Zone 6 wall construction - Is Zip R sheathing (R12.6) adequate

Hi

A contractor I am considering for a new house build in Fond du Lac Wi (zone 6) is recommending using the foam zip sheathing (2"foam - R12.6) and HD batt. The wall is 2x6 So the total R value is (20+12.6). After reading the articles here on gba for calculating the minimum ridged foam thickness, I'm concerned this isn't enough because the foam is de-rated at extremes temps. But since the zip foam faces the wall cavity, I wasn't sure if the dew point being inside is still an issue as long as the wall can dry to the inside by providing the class III vapor barrier. I was thinking of asking the contractor to go back and give me a quote for zip sheathing (non insulated - just osb) and 3"EPS foam over the top of it. What do you recommend?

Another contractor I am considering just uses 1"ridged foam and batt insulation also with 2x6. And no wood sheathing. I think the total r value here is 25. I realize this isn't nearly as energy effiecent as the first contractors recommendation but would this wall have condensation/moisture issues?

Thanks I appreciate everyone's perspective.

Asked by Jim Cuhel
Posted Nov 14, 2017 4:48 AM ET

Tags:

1 Answer

Select your preferred way to display the comments and click "Save settings" to activate your changes.
1.

Jim,

I think this thread will provide some pros and cons on Zip-R: http://www.greenbuildingadvisor.com/community/forum/green-building-techn...

Some folks on GBA don't like ZIP-R because they feel the foam is on the wrong side. That may be a valid argument. If you decided to use exterior foam, you would need R-11.25. Three inches of EPS wouldn't get you there, but 2 inches of XPS would be pretty close. See this article for more information: http://www.greenbuildingadvisor.com/blogs/dept/musings/calculating-minim...

Answered by Steve Knapp CZ 3A Georgia
Posted Nov 14, 2017 9:31 AM ET

Other Questions in Green building techniques

What materials meet code for "flash and batt" on my ceiling?

In Energy efficiency and durability | Asked by Robert Wan | Jan 12, 18

Rim Joist External Insulation and Air Barrier - How To?

In Energy efficiency and durability | Asked by Lance Peters | Jan 21, 18

Radon 9.3 pCi/L even after radon mitigation-is this OK??

In GBA Pro help | Asked by hotandhumid | Jan 22, 18

Where can I get a forced air heating wall vents that can be 100% sealed shut?

In Green products and materials | Asked by Bryce Nesbitt | Jan 22, 18

Header hangers vs. jack studs: Thermal bridging?

In Energy efficiency and durability | Asked by Lance Peters | Jan 21, 18
Register for a free account and join the conversation


Get a free account and join the conversation!
Become a GBA PRO!