on the flat" instead of on edge, resulting no real cavity to house the batts properly.

In my case the options I'm considering are as follows:

1. Keep the fiberglass, and fur out the framing to accept the full width of the batts without compression. I would then cover the batts with rigid foam board of some kind, and air seal the whole assembly.

2. Do away with the fiberglass, and install pieces of foam board in the 1 1/2" spaces provided by the "flat framing", then cover the entire framing with layers of rigid foam board of some kind, sufficient to give me a respectable R-value. And I would air seal the whole assembly.

3. Do away with the fiberglass, and have the shafts sprayed with closed cell foam. Sounds like the easiest and perhaps the best method. But surely the most costly I would think (?)

I am aware of the possible code requirements for a fire barrier for the foam board in these first two proposed methods of installation. I'm checking with a friend who is an inspector for a definitive answer on that for my locale.

Any opinions would be greatly appreciated! I'm sure there are things I haven't considered.

I'm in Zone 2 BTW….

photo 1-1.JPG945.91 KB
photo 1.JPG982.65 KB
Asked by Tommy Detamore
Posted Thu, 08/21/2014 - 09:27

Tags:

3 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.
Helpful? 0

Tommy,
Any one of your suggested approaches will work fine, as long as your pay attention to airtightness.

Answered by Martin Holladay, GBA Advisor
Posted Thu, 08/21/2014 - 09:47

2.
Helpful? 0

Thank you Martin!

So in trying to get a handle on costs, would it be safe to say that if I chose method #1 that keeps the fiberglass, I might be ahead of the game? If I furred out the framing to sufficiently house the 6" fiberglass without compression, and made sure the fiberglass was enclosed on six sides (and sealed), wouldn't that theoretically give me R-19 to start with? If so, I wouldn't need so many layers of foam board to get to a respectable R-value for the assembly, so this might end up being the most cost effective way to do this.

Is my thinking sound here?

Answered by Tommy Detamore
Posted Thu, 08/21/2014 - 11:44
Edited Thu, 08/21/2014 - 11:46.

3.
Helpful? 0

Tommy,
Your thinking is correct.

Answered by Martin Holladay, GBA Advisor
Posted Fri, 08/22/2014 - 09:05

Other Questions in General questions

Any good thoughts on Drolet wood stoves?

In Energy efficiency and durability | Asked by Paul Kuenn | Nov 23, 14

Window flashing and trim with exterior rockwool

In General questions | Asked by colin slade | Nov 25, 14

What's a good damper for a bath fan/range hood vent?

In Mechanicals | Asked by Nathaniel G | Nov 23, 14

Seeking an air-to-water heat pump

In Mechanicals | Asked by Allison Ashcroft | Jul 28, 09

Insulating a cathedral ceiling

In Energy efficiency and durability | Asked by jon cypert | Nov 25, 11
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!