Spray foam - how thick to air seal a rim joist?

What is the minimum thickness of spray foam on a rim joist for effective air sealing? I'm using a disposable 2 part 200 board foot kit.

Asked by Walter Gayeski
Posted Sep 4, 2014 10:10 PM ET

Tags:

4 Answers

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Walter,
Assuming you are doing a perfect job, I would put the minimum at 1 inch.

A thicker installation may allow you to be somewhat imperfect in your application technique (although it's always possible to screw up this type of work, regardless of how thick the foam is).

Answered by Martin Holladay, GBA Advisor
Posted Sep 5, 2014 5:58 AM ET

2.

New home tract built I am adding electric circuits in basement. Check this out, they sprayed closed cell on the rim joist and that's it. The thickness, 1/8-1/4".

The builders are loved for the attention to improving the lawn after you move in though... House "looks" nice, who is gonna be looking at insulation.

Answered by aj builder, Upstate NY Zone 6a
Posted Sep 5, 2014 8:09 AM ET

3.

For air-sealing purposes you can first "picture frame" it shooting a thin initial shots directly at the seams you're trying to seal, then go over it with a 1/2-1" shot directly on the major field of the wood for vapor retardency.

Even a half-inch of 2lb foam is a ~ 2perm vapor retarder that won't wick moisture during condensation events, but a mere 1/8-1/4" shot is only about as vapor tight as standard latex primer paint.

Answered by Dana Dorsett
Posted Sep 8, 2014 1:37 PM ET

4.

Who remembers Flash and Batt? I recall articles illustrating moisture and mold problems in wall cavities where the foam is less than 2 inches. Why would this application be any different when the foam is less than 2 inches? Aside from the perm rating any thickness will block air flow. The risk of moisture and mold is another issue to consider.

Answered by Richard Beyer
Posted Sep 8, 2014 1:55 PM ET

Other Questions in General questions

Are holes in exterior plywood sheathing necessary?

In Building Code Questions | Asked by Frances Bucinel | Feb 10, 16

If the IRC specs a 3.5" nail for framing, why do so many use just a 3.25" nail

In General questions | Asked by Brad Hardie | Feb 11, 16

Rigid foam on the roof

In Green building techniques | Asked by Ryan Knight | Feb 11, 16

Mitsubisi Heat Pump- heat and cool

In General questions | Asked by Fred Gabriele | Jan 31, 16

Powerful High Ticket Profits - 5 Secrets To Explode Your High Ticket Profits

In General questions | Asked by Dick Slavin | Feb 11, 16
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!